For a starter you spindle can only run form 6,000RPM to 24,000RPM it can not be run below 6,000Originally Posted by AllanUrup2026748
The first thing you have to check it the Spindle Ground/Connection the 4th pin on most are not connected in side, this has to be corrected before you power up the spindle
Here are the Parameters to set, they have to be set as below or damage can happen to the VFD drive and Spindle
Huanyang Mactec54
PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
PD001=0 (1 For Remote Control)
PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )
( J1 Also Needs to be set for Terminal Control )
PD003=400
PD004=400
PD005=400
PD007=20
PD008=220 (Motor Rated Voltage, If you have 120v spindle then set to 120v )
PD009=15
PD010=8
PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)
PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
PD014 Acceleration=12 ( Adjust to suit)
PD015 Deceleration=12 (Adjust to suit)
( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )
PD142= ( Motor Max Amps)
PD142=( 220vSet for your motor Amp Rating 2.2Kw Spindle 9 amp )
PD142=( 220VSet for your motor Amp Rating 1.5Kw Spindle 7 amp )
PD142=( 220v Set for your motor Amps Rating 800w Spindle 4 amps )
PD142=( 120v Set for your motor Amp Rating 800w Spindle 7 amp )
PD143=2 ( Motor Number of Poles)
PD144=3000 (Max Motor RPM) =3,000= (24,000)
PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )
PD72=400
PD73=120 ( 100 Minimum Setting )