    I have had my UC300ETH-UB1 successfully connected to my Delta VFD-B and working properly for better than a year. Suddenly, this AM, I cannot control the spindle from Mach4. The spindle will not turn on

    Testing Delta VFD-B (VFD022B21A) to UB1-screenshot-2024-12-07-111510-png

    I have tested AH1 to AL1 = 10V. I can see that AL1 to AO1 has ~ 5V when I try to spin the spindle at 10,000 RPM (roughly 1/2 its max). I cannot seem to prove that relay K2 works. I read ~22V between CM2 and NO2, both when I have the spindle idle and when I attempt to engage it to spin.

    How can I prove that the relay works?

    Thanks for any thoughts.

    Similar Threads:


  2. #2
    Member
    Join Date
    Jul 2008
    Location
    usa
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Testing Delta VFD-B (VFD022B21A) to UB1

    I have confirmed that K2 relay contacts no longer function as a switch to start the spindle. Does anyone know how to use K1 contacts for the same purpose? The UB1 owner manual is not clear to me on how to use K1.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Testing Delta VFD-B (VFD022B21A) to UB1

Testing Delta VFD-B (VFD022B21A) to UB1