Tig welder tripping GFI's

My welder was originally installed within 3 feet of a GFI in my shop..... Ah, don't you agree shop sounds bigger and more professional than 2-car agrage?
The welder tripped the GFI's every time I stepped on the pedal. So, I've spent over a hundred dollars moving the welder to the other side of the gara... ah, I mean shop and everything was happy for a day.

Then I discovered I had the HF switched to "continous" and when I switched it to "start only", the GFI's again trip.

When I moved the thing I added a 14 ga wire from the welder frame to the conduit assuming this additional ground might help.

So, if running the HF on "continous" actually was the reason it didn't trip the GFI's, should I run it that way even for DC welding? Or, should I replace the GFI's with ordinary receptacles and live in fear of the electric code police hunting me down? .... I'll try to remember not to water down the floor and operate electric tools when barefoot.
Tweet this Post!Share on Facebook
Reply With Quote

  #2  
Old 11-27-2006, 11:03 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,706
Al_The_Man is on a distinguished road
Buy me a Beer?
What size GFI are you using for a TIG welder, is there a reason you hooked it into a GFI in the first place?
Every time you connect the work or the the 14g wire to ground, you are defeating the GFI.
unless you have 100% isolation between the supply and the output, you are causing it to trip, If you used a GFI because of a lack of adequate service ground, you could set up a ground rod, but I would use the service ground direct with a fused disconnect or a normal breaker.
Your unit should be wired with 2 wire and ground if 1phase.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 11-27-2006, 08:32 PM
 
Join Date: Oct 2004
Location: USA
Posts: 71
Dugg is on a distinguished road
Sorry Al and gentlemen, I didn't do a very good job explaining my problem. The welder is not on a GFI.
The welder is powered from a 220v 50 amp breaker in a sub-panel I installed in the garage.
The welder was originally located within 5 feet of this sub-panel.
The welder used to trip a 110v GFI breaker that was fed from the main panel in the house located within 3 feet of the welder.
The welder used to also trip a second 110v GFI fed from the sub-panel.
Then I moved the welder to the other side of the garage by installing 3 each number 4 wires in 1" metal conduit from the sub-panel to the other side of the shop... (although it's still only a 2 car garage)
The new welder location is about 10 feet from the second GFI and twenty plus feet from the first GFI.
Now, it still trips both GFI's within what seems to be a few seconds which I associate with the duration of the "start only" HF used for DC welding.
When I inadvertently had the HF on the "continuos" setting, I think it was the reason the GFI's didn't trip.
So, should I leave the welder set on continuos HF? Will this hurt the welder when in DC? Or should I get rid of the GFI's?
I hope this gives a better picture of the layout and again, I apologize for my lacking first explaination.
Tweet this Post!Share on Facebook
Reply With Quote

  #4   Ban this user!
Old 11-27-2006, 08:35 PM
 
Join Date: Aug 2004
Location: US
Posts: 2,782
ViperTX is on a distinguished road
My GFI in the garage trips ocassionally when I switch off the shop lights in the garage....so,...
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 11-27-2006, 11:50 PM
 
Join Date: Aug 2003
Location: United States
Posts: 28
JEFFY is on a distinguished road
I know you said your welder power is in conduit, but what about the rest of the wiring?(romex, plastic conduit,steel conduit)
When you ran the sub panel did you run a common ground to the same ground point of the main panel?(water main or ground rod) I seem to remember that a loss of a true ground can cause havic at times. You may also try a hospital grade or commerical grade of GFI if you haven't tried already tried a differant GFI. Also is there anything else being protected by the GFI or pluged into the GFI at the time it trips? Exstension cords, shop lights, drop lights and other misc shop equipment are not always shielded enought to keep out the EMI from the RFI of the hi freg. causing GFI to trip
I'm very curious about this as I'm building a new shop now and planned on the safty of GFI's, if you do find the cause or solution please post the cause.
__________________
JEFFY
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6  
Old 11-28-2006, 09:12 AM
mxtras's Avatar
Silver Member
 
Join Date: May 2005
Location: USA
Age: 45
Posts: 1,810
mxtras is on a distinguished road
Or try GFCI breakers instead of outlets? I have no personal experience but I have read/heard they are more stable.

Scott
__________________
Consistency is a good thing....unless you're consistently an idiot.
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 11-28-2006, 02:36 PM
 
Join Date: Aug 2004
Location: US
Posts: 2,782
ViperTX is on a distinguished road
I've never had problems with my GFI Breakers....just the outlets that have GFI built into them.
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 11-29-2006, 10:44 AM
 
Join Date: Oct 2004
Location: USA
Posts: 71
Dugg is on a distinguished road
Hey Jeffy, Your post got me thinking.... yes, I do occasionally think, but I didn't inhale.
When I added the sub-panel in the garage, I piped it from the main box in plastic conduit. There are three number 4 wires and a single number 6 for the ground between the two panels. The whole project was done with a permit, inspected and signed off with no problems.
I'm beginning to think I need a better ground at the sub-panel. So, I'm going to pound one of those eight foot grounding rods onto the soil (soil? this is the mountains in Colorado, we have rock) and add a ground wire to the sub panel..... all this will be addressed next summer when the ground isn't frozen and covered with snow.
Hmmmm, maybe I can run a ground wire from that panel through the garage ceiling and attach it the water pipes for the room above.....Thanks
Tweet this Post!Share on Facebook
Reply With Quote

  #9  
Old 11-29-2006, 12:38 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,706
Al_The_Man is on a distinguished road
Buy me a Beer?
Re-thinking, Ironically a better ground might make it worse, the method GFI's use detects whether even an ungrounded piece of equipment is actually passing current to ground, as in 2 wire, double insulated power tools.
The way it is done the GFI monitors current in both conductors, live and neutral, not the ground conductor, per-se.
If equipment actually has a condition where a minute ground current is actually flowing, the current between the two conductors is unbalanced, and the GFI trips.
I suspect that the High frequency is causing a small current to pass to ground, either capacitively or inductively and causing the trip.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #10   Ban this user!
Old 11-29-2006, 12:48 PM
 
Join Date: Jul 2003
Location: Holmen, WI
Posts: 1,055
samco is on a distinguished road
I have had issues with gfi's and inductive loads. (even when they are not on the same circuit.) I just figured I needed to buy better quality ones not the 10 dollar ones from menards. (have not yet)

sam
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 12-10-2006, 01:26 AM
 
Join Date: Mar 2003
Location: Utah
Posts: 214
Mortek is on a distinguished road
You need to try isolating the HF as much as possible. It's noise can affect electronics everywhere. Ground the sub panel as you are planning, also drive another ground rod next to the welder and ground it. run a ground wire from the soil ground at the welder to your work table. I have a welder in my garage also plus a 3axis machining center. I was welding aluminum one day (HF continuous) while running a 3d machining operation and the hf cause my work coordinate to shift in my mill. It used to send my vcr into fast forward while playing a movie. I've seen it type in characters in a computer just by waving your hand over the keyboard. I have a miller 350LX Syncrowave machine and the manual gives a diagram of how to ground the hf.

Ken
Tweet this Post!Share on Facebook
Reply With Quote

  #12   Ban this user!
Old 12-10-2006, 10:37 AM
 
Join Date: Oct 2004
Location: USA
Posts: 71
Dugg is on a distinguished road
Thanks Mortek,

Your suggestions will be followed next spring when the rocks aren't all frozen together and I can pound a rod into the ground. I've been kicking an idea around to build an air powered hammer that could be used to pound in these ground rods and then rent it out to contractors.... oh the heck with it, I'll beat the rod into the ground like everyone else

What is working for now, is just leaving the HF on the continuous.

Thanks all.

Doug
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 04:03 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353