Can you post a video of the spindle stalling during work? a picture of the VFD too, 2200W is a lot of power on my opinion.
Hey guys,
I purchased a 110v 2.2kw spindle and vfd from buildyourcnc.com recently and just got around to installing it. I cannot tell the brand of vfd and all the parameters in the small user guide are in Chinese. I set up and programmed the vfd per the site instructions. All air cut tests have been successful. However when I try taking wood test cuts the motor loses power dramatically. I am replacing a porter cable 7518 with this. I ran a proven program using the same whiteside 1/2" carbide spiral bit with .150 doc @ 75ipm with 18k rpm/300hz in northern ash. Now the vfd and spindle both have 8.5 amps on them. I programmed the vfd at 8.5 amps per the website instructions. But logic tells me that the input amps should really be 17 amps at 110 volts. I set the vfd to 16 amps input voltage and the spindle still bogged in the full width cut. Rpms increased to what sounded like full power when it was doing a 40% step over but would then stall when it was taking a full width cut.
Do you guys have any ideas?
Thank you advance
Chris
Similar Threads:
Last edited by factory5150; 08-09-2017 at 12:18 PM.
Can you post a video of the spindle stalling during work? a picture of the VFD too, 2200W is a lot of power on my opinion.
The Parameters for the spindle is what you set in the VFD 9 amps is max for this spindle, so your VFD should not be set above this number, you will smoke your spindle with 16 amps set
Do you have this on a 25A to 30A amp circuit for the input power your 120v would need to be a minimum of 25 amps, a standard 15 amp circuit is not going to do it, this is also a bad idea for a 2.2Kw spindle the VFD should of been for 220v / 240v input supply voltage
1.5Kw is about the limit if someone only has 120v supply
Mactec54
This is on a 20 amp circuit. It only ran at the higher amps for less than 30 seconds. Verified the settings for the 4th time and set the amps back to 8.5 and shot this video.
https://youtu.be/sbOd8830D6I
I understand due to my input voltage that I will never see the power it could using 220 but I didn't think it would be this bad. I have trim routers with more balls than this. So if this is as good as it gets I guess ill need to sell this setup, call an electrician to rewire my tapped panel and get a proper 220v vfd/spindle.
I was lead to believe that you can program the input and output amps to control the ceiling of power it will consume.
How many mm is your cut depth on the video? and what tool bit? sounds like too much drag it almost like braking the spindle RPM, if you have a clamp meter try to read how many amps. while on that dragging sound. on that we can tell if it`a a wrong setting on the VFD or it`s just too much for the tool bit to cut causing it to drag on the material, is the tool bit in a correct rotation?
This is a 'low-price' Chinese VFD, yes?
Cheers
Roger
I had that info in the first post. 3.8mm depth of cut using a brand new Whiteside ru5200. I have been using these programs for years without issue running on my old porter cable 7518 setup. Spindle is rotating the correct direction, that was one of the first things I checked.
I only have a multimeter with probes, not alligator clips. Where would I put the probes to test how many amps during a load?
And yes I suppose this would be a cheap vfd, but guys run cheap eBay vfds all day long. Is it going to have the longevity of the good ones? No, but the price point doesn't reflect that either.
110v 3ph 2.2Kw would be a dog, only the Chinese would do such a thing to try to get extra sales / business
The problem is your spindle can't be 2.2Kw @ 8.5A that would need to be 20amps at 110v to run correctly, so what you have is a less than 1Kw spindle running at 8.5A on 110V
So your router you where using was more powerful than what you have, you would have to take lighter cuts for this to work
Mactec54
Buildyourcnc.com is standing behind the product and I'm swapping this for the 220v version. Should be good to go once I get the new parts and the electrician out to do the install.
I appreciate the help fellas.
Chris
Even so, 220 V x 8.5 A = 1.87 kW. Not really enough to drive a 2.2 kW motor, especially after allowing for some efficiency losses.
Cheers
Roger
I was going on the OP's comments in posting #1 and subsequent.
Cheers
Roger
Sounds like caveat emptor.
Perhaps there is more tech knowledge here than with some vendors?
Cheers
Roger