Need Help! Torq Cut 22 Spindle drive fault - Page 2
Page 2 of 2 FirstFirst 12
Results 13 to 21 of 21
Thread: Torq Cut 22 Spindle drive fault
  1. #13
    Gold Member
    Jan 2005
    Default Re: Torq Cut 22 Spindle drive fault
    Quote Originally Posted by cooperjm View Post
    After turning on machine an enabling axsdrv I get this error. Sometimes it will wait a minute or two before erroring.
    I had the spindle running one time when it errored and it didn't apply the brake
    Sent from my SM-G955U using Tapatalk
    Ok remove the Jumper and we will do it another way, Remove the original jumper that you put in
    The L3 line to the VFD T connection can be put back on
    Remove the L3 Fuse
    Now Jumper L1 to L3 at the power input, make sure you remove the Jumper you added when you first run your machine
    Mactec54
  2. #14
    Registered cooperjm's Avatar
    Sep 2009
    Wouldn't swapping the lines on the vfd have the same effect?
  3. #15
    Gold Member
    Jan 2005
    No it would not, you can not change R and S
    Mactec54
  4. #16
    Sep 2009
    This is how it has been connected for the past year. No issues until the other day. I have a single phase coolant pump so no modifications were needed there.
    Do I need the jumper from R to T in the VFD?
    Torq Cut 22 Spindle drive fault-power-connections-jpg
  5. #17
    Dec 2005
    Does any on know what the F602 fault is?
    It can be more than a lost phase. If it has been working for a year, and/or is intermittent it's likely a loose connection or distorted power. It's summer and everyone's AC units are running hard. Depending on your location voltages can be swinging wildly during the day. If you try in the middle of the night does it behave?
    See page 208 of the manual.
    https://www.yaskawa.com/delegate/get...IE-S626-6C.pdf
    Torq Cut 22 Spindle drive fault-yaskawa_f602-jpg
  6. #18
    Gold Member
    Jan 2005
    Yes if you connect it the way you have, your jumper, it will help with fooling the phase detection
    The other way I suggested is you don't need your jumper in Green or a jumper at the VFD only one Jumper is needed L1 to L3 this will do the same as what you have without the need to have a jumper at the VFD, so all the wiring would stay the same
    Mactec54
  7. #19
    Sep 2009
    I ran jumper on the fault circuit for the VFD then turned on the machine. With the jumper in place I do not get the axis fault. Also if I hold in the VFD contractor while enabling the drives I still get the 602 error.
    I am confident that the VFD is bad. We will know in a couple of days when the replacement arrives.
  8. #20
    Sep 2009
    Mactec54
    My machine has circuit breakers not fuses.
    Could you draw on the schematic the way you would wire it up. That would take the confusion out this.
    Thanks for the help.
  9. #21
    Gold Member
    Jan 2005
    Mactec54
    Ok no problem you can use a jumper from L1 to L3 in front of the breakers, this schematic shows how the 2 Transformers are wired they use L1 L2 L3 for there supply power , by connecting this way everything with the wiring of the machine stays the same, no jumpers needed anywhere only at the power input
    You can continue to use it the way you have and just add the Jumper at the VFD drive R to T
    The way I suggest you don't need your Green jumper or the one at the VFD
    Connecting L1 to L3 with a Jumper takes care of all the power requirement's
    Attached Thumbnails Attached Thumbnails Torq Cut 22 Spindle drive fault-torq-cut-22-dx32-schematic-2-pdf
    Mactec54