Hello,
To solve the problem PLC IN BLOCCO is necessary to perform the AutoSetup. From step 1 with the formatting and reset the CN ESA loading the PLC in step 12.
But the important thing is to know why the PLC has been Blocked.
Usually the reason is the 3.7volts lithium battery is low on charge. CNCs old KVARA5 or 6, Or battery CR202 for NEW ESA S500.
Is it must be replaced with the machine.
For Autosetup occur without errors is necessary to folder C: / KVARA with the correct files for the Serial Number of your machine.
Hello Friend.
You did very well to replace the battery.
For detailed information I believe you need to contact the manufacturer CN. The ESA.
But in CN we use in SCM, (and I know not taken the Magic and not part of SCM Group). within the C: \ Kvara there is AutoSetup.ini file and
within the folder C: \ Kavara \ Exe you run the basemenu.exe
File that it had opened in auto setup mode where you choose the Language and then starts the auto setup procedure step 1-12.
sorry but i have the analog problem but i do the autosetup but when it arrive at plc loading there is a message "file non found: /c:slowplc.cmd its urgently sorry for english i'm italian