Problem TNC2500 Control Operating Temperature Exceeded


Results 1 to 5 of 5

Thread: TNC2500 Control Operating Temperature Exceeded

  1. #1

    Red face TNC2500 Control Operating Temperature Exceeded

    Hi,
    Have a Bridgeport VMC412 with TNC2500 control.
    When we bought the machine pre-owned some 18 years ago it gave me aTNC operating temperature exceeded and the monitor goes Phoosssshhhhh and lot of numbers flashing.
    We made a hole at the bottom and fitted a small extractor and a hole on the side with a car filter fitted and the machine has worked for years trouble free.
    Now we are machining a large complex part which takes 30 hours straight and the machine is doing the same. I fitted a stand fan blowing over the cabinet and it works ok but this is risky.
    I know there should be a thermistor somewhere which monitors the temperature. The temperature inside is very low as it is winter as well.
    I also know that there is a parameter in the machine which controls this. I wish to look at this as well.
    Could somebody identify where this thermistor might be?
    Somebody some years ago had this problem and somebody suggested a dangerous solution according to my tech
    help please! everytime this happens the workpiece is bust.

    Similar Threads:


  2. #2
    Member
    Join Date
    Jan 2005
    Location
    us
    Posts
    1121
    Downloads
    0
    Uploads
    0

    Default

    I do not believe there is a parameter for this, it is not part of the controlling software, rather internal background stuff

    This is not a normal error, so either the control is actually too hot or the sensor is bad. There maybe technical manuals around, I think the 2500 is really a TNC360 IIRC

    call Heidenhain and see if they have any guidance.

    Is the time before error predictable?
    if so, see if you can pause the program at a tool change prior and shut it down for a few hours to avoid lost parts



  3. #3

    Default

    Yes its not a parameter. Its a thermistor somewhere in the panel. It happens when it reaches a certain temperature and far off from the exceeded temperature. I can get around this by placing a fan near the open control which is not acceptable.
    Haidenhain suggested I send the control for repair but that is no option... I have already located something looking like a thermistor on the board.... but not sure..



  4. #4
    Registered
    Join Date
    Mar 2013
    Location
    Canada
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default 2 possible sources of the error

    Quote Originally Posted by sputnikprec View Post
    Yes its not a parameter. Its a thermistor somewhere in the panel. It happens when it reaches a certain temperature and far off from the exceeded temperature. I can get around this by placing a fan near the open control which is not acceptable.
    Haidenhain suggested I send the control for repair but that is no option... I have already located something looking like a thermistor on the board.... but not sure..

    On a TNC150, The thermal component is on the analog board (this is the board with the feedback connectors plugged in, second from the back). It is a large black component on the right side marked MTS70B. This should have a low resistance of maybe 0.6 ohm.

    On the position input board (where the scale feedback plugs in) check the capacitor sips ID 202862-02 .



  5. #5
    Member MORPHIOUS's Avatar
    Join Date
    Nov 2022
    Posts
    1
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by sputnikprec View Post
    Yes its not a parameter. Its a thermistor somewhere in the panel. It happens when it reaches a certain temperature and far off from the exceeded temperature. I can get around this by placing a fan near the open control which is not acceptable.
    Haidenhain suggested I send the control for repair but that is no option... I have already located something looking like a thermistor on the board.... but not sure..
    Hello! By any chance did you find our how to solve this issue I'm currently experiencing the same issue.
    Regards!



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

TNC2500 Control Operating Temperature Exceeded

TNC2500 Control Operating Temperature Exceeded