Need Help! Problem with running Chinese 2.2kW spindle from Hitachi WJ200 - Page 2
Page 2 of 3 FirstFirst 123 LastLast
Results 13 to 24 of 31
Thread: Problem with running Chinese 2.2kW spindle from Hitachi WJ200
  1. #13
    Jun 2011
    Just thought of something else to check. Is there a parameter in the inverter that sets how quickly the inverter accelerates to the required frequency. It may be accelerating too quickly for the spindle to keep up.
    Paul
  2. #14
    Registered cnc3678's Avatar
    Aug 2011
    Default Found the problem!
    Thanks to Mactec54, I've found the problem and it came down to a single setting on the inverter.
    A003 – spindle base frequency was set to 50Hz and changing it to 400Hz fixed the problem. This is despite the manual suggesting that this 'base' value should be set to 50Hz or 60Hz as shown in the picture below. Hence setting the max frequency to 400 Hz (A004) wasn't enough and required the A003 base frequency to be set to this value as well.
    So I'm very relieved, but a little fustrated that I wasted a number of hours of testing and pulling down the spindle.
    Richard
    Attached Thumbnails Attached Thumbnails Problem with running Chinese 2.2kW spindle from Hitachi WJ200-hitachi_manual_snapshot-jpg
  3. #15
    Gold Member
    Jan 2005
    cnc3678
    Your spindle base frequency is 400hz, so needed to be set to the 400hz
    The 3ph motor you tested the VFD with, had a base frequency of 50hz this would be the setting for that motor
    Mactec54
  4. #16
    Aug 2011
    Mactec54,
    thanks again for your help. From your experience, what's the lowest frequency that these spindles will operate at without losing too much torque (or getting too hot)?
    Or is this a limitation of the inverter capability?
  5. #17
    Dec 2004
    Quote Originally Posted by cnc3678 View Post
    Mactec54,
    The 8000-24000 rpm rating on the motor seems about right to me.
    From tapatalk
  6. #18
    Jun 2011
    In theory the torque should remain reasonably constant, but without an encoder feedback for the inverter, the torque drops away as frequency decreases.
    Power is proportional to Torque x angular velocity, so a 24000rpm rated spindle will be
    2.2kW @ 24000rpm
    1.1kW @ 12000rpm
    about 750W @ 8000rpm
    and dropping away to not much power at all below that.
    Cheers
    Paul
  7. #19
    Aug 2011
    Another question.
    I'm using a Gecko G540 controller and have been able to use the 0-10v analog output to control the speed successfully on the inverter. However I'm keen to also control run/stop and can't figure out how to wire one of the Gecko's output's to the WJ200's input terminals? Can someone help?
    Many thanks
  8. #20
    Aug 2011
    Worked it out. Just needed to wire one of the g540 outputs to a 48v relay. On the relay side, I ran one of the wires to the WJ-200 digital input 1 and the other to ground. Then set A002 to 1 which switched the RUN control to the digital input.
    Works a treat.
  9. #21
    May 2012
    cnc3678
    Your settings should look something like this
    A001- 00
    A002 – 02
    A004- 400HZ
    A003 – 400Hz is Spindle base frequency
    A061 – 400HZ
    A062 – 0
    A082 – 230V/240V
    A151- 0
    A152 – 400HZ
    A153 – 0
    A154 – 100
    A155 - 00
    B012 – 10 Amps of your spindle
    H003 – 2.2 KW this is your spindle kw rating
    H004 - 2 poles most of these spindles are only 2 pole
    Just to reconfirm; these settings looks like for the X200 and not the WJ200?
    As i am currently looking at the WJ200 Manual and A151/2/3 are all % 0 to 50% range.
    Been trying to setup WJ200 with 300Hz 3KW (10A) Spindle and i am almost sure i am missing few settings. Anyone can post the minimum settings required to be changed for WJ200?!
    Thanx.
  10. #22
    Aug 2011
    Raider,
    Here are absolute minimum settings on the WJ-200 for my 400Hz 2.2kW spindle. It assumes that you are manually running the spindle from the control panel (ie not from an external source). Change the various max freqs back to 300Hz if this is the limit of your spindle.
    1. Select the digital operator as the source of motor speed command (A001=02). Also set the run-time motor speed with F001 (say 400Hz).
    2. Select the digital operator as the source of the RUN command (A002=02).
    3. Set the motor base & max frequency (A003=400Hz, A004=400Hz) and AVR voltage of the motor (A082=240V).
    4. Set the motor current for proper thermal protection (B012=your spindle's max rated current, mine is 9A).
    5. Set the number of poles for the motor (H004=2).
    Spindle should then power up when you hit the 'START' button. Don't forget to set the 'F001' starting frequency as the motor won't move without this.
  11. #23
    May 2012
    Thank you.
    Guess i need to open the Spindle and inspect it. It runs fine from 0 Hz to 45Hz, when i try to speed it up more, Error 30 (Only when the spindle connected); When trying the spindle on another VFD; it shows output is shorted after 10Hz.
  12. #24
    Gold Member
    Sep 2010
    A044=0 for v/hz mode (default). I assume that is what u r using since it makes no sense to use any other mode for a 400hz base speed motor.
    that said, NO H SERIES PARAMETER HAS ANY MEANING
    H parameters r only used in vector mode. u dont want that mode.
    so forget any H parameters - they do nothing.
    min params are base freq, base voltage, Motor current rating if different than default, and max speed freq.