    Angry VFD induces terrible vibration in 2 different motors. SOS

    the troubles continue. My KB Electronics KBAC 27D 2HP VFD controller
    causes really bad vibrations in 2 different motors: 2 HP 3600 RPM
    Emerson and 1.5 HP 1750 RPM Dayton. Both are Invertor duty, brand new motors from Grainger. So is the controller. 220V in , 3 phase 208 out.


    While it is not that bad with 2HP , as it is used in belt grinder, the
    other motor was supposed to become VFD drive for my 9x20 lathe. With it shaking like this (NOTHING on the shaft, firmly bolted down to a massive bench, it shakes it badly, throughout whole range of speeds) there's no way it is going to work on a lathe. Vibrations only disappears at the max RPM.

    To load it some, I removed a chuck from a lathe and chucked it right
    onto the shaft of 1.5 HP. No effect.


    What gives ? Is it typical for VFD contoller to induce this type of
    vibrations ? I reckon not, as so many people use VFD drives on their mills and lathes ... I am @ loss.


    Will call KB electronics, now that I know it is not a problem with a
    motor.


    If I spin both motors to high RPM, and then turn off the controller,
    the vibrations instantly disappers and motors become smooth as silk and coast down to stop.

    Similar Threads:


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24220
    Downloads
    0
    Uploads
    0

    Default

    Sounds like VFD problem (fault), Off load especially, a motor should be silent and smooth throughout the speed ranges.
    All the VFD's I have installed have fired up smooth out of the box with the default parameters, even before tuning etc.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Member JPMach's Avatar
    Join Date
    Aug 2005
    Location
    USA
    Posts
    413
    Downloads
    0
    Uploads
    0

    Default

    Check the carrier frequency, if this is to low the motors will be jerky. This is not the variable frequency you use for speed, this is the frequency at which the dc pulses are sent to the motor to mimic the sine wave. I don't remember exactly but I think this should be around 400 + cycles.

    JP



  4. #4
    Registered
    Join Date
    May 2005
    Location
    USA
    Posts
    66
    Downloads
    0
    Uploads
    0

    Default

    When the VFD is new they typically ship with default parameters set so that it should fire up and run the motors without requiring any adjustments and the motors should run very smoothly. The fact that 2 different motors aren't running right is making it likely that either the VFD is defective or somehow one or more of its parameters got set to bad values. I'd get a guy for KB on the phone, have him go through the setup of the unit to make sure its set right and if the motors still don't run smooth they should exchange the unit.

    Paul T.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

VFD induces terrible vibration in 2 different motors. SOS

VFD induces terrible vibration in 2 different motors. SOS