    Hello,

    I'm attempting to fire up my Chinese 2.2kW spindle for the first time using a Hitachi WJ200 inverter. I've correctly wired the three phases and connected the spindle with a shielded cable (shielding earthed at one end only). The inverter seems to be correctly configured with input voltage/freq and current limit settings.

    When I hit start button, the spindle starts turning very slowly (5-10 rpm) and makes a strange buzzing sound. After about 5-20 secs, the inverter trips out with an over-current alarm.

    Any ideas? Does someone have a standard config for the WJ200 that I could look at?

    Regards, Richard

    Similar Threads:


  2. #2
    Member bill south's Avatar
    Join Date
    Apr 2005
    Location
    usa
    Posts
    1268
    Downloads
    0
    Uploads
    0

    Default

    Make sure that the inverter frequency is set for the 400 hz spindle. That would be my first guess.
    B

    billyjack
    Helicopter def. = Bunch of spare parts flying in close formation! USAF 1974 ;>)


  3. #3
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default

    Already checked. I've set min freq to 50hz and max to 400hz. I'm getting access to a cro tonight to have a look at the wave forms.



  4. #4
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default

    It now appears that the VFD is OK as I managed to connect a different 3 phase motor and it worked fine at 50hz.

    So it looks like I have a problem with the spindle. Any ideas as I don't think I'll get a refund (purchased it over 12 months ago). Anyone one had problems with the windings on these cheap Chinese ones?



  5. #5
    Registered
    Join Date
    Dec 2004
    Location
    USA
    Posts
    783
    Downloads
    0
    Uploads
    0

    Default

    I would take the rear cover off and check the connections. First thing I did to mine was replace the cheap Connector with something better. The rest of the spindle has been flawless for close to a year, no complaints...

    From tapatalk



  6. #6
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default

    Good thought, but I had already changed the plug before I started using it.



  7. #7
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default

    cnc3678

    I would say you have not set the VFD correct, were you have the 50hz setting this has to be 400hz too, there are other settings as well, but do this first, another one you will have to set the ramp up time & the ramp down time as well or it will trip out in over load

    Mactec54


  8. #8
    Registered
    Join Date
    Jun 2011
    Location
    Australia
    Posts
    72
    Downloads
    0
    Uploads
    0

    Default

    A growly noise and no rotation sounds like you could be losing a phase between the inverter and the spindle. Check the plug/socket on the top of the spindle - i suggest replacing them with an amphenol plug and socket, and connecting an earth while you have it open. If you have changed it already, then check that all three phase wires are connected (can to it as below without the cable).

    If you have a multimeter, disconnect the cable to the spindle motor at the inverter. On the cable (disconnected from inverter, so no power on it), measure resistance between 2 phases x3 and make sure the numbers are all consistent (they should be low numbers as it is only the resistance of the cable and the winding).

    Let me know the resistance results and we can go from there.

    Paul



  9. #9
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default

    Thanks Paul, I'm already using a new amphenol plug and socket but I will now open the spindle up again and double check everything. Good point about checking winding resistance to see if there is consistency across the three phases (I'm assuming the're wired in delta).

    Mactech54 - Thanks for your suggestion as well. Originally I had the inverter configured to run at 400Hz max, but the test motor is rated at 50Hz and hence the reason why I lowered the output frequency. The ramp up and down time is set for 10 secs and this worked fine on the other motor.

    Richard

    Last edited by cnc3678; 01-16-2013 at 06:38 PM.


  10. #10
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default

    cnc3678

    Your settings should look something like this

    A001- 00
    A002 – 02
    A004- 400HZ
    A003 – 400Hz is Spindle base frequency
    A061 – 400HZ
    A062 – 0
    A082 – 230V/240V
    A151- 0
    A152 – 400HZ
    A153 – 0
    A154 – 100
    A155 - 00
    B012 – 10 Amps of your spindle
    H003 – 2.2 KW this is your spindle kw rating
    H004 - 2 poles most of these spindles are only 2 pole

    Mactec54


  11. #11
    Registered
    Join Date
    Jun 2011
    Location
    Australia
    Posts
    72
    Downloads
    0
    Uploads
    0

    Default

    I've never really looked at the internal connection. Delta connection would be most obvious.

    I have a spindle open here and get about 1.6ohm between each pair of wires. This could vary an ohm or 2 depending on your leads lengths etc.

    Paul.



  12. #12
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default

    Thanks Mactec54, I'll compare these settings to mine and report back.

    Richard



  13. #13
    Registered
    Join Date
    Jun 2011
    Location
    Australia
    Posts
    72
    Downloads
    0
    Uploads
    0

    Default

    Just thought of something else to check. Is there a parameter in the inverter that sets how quickly the inverter accelerates to the required frequency. It may be accelerating too quickly for the spindle to keep up.

    Paul

    Last edited by bushwakka; 01-17-2013 at 03:46 AM. Reason: changed content


  14. #14
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default Found the problem!

    Thanks to Mactec54, I've found the problem and it came down to a single setting on the inverter.

    A003 – spindle base frequency was set to 50Hz and changing it to 400Hz fixed the problem. This is despite the manual suggesting that this 'base' value should be set to 50Hz or 60Hz as shown in the picture below. Hence setting the max frequency to 400 Hz (A004) wasn't enough and required the A003 base frequency to be set to this value as well.

    So I'm very relieved, but a little fustrated that I wasted a number of hours of testing and pulling down the spindle.

    Richard

    Attached Thumbnails Attached Thumbnails Problem with running Chinese 2.2kW spindle from Hitachi WJ200-hitachi_manual_snapshot-jpg  
    Last edited by cnc3678; 01-21-2013 at 05:01 AM.


  15. #15
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default

    cnc3678

    Your spindle base frequency is 400hz, so needed to be set to the 400hz

    The 3ph motor you tested the VFD with, had a base frequency of 50hz this would be the setting for that motor

    Mactec54


  16. #16
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default

    Mactec54,

    thanks again for your help. From your experience, what's the lowest frequency that these spindles will operate at without losing too much torque (or getting too hot)?

    Or is this a limitation of the inverter capability?

    Last edited by cnc3678; 01-21-2013 at 08:08 PM.


  17. #17
    Registered
    Join Date
    Dec 2004
    Location
    USA
    Posts
    783
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by cnc3678 View Post
    Mactec54,

    thanks again for your help. From your experience, what's the lowest frequency that these spindles will operate at without losing too much torque (or getting too hot)?

    Or is this a limitation of the inverter capability?
    The 8000-24000 rpm rating on the motor seems about right to me.

    From tapatalk



  18. #18
    Registered
    Join Date
    Jun 2011
    Location
    Australia
    Posts
    72
    Downloads
    0
    Uploads
    0

    Default

    In theory the torque should remain reasonably constant, but without an encoder feedback for the inverter, the torque drops away as frequency decreases.

    Power is proportional to Torque x angular velocity, so a 24000rpm rated spindle will be
    2.2kW @ 24000rpm
    1.1kW @ 12000rpm
    about 750W @ 8000rpm
    and dropping away to not much power at all below that.

    Cheers
    Paul



  19. #19
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default

    Another question.

    I'm using a Gecko G540 controller and have been able to use the 0-10v analog output to control the speed successfully on the inverter. However I'm keen to also control run/stop and can't figure out how to wire one of the Gecko's output's to the WJ200's input terminals? Can someone help?

    Many thanks



  20. #20
    Registered cnc3678's Avatar
    Join Date
    Aug 2011
    Location
    Australia
    Posts
    73
    Downloads
    0
    Uploads
    0

    Default

    Worked it out. Just needed to wire one of the g540 outputs to a 48v relay. On the relay side, I ran one of the wires to the WJ-200 digital input 1 and the other to ground. Then set A002 to 1 which switched the RUN control to the digital input.

    Works a treat.



Page 1 of 2 12 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Problem with running Chinese 2.2kW spindle from Hitachi WJ200

Problem with running Chinese 2.2kW spindle from Hitachi WJ200