    Default Re: 'Air Pressure Low' - Interact 308 TNC2500B

    Maybe this Tech Manual will help. It's for TNC2500B control

    Attached Files Attached Files


  2. #14
    Member Rickytoo's Avatar
    Join Date
    Sep 2018
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default Re: 'Air Pressure Low' - Interact 308 TNC2500B

    Thank you kindly. I have all the available Heidenhain manuals for this control I believe, the technical manual being well thumbed at the moment :-)



  3. #15
    Member Rickytoo's Avatar
    Join Date
    Sep 2018
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default Re: 'Air Pressure Low' - Interact 308 TNC2500B

    Having observed changing states in the tables, I've got useful output from trace-buffer. Only the first part of a manual tool change is shown here, but it completes as expected.

    Input 128 Air pressure switch
    Input 7 Unclamp microswitch
    Input 8 Clamp microswitch
    Input 9 Tool change button
    Output 5 Relay 9 - air solenoid
    Timer 26 - on for as long as tool change button pressed
    Timer 74 - on for 1725ms or 1.75s
    Marker 2942 - 'Air Pressure Low' warning - stays on until cancelled with CE

    I used I9 as a trigger. I'm not sure of the significance of the timers.

    From the attached image of the display, you can see that the air pressure low warning comes on immediately with pressing the tool change button and that the air pressure switch remains logic high, or on, all the time. You can see the microswitches switching, with 8*23=184ms being the ram operating time.

    Although the tail-end of the tool change sequence is not shown, it performs as expected.

    So, apart from the low air pressure message, toolchange appears to work correctly.

    I've just about run out of ideas as to what might be causing the air pressure warning...

    Attached Thumbnails Attached Thumbnails 'Air Pressure Low' - Interact 308 TNC2500B-trace-buffer-1-png  


  4. #16
    Member
    Join Date
    May 2004
    Location
    United Kingdom
    Posts
    402
    Downloads
    0
    Uploads
    0

    Default Re: 'Air Pressure Low' - Interact 308 TNC2500B

    Bridgeport have a habit of 'grouping up' error messages. Check the level of your lube oil reservoir, I have a feeling that it's level switch is in series with the air pressure switch

    Andrew Mawson
    East Sussex, UK


  5. #17
    Member Rickytoo's Avatar
    Join Date
    Sep 2018
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default Re: 'Air Pressure Low' - Interact 308 TNC2500B

    I've just checked today. The reservoir has sufficient oil and the switch is closed. In the past it has reported low oil correctly.

    However, I connected a switch on flying leads in place of the level switch so I could interact with it whilst observing the CRT display. Setting the switch to 'oil level low' or 'sufficient oil' makes no difference to the issue with the low air pressure warning. Furthermore, running PLC Program Trace, I see input 6 change state when operating my temporary switch, marker 3286 changes state also. Interestingly, when the switch is set to 'low oil level', it takes approximately 135seconds for the low oil message to show, yet I don't see a timer running for that delay.



  6. #18
    Member
    Join Date
    Nov 2012
    Location
    Canada
    Posts
    139
    Downloads
    0
    Uploads
    0

    Default Re: 'Air Pressure Low' - Interact 308 TNC2500B

    What does the manual say for min pressure? On my Haas it’s 100 lbs when we installed a air dryer we had to up the pressure for when it discharges lowering the air pressure.



  7. #19
    Member Rickytoo's Avatar
    Join Date
    Sep 2018
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default Re: 'Air Pressure Low' - Interact 308 TNC2500B

    It's not specified, currently the switch operates at about 40psi and the pressure is set to 80psi. However, the control only sees an open or closed switch. As I've described, I've bypassed the switch for testing purposes, so the error message is not caused by low air pressure.



Page 2 of 2 FirstFirst 12

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

'Air Pressure Low' - Interact 308 TNC2500B

'Air Pressure Low' - Interact 308 TNC2500B

'Air Pressure Low' - Interact 308 TNC2500B