    Default Huanyang VFD Wiring

    Hey guys

    Have just purchased a Huanyang VFD (Model HY02D223B), but I'm unsure of what wire gauge to use. The label on the VFD indicates that the unit is 1 phase in (220v) and 3 phase out.

    So, should I be using 15 amp wire for both the input and output sizes of the VFD? Or could I use 10 amp for the (240v) input and 15 amp for the 3 phase output?

    Note, that I will be using the full power of the spindle (24,000 rpm) which will attach to the VFD.

    Thanks in advance
    Dave

    Similar Threads:


  2. #2
    Member ger21's Avatar
    Join Date
    Mar 2003
    Location
    Shelby Township
    Posts
    35538
    Downloads
    1
    Uploads
    0

    Default Re: Huanyang VFD Wiring

    The wire for the input should be able to handle at least 20-25 amps.

    Gerry

    UCCNC 2017 Screenset
    [URL]http://www.thecncwoodworker.com/2017.html[/URL]

    Mach3 2010 Screenset
    [URL]http://www.thecncwoodworker.com/2010.html[/URL]

    JointCAM - CNC Dovetails & Box Joints
    [URL]http://www.g-forcecnc.com/jointcam.html[/URL]

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)


  3. #3

    Default Re: Huanyang VFD Wiring

    Grab this from bunnings and cut the end off,

    HPM 10m 15A Extra Heavy Duty Caravan Extension Cable

    I use them on my machines, each of my machines are plugged into 32amp circuit breakers, with 6mm 3 core cable

    works a treat



  4. #4
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang VFD Wiring

    Quote Originally Posted by pootaholic View Post
    Hey guys

    Have just purchased a Huanyang VFD (Model HY02D223B), but I'm unsure of what wire gauge to use. The label on the VFD indicates that the unit is 1 phase in (220v) and 3 phase out.

    So, should I be using 15 amp wire for both the input and output sizes of the VFD? Or could I use 10 amp for the (240v) input and 15 amp for the 3 phase output?

    Note, that I will be using the full power of the spindle (24,000 rpm) which will attach to the VFD.

    Thanks in advance
    Dave
    The output of the drive is 10A the input current will be double the output current, for single phase use so the cable should be rated at least 25A

    Mactec54


  5. #5
    Member
    Join Date
    Aug 2014
    Posts
    125
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang VFD Wiring

    Connected to a 10A 220V supply? I think 25A is pretty much overkill for NZ/Australian 220/240V systems.

    Maybe in your asthmatic 110V world... but we have full-fat electricity and are man enough to use it



  6. #6
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang VFD Wiring

    Quote Originally Posted by ledaero View Post
    Connected to a 10A 220V supply? I think 25A is pretty much overkill for NZ/Australian 220/240V systems.

    Maybe in your asthmatic 110V world... but we have full-fat electricity and are man enough to use it
    You are very uneducated, USA and all of NA uses 240v Ac Single Phase just the same as you, and you need a 25A circuit In NA they just have an option to split the 240v to 120v there is no such thing as 110v Ac single phase in the USA

    Even in Australia an NZ they have electrical code for VFD Drive installation which are stricter than in NA you need to look at your electrical code requirements for a VFD Drive installation

    The output cable depending on what motor or spindle you are using a shielded 4 core 16 gauge is all you need for that size VFD Drive ( High Flex Cable if you are using this for a Zaxes on a Router )

    If you read the VFD Drive manual you will find the input amp requirement for single phase use like the snip below

    Attached Thumbnails Attached Thumbnails Huanyang VFD Wiring-vfd-drive-single-phase-240v-amp-requirement  
    Mactec54


  7. #7
    Member
    Join Date
    Aug 2014
    Posts
    125
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang VFD Wiring

    You are very thin-skinned.

    Ever seen one of these ””? Do you know what they represent?



  8. #8
    Registered
    Join Date
    Aug 2006
    Location
    Australia
    Posts
    16
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by ledaero View Post
    You are very thin-skinned.

    Ever seen one of these ””? Do you know what they represent?

    Mactect is right, the input current on a single phase 240V drive is much higher than the output.

    If the output is to be fully loaded, a dedicated circuit would be required, typically a 10A GPO won't be big enough.

    We do have reasonably good standards here, but also a massive knowledge gap with respect to how drives work and the importance of the screened motor cable and how it must be bonded at both ends, not just bunched up and put in a lug!!

    Last edited by ger21; 02-15-2019 at 06:26 PM.


  9. #9
    ericks
    Guest

    Default Re: Huanyang VFD Wiring

    Quote Originally Posted by zxhoon View Post

    Mactect is right, the input current on a single phase 240V drive is much higher than the output.

    If the output is to be fully loaded, a dedicated circuit would be required, typically a 10A GPO won't be big enough.

    We do have reasonably good standards here, but also a massive knowledge gap with respect to how drives work and the importance of the screened motor cable and how it must be bonded at both ends, not just bunched up and put in a lug!!
    I work with "Australians" and you are not correct, there is not a knowledge gap with regards to drives and their installation. Possibly you referring to diy guys....anyway they not supposed to install and wire electrical devices

    Last edited by ger21; 02-15-2019 at 06:27 PM.


  10. #10
    Registered
    Join Date
    Aug 2006
    Location
    Australia
    Posts
    16
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang VFD Wiring

    Quote Originally Posted by ericks View Post
    I work with "Australians" and you are not correct, there is not a knowledge gap with regards to drives and their installation. Possibly you referring to diy guys....anyway they not supposed to install and wire electrical devices
    I work in the industry in Australia and I can assure you, there is.

    I work with some of the biggest users of drives kin industry, anywhere from 0.75kw up to 630kw, with some sites having over 600 drives installed and without a doubt they have very little knowledge about drives.

    I'm not talking about DIY guys who are a scary breed on their own haha

    Industrial electricians simply don't have the training or experience on drives that they should have here, it's not taught at the basic TAFE level when they are being trained to become electricians, the drives module consists of some very basic information but not enough.

    This is not aimed at electricians or to put anyone down, it is just simply the way it is in my experience.

    Maybe you talk to skilled electricians or technicians who work with drives a lot, but the vast majority do not know everything they should before working on drives.

    I've seen anything from motor cable run in three parallel runs of TPS (house building wire) to screened motor cable only bonded at the drive and not the motor (because an electrical inspector would not pass it if it was bonded at the motor - confusion between bonding motor screen and analog signal screens!), screened motor cable not terminated at the motor as they have used nylon glands instead of EMC glands, the list could go on.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Huanyang VFD Wiring

Huanyang VFD Wiring