I first post on these VFD Drives in November 2011, used to get lots of them for repair, most today when they fail are not worth repairing, as the cost of these VFD Drives is so low, repair cost plus shipping cost, you can buy a new one
Nothing has changed except, the drives are much better built, better component's Etc. than they where then, and most of the everyday failure's are not happening now, some of the main components that Mitsubishi use in there VFD Drives, Haunyang are using also
Is there a need to worry about how you wire the input to these VFD Drives, not really, if you can follow the manual, they say you can connect to any 2 phases, it is a choice you have, It is not only me that has said to use R and T connections, any of the good resellers also say to connect for single phase use R and T, from the hundreds of posts on the subject you can see for your self which has been the most reliable connection, it's up to the user they can do what ever they like, and if it works then they are up and running, nothing is written in stone as to what to use for your connection
This is the only VFD Drive manufacture that says, in there manual that any 2 phases can be connected, all other manufactures specify which 2 phases to connect for Single Phase connection
Most VFD Drive Manufactures, Use R and S for Single Phase Connection, as per there Manuals, the rest use R and T as per there Manuals But they do specify which 2 connections to use
The biggest problem with these and other VFD Drives, has been with users not setting the correct Parameters, this is what cause's the most Damage to the VFD drives or the Spindle Motor, Not very often does the wiring cause any major problems, only when you get over current under current Fault, then this is usually caused by a wiring problem, ( and may not be from the input connection choice ) damage has already happened in most cases, when you get this fault, some times the fault has saved the drive and the wiring can be corrected the user got lucky this time