003 could be set at 60, that is the start up speed, adjustable with the buttons or pot.
004 should be set to 60
142 seems a bit high, should be motor nameplate amps, around 3.2 - 3.6 or so for a 220V, 1HP, 3PH motor..
Hate to beat a dead horse, but.
I have a 2.2kw Huanyang vfd, or should I say a second one, toasted the first.I'm looking to use it on an industrial slicer. I wired the first one and set what I believed were the necessary parameters. Motor worked FWD/REV, stop, etc.
Onboard pot would not function. I only want to use this vfd to slow down the slicer. Parameters were set as follows:
PD000 lock 0
PD001 source 0
PD002 source 0
PD003 main freq ? can't remember, there is only an asterisk in manual, however if settable I used 60hz
PD004 base freq 60
PD005 max op freq 60
PD006 Interm. Freq 2.5
PD141 Motor Volts 220V
PD142 Current 15 FLA
PD143 Poles 4
PD144 RPM 1740
Motor: 1 hp Leeson 220V, 60hz, 3P, 4 pole, 1740 rpm
Jumper was set, I think, for the onboard pot. Pot would not function. Rpm was exceeding 1740 so I shut it down.
Set PD004, base freq to 0.01 and vfd made a loud unpleasant noise when run pressed. I would like not to hear that
noise again so any help would be appreciated.
Similar Threads:
- Huanyang VFD Troubleshooting
- Huanyang 7.5 kw VFD help
- Need Help!- Huanyang 2.2kW VFD.
- Huanyang VFD
- Need Help!- Huanyang VFD
003 could be set at 60, that is the start up speed, adjustable with the buttons or pot.
004 should be set to 60
142 seems a bit high, should be motor nameplate amps, around 3.2 - 3.6 or so for a 220V, 1HP, 3PH motor..
Don't confuse FLA with locked rotor amps or fuse amps.