Proper grounding

I have been searching for answers but can't find one for me...so I did try before posting.

First...I have a Xylotex 4 axis driver and their power supply. I am driving 4- 495 oz steppers through four wire shielded cable with ground. From the steppers they go to the driver which is mounted in a plastic box mounted to the steel table. There is no electrical path between the driver, power supply,
and computer to the table.
Question........grounds and shielding has never been connected. What is the
best way to ground?
Do I ground the ground wire, shielding, or both?

Does the cable shield/ground need to be commom with the driver/power
supply and or computer?

I assume the grounding of the stepper wiring is for RF noise.

Can I just ground each cable at each stepper location to steel table and leave the ends in the plastic box by the driver disconnected?
The easiest way for me would be to tie all four stepper cables grounds
or shields together after they enter the driver box. If that's ok do they need to be grounded to the table, driver board etc. I am not having any problems
but this should be completed properly.
I hope I have made myself clear............thanks.............Nick
Reply With Quote

  #2   Ban this user!
Old 12-03-2006, 12:30 PM
 
Join Date: May 2004
Location: United States
Posts: 104
jkeyser14 is on a distinguished road

Shielded cable should only be grounded at one end. Normally you ground it on the controller side, though I'm not sure of the exact reason.
__________________
-John
http://www.engineeringhobbyist.com
Reply With Quote

  #3   Ban this user!
Old 12-03-2006, 01:21 PM
 
Join Date: Oct 2006
Location: UK
Posts: 36
Geetar-ist is on a distinguished road

the reason for only connecting to ground at one end is that the "noise" - electrical interferance which can cause crosstalk in control systems - especially analogue systems (0-10v etc) by raising the actual ground value to a positive voltage which loses the control ground reference.

noise is introduced to the system and then like any other type of electrical voltage/signal looks for the route of least resistance (ground hopefully). this is where the shield comes in ! it routes this signal to ground before it can effect the signal cables inside.

if you ground the shield at both ends you are creating an earth loop effectively keeping those signal from leaving the shield quickly..

these shields should be grounded at source - the controller as jkeyser14 rightly says!

sorry its not a very good explanation but thats the way I understand it !
Reply With Quote

  #4   Ban this user!
Old 12-03-2006, 04:25 PM
 
Join Date: May 2004
Location: United States
Posts: 456
JRoque is on a distinguished road

Hi. I have my steppers and spindle grounded to the frame of the machine as close to the motors as possible. I also ground the shields on both ends since I don't want any potential to develop along that. The frame is then connected to power earth on the AC outlet. All of my logic connection bundles run their own ground returns and are connected only to a common place at the PC controller end.

JR
Reply With Quote

  #5  
Old 12-03-2006, 04:45 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by JRoque View Post
I also ground the shields on both ends since I don't want any potential to develop along that.
JR
Actually a potential is what can happen if you ground both ends.
The reason you only ground one end is, If you have both ends grounded and some part of the circuit seeks a ground path (also known as ground loop) and your shield is the lowest resistance path, then the shield passes current and the resultant field is impressed on the conductors within, which you certainly do not want.
The whole concept of grounding is to produce a common plane ( ground, Earth etc) This is done by setting up a common point in the form of a copper bus or strip of grounded terminals where every shield, ground, incoming service ground, power suppy commons etc, are connected to.
This means that there is a common point where no potential should exist anywhere common to this point and ground ( the machine and the planet (Earth) you are standing on!)
See this post also http://cnczone.com/forums/showthread.php?t=28227
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-03-2006, 10:42 PM
 
Join Date: May 2004
Location: United States
Posts: 456
JRoque is on a distinguished road

Hi Al. Right, but chances are the large frame on my machine is a better conductor than the shield on my cables. If a noise spike is introduced at the open end of the shield, it would have to travel all the way to the other end before finding it's way to ground. That means that there's a better chance of picking it up along the way.

I would agree that for the larger potentials - as is with lightning - you certainly want to ground only one end. The small resistance difference to ground between the ends would create a huge potential in that scenario.

I just did a quick search on this topic and there are two camps: one that grounds at one end and another that grounds at both. It seems to depend on the nature of the signals being carried and how much current they are likely to carry.

JR
Reply With Quote

  #7   Ban this user!
Old 12-04-2006, 04:58 AM
 
Join Date: Oct 2006
Location: UK
Posts: 36
Geetar-ist is on a distinguished road

yes, there are two camps when it comes to grounding, I work with large servo motors which control conveyor systems. - xxkW

these are grounded at the servo motor controller only and very rarely experience issues.

as for grounding on the frame, that really depends on the construction of your frame, when we ground to the chassis etc a proper resistance test should be conducted to ensure a true low resistance route to ground at each proposed earth point...
Reply With Quote

  #8  
Old 12-04-2006, 07:17 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by JRoque View Post
I just did a quick search on this topic and there are two camps: one that grounds at one end and another that grounds at both. It seems to depend on the nature of the signals being carried and how much current they are likely to carry.

JR
That surprises me as in all the years I have been involved with industrial machinery, I have never seen a manufacturer specify or read of a recommended practice to ground both ends of a shielded cable, because of ground loops.
Co-incidentally, if you go to the link I showed above, he has just cured his problem, which could easily been caused by shields grounded at both ends or at least, would have aggravated the situation.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.

Last edited by Al_The_Man; 12-04-2006 at 07:36 AM.
Reply With Quote

  #9   Ban this user!
Old 12-04-2006, 07:43 AM
 
Join Date: Nov 2006
Location: USA
Posts: 590
NinerSevenTango is on a distinguished road

The grounds for everything should be configured as a star, meaning all of them connect to one point only.

If you ground both ends of a shield in a cable, then consider what happens if a power line ever accidentally zaps to ground. It's the fault current that you really want to watch for. If there are ground loops in your system, then when an accident happens or someone decides to weld a bracket on the side of your machine, the currents can pass through the common traces on your circuit boards. And yes, copper wire has lower resistance than a huge steel machine. So an appreciable fraction of any fault current will try to find its way home through your expensive controls.

As for noise control, if the shield is grounded at both ends, and there is a noise generator near your cable, then there is a current path for inductively coupled noise. The current gets generated and can pass through the machine and back to the other end. This now floats the ground reference at one end of the cable relative to the other, or it inductively couples the noise into your signal wires. So the best thing is to pop that loop open. With it open, any noise generator near the cable will allow the shield to wiggle a harmless voltage on the ungrounded end of the shield, but none of the noise gets through into the signal wires you are protecting.

I do analog and digital control with huge noise generators, and this kind of practice is mandatory. If we start a new machine up and it acts illogically, the first thing we do after double checking all the obvious stuff is try to find out where somebody created a ground loop. It takes vigilance to keep them out of a sizable system.

--97T--
Reply With Quote

  #10   Ban this user!
Old 12-04-2006, 08:35 AM
 
Join Date: Jun 2006
Location: usa
Posts: 214
monte55 is on a distinguished road

I read all the posts and still don't quite have an answer to my questions.
I got some good info though.
My 60X60" table is steel. The driver is in a plastic box not grounded to table.
If I take each stepper wires shield and ground as it enters the plastic driver
box and connect them all together, what do I connect that to or do I leave
it in space?
I don't think I want it ground with the driver in case the router would short and maybe harm the electronics. The only ground the table has now is the ground on the router motor.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 12-05-2006, 05:48 AM
 
Join Date: Nov 2006
Location: USA
Posts: 590
NinerSevenTango is on a distinguished road

Monte, I'll go out on a limb and suggest you connect the grounds and shields together at one point, with a single connection to ground.
Reply With Quote

  #12  
Old 12-05-2006, 06:09 AM
*Registered User*
 
Join Date: Oct 2006
Location: USA
Age: 48
Posts: 143
DayneInfo is on a distinguished road

Monte55 - I emailed Jeff at Xylotex with the sme question...here is his answer.

Dwayne

support@xylotex.com wrote:
> >> Hi,
> >> The sheilds should be connected to the Earth Ground (green wire) on
> >> the
> >> power supply.
> >>
> >> Jeff
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 12:30 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361