View Full Version : Problem TNC 155B dripfeed



Tommie
04-03-2012, 03:24 AM
Hello,

I have a Bridgeport interact II with TNC155B control.
I have set up comunication with TNCserver. This works fine.
When I go to dripfeed the problems start!!
Al the settings are correct according A LOT of treads around here, but still no luck. I have some questions!
1: a the solutions around here, are the based on software ore hardware handshake!
my cabel is <25 way tnc> <9 way pc> 2-2, 3-3, 4-8, 5-7, 6-4, 7-5, 20-6.
MP71-515,
MP218-515,
MP219-17736,
MP220-16712,
MP221-279,
MP222-168,
MP223-1,
MP224-4,
The machine is on FE with 2400. So is the TNCserver.
COM settings are: 2400 baut, 7 datab, even par, 1 stop b, Xon / Xoff
What setting makes the handshake sofeware ore hardware?

How must a heidenhain pgm being saves (i found like 1.h), but whats the exact content of the start en end of the program!?
If any one has a example (tth.jespers at gmail.com).

Hope anyone can get me to the next level!! I feed that I a close, just missing some details.

csg67
04-09-2012, 06:06 AM
MP71 - 515
MP218 - 17736
MP219 - 16712
MP220 - 279
MP221 - 5382
MP222 - 168
MP223 - 1=DNC, 0=standard RS232C
MP224 - 4

cabel:
PC 9 pin --- TNC 25 pin (adapter block Id.:239 758-01)
1 - 20
2 - 2
3 - 3
4 - 6 + 8
5 - 7
6 - 20
7 - 5
8 - 4
9 - -

COM setting is unnecessary. The TNCserver set the COM port.