    Question 3.7KW Spindle problem

    Hello every body
    I am using a 3.7 KW 220V 400 Hz Chinese water cooled spindle to mill aluminium
    It worked fine for week and then I started to get some errors on my LS inverter VFD
    it started with a POT (output phase loss) and when I reset the inverter VFD it worked fine for while,
    then I started to get GFT (Ground Fault error) from time to time and then it got more frequent,
    I measured the ground terminal Current with an Ammeter and it reads zero all the time, now the spindle works for a minute or two then I get GFT error some times less than 5 secs

    I am frustrated since this is my second spindle in one month ( the first one came with a problem )

    Similar Threads:


  2. #2
    Member KH0UJ's Avatar
    Join Date
    Jul 2016
    Location
    Philippines
    Posts
    660
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    does it spin in manual mode?



  3. #3
    Member
    Join Date
    Mar 2017
    Location
    Egypt
    Posts
    35
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    it spins but the same issue happened



  4. #4
    Member
    Join Date
    Jun 2005
    Location
    USA
    Posts
    1723
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Sounds like the IBGT inside the VFD are going and will fail shortly. You might want to swap out the VFD before it fails and takes your spindle at the same time.

    Russ



  5. #5
    Member
    Join Date
    Mar 2017
    Location
    Egypt
    Posts
    35
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    I will try another VFD and tell u wht happened



  6. #6
    Member
    Join Date
    Mar 2017
    Location
    Egypt
    Posts
    35
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    I have just tried a new VFD with different brand, and it got me Over current ( the current measured and displayed on the VFD didnt exceed 4.5 amps)
    ???!!!!!!!!



  7. #7
    Member
    Join Date
    Jun 2005
    Location
    USA
    Posts
    1723
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Yasser47,
    You must have some parameters set wrong in the VFD, did the motor spin at all? Normally when you see issues like this it is caused due the settings in the VFD. User Mactec is a good resource when setting up parameters in a VFD. Are you using the standard Chinese spindle, 24000 RPM, etc.

    Russ



  8. #8
    Member
    Join Date
    Mar 2017
    Location
    Egypt
    Posts
    35
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Yes, The spindle rotates and cuts in the material for some time then it stops at completely random run positions, some times when contacting the material, and some time after it finish the cut, and sometimes when i just start it it fails, what parameter do i have to check?
    I am using
    GDZ spindle
    3.7KW
    220V 400 HZ
    24,000 RPM
    13 A



  9. #9
    Member
    Join Date
    Jun 2005
    Location
    USA
    Posts
    1723
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Yasser47,
    The first one I would check in the VFD is the voltage setting, the current settings, and the frequency settings. Then I would check the acceleration and deceleration and make sure they are at 2-3 seconds. Not sure which VFD you are using.
    Russ



  10. #10
    Member
    Join Date
    Mar 2017
    Location
    Egypt
    Posts
    35
    Downloads
    0
    Uploads
    0

    Default

    Output voltage 220 V
    Motor no load current 5.5 A
    Motor rated current 12.9 A
    Acc is 10 sec
    Dec is 20 sec
    Base freq 400

    Video of the problem
    https://youtu.be/7THCRCGuFPQ

    Last edited by Yasser47; 03-29-2017 at 03:09 PM.


  11. #11
    Member
    Join Date
    Jun 2005
    Location
    USA
    Posts
    1723
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Yasser47,
    Clearly some parameter is wrong in your VFD. That was very little load but it does sound like the frequency is set correctly. It looked like it was falling out at low amperage, appeared to be only 4amps or so. Let me see if I can find a typical parameter list you can compare against, clearly one is wrong. Kind of long acceleration and deceleration but that should be fine anyway. There is another parameter wrong, be careful not to do that to many times you don't want to damage the VFD.

    Russ



  12. #12
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Quote Originally Posted by Yasser47 View Post
    Output voltage 220 V
    Motor no load current 5.5 A
    Motor rated current 12.9 A
    Acc is 10 sec
    Dec is 20 sec
    Base freq 400

    Video of the problem
    With your first VFD it could be you spindle is not Grounded, this is why you have the fault, check the continuity of the spindle Ground Connection to the spindle body, you will have to correct this inside the spindle, and then you will be fine

    You will have to remove the top cap on the spindle to fix this Ground connection, blow all the water out before you remove the top cap

    Mactec54


  13. #13
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Quote Originally Posted by CNCMAN172 View Post
    Sounds like the IBGT inside the VFD are going and will fail shortly. You might want to swap out the VFD before it fails and takes your spindle at the same time.

    Russ
    This fault has nothing to do with the IBGT

    Mactec54


  14. #14
    Member
    Join Date
    Jun 2005
    Location
    USA
    Posts
    1723
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    mactec54,
    Yup it appeared to be acting up based on the various failure messages. He tried a new VFD out of the box and has the same errors, I am pretty sure he has a parameter set wrong, never seen the type of VFD he is using, but I am sure they have similar parameters. If you watch his video the frequency appears to be set correct, it spins right up, but as soon as the load hits maybe 4am it faults out.

    Russ



  15. #15
    Member
    Join Date
    Mar 2017
    Location
    Egypt
    Posts
    35
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Quote Originally Posted by mactec54 View Post
    With your first VFD it could be you spindle is not Grounded, this is why you have the fault, check the continuity of the spindle Ground Connection to the spindle body, you will have to correct this inside the spindle, and then you will be fine


    You will have to remove the top cap on the spindle to fix this Ground connection, blow all the water out before you remove the top cap

    I have checked the ground terminal and its connected to the spindle body physically and tested with a buzzer!!

    {GFT; Ground Fault error;The inverter turns off its output when a ground fault occurs and theground fault current is more than the internal setting value of theinverter.}



  16. #16
    Member
    Join Date
    Mar 2017
    Location
    Egypt
    Posts
    35
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Quote Originally Posted by CNCMAN172 View Post
    mactec54,
    Yup it appeared to be acting up based on the various failure messages. He tried a new VFD out of the box and has the same errors, I am pretty sure he has a parameter set wrong, never seen the type of VFD he is using, but I am sure they have similar parameters. If you watch his video the frequency appears to be set correct, it spins right up, but as soon as the load hits maybe 4am it faults out.

    Russ
    Sometimes the fault happens before it touches the materials, and some times it works for 5 mins of so and then suddenly I get the error, its independent to the load



  17. #17
    Member
    Join Date
    Jun 2005
    Location
    USA
    Posts
    1723
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Post the exact model of your VFD and/or a link to the manual. This must be a setting that is not getting configured correctly.
    Russ



  18. #18
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Quote Originally Posted by Yasser47 View Post
    Sometimes the fault happens before it touches the materials, and some times it works for 5 mins of so and then suddenly I get the error, its independent to the load
    What is the Name and model of the VFD Drive

    So the spindle Ground is correct then how is the Ground connection between the spindle and the VFD, and then the VFD Ground connected to the incoming Power supply Ground

    Take a close up photo of your VFD wiring

    Check your spindle Plug wiring

    Are you using shielded cable???

    Is the shield terminated correctly as photo below???

    Attached Thumbnails Attached Thumbnails 3.7KW Spindle problem-grounding-shields-3-png  
    Mactec54


  19. #19
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    Quote Originally Posted by CNCMAN172 View Post
    Post the exact model of your VFD and/or a link to the manual. This must be a setting that is not getting configured correctly.
    Russ

    No Parameter is going to fix a Grounding problem, he has a wiring problem

    Mactec54


  20. #20
    Member
    Join Date
    Jun 2005
    Location
    USA
    Posts
    1723
    Downloads
    0
    Uploads
    0

    Default Re: 3.7KW Spindle problem

    mactec54,
    Look at the video of his machine it appears to be a commercial type machine not a home grown cnc machine. It appears to be a VMC based on the video, so I would expect the commercial company would have used the correct cabling to the Spindle. However, it is a 24,000 RPM Chinese spindle so they might have changed the original spindle and put this high speed spindle in which required new cabling. Look at the video and you will see what I mean.
    Russ



Page 1 of 4 1234 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

3.7KW Spindle problem

3.7KW Spindle problem