Huanyang Chinese VFD settings and manual here! - Page 21


Page 21 of 41 FirstFirst ... 111819202122232431 ... LastLast
Results 401 to 420 of 808

Thread: Huanyang Chinese VFD settings and manual here!

  1. #401
    Member Azalin's Avatar
    Join Date
    Mar 2014
    Location
    Turkey
    Posts
    1131
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hi again,

    Motor runs fine for a short time then starting to shake. The best I could achieve is by using the high torque curve (the lower right curve on the attached image). I also played with Carrier Frequency for smoother run but nothing changed.

    I also have a Siemens Sinamics V20 3kw inverter that I'm using for my cnc router. I'll pull it out and make a test with the motor. If it runs fine then I'll buy another Sinamics. If not then I'll buy a 6 pole 1000 RPM motor. But I think the working duty of the motor must be S3 for the job. The motor I have is S1 rated which means "start once, run for long periods".



    Attached Thumbnails Attached Thumbnails Huanyang Chinese VFD settings and manual here!-torque_curves-jpg  
    Suat
    Proud father, C# developer, Model heli pilot, newbie free time machinist for hobby


  2. #402
    Member Azalin's Avatar
    Join Date
    Mar 2014
    Location
    Turkey
    Posts
    1131
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    By the way mactec54,

    The manual that came with my Huanyang as a parameter set for frequency skipping. It allows you to setup multiple frequency ranges. I don't remember the parameter numbers but let me know if you want them.

    Suat
    Proud father, C# developer, Model heli pilot, newbie free time machinist for hobby


  3. #403
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Azalin View Post
    By the way mactec54,

    The manual that came with my Huanyang as a parameter set for frequency skipping. It allows you to setup multiple frequency ranges. I don't remember the parameter numbers but let me know if you want them.
    I have the Skip Frequency Parameters, what I meant was not all the cheaper Drives have these Parameters to set, but what you are seeing should not be happening at 50Hz it should be smooth and quiet just as it is at 20Hz

    Your motor is very noisy at 50Hz it should be quiet at those settings, something is not set correct or the VFD is doing a really bad job, I don't think you would want a 6 pole motor, it would run too slow for your need

    Swap the output wires around, it may run in reverse, of what you want, but sometimes this can have an effect on a motor driven by a VFD

    Do you have good Grounding, motor to the VFD and Input power supply to the VFD

    Mactec54


  4. #404
    Member Azalin's Avatar
    Join Date
    Mar 2014
    Location
    Turkey
    Posts
    1131
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Yes, I swapped the wires. The cable from VFD to the motor is 4x2.5mm^2 shielded. Grounding is as as it should be.

    As I said I'll try my other VFD and see how it works with the motor. I don't know what else I can try.

    Suat
    Proud father, C# developer, Model heli pilot, newbie free time machinist for hobby


  5. #405
    Member Azalin's Avatar
    Join Date
    Mar 2014
    Location
    Turkey
    Posts
    1131
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Look, I have a walking motor. No need to walk it twice a day.



    Suat
    Proud father, C# developer, Model heli pilot, newbie free time machinist for hobby


  6. #406
    Member Azalin's Avatar
    Join Date
    Mar 2014
    Location
    Turkey
    Posts
    1131
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    New motor. Works fine.



    Suat
    Proud father, C# developer, Model heli pilot, newbie free time machinist for hobby


  7. #407
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by Azalin View Post
    New motor. Works fine.

    You can take it up to 80Hz if it is happy at that go up to 100Hz

    Mactec54


  8. #408
    Member
    Join Date
    Dec 2014
    Location
    United States
    Posts
    46
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    I have been having the Huanyang blues,

    I have tried for two days to get the VFD to work with Mach3 no luck.

    Now I am trying to reset the factory settings I have tried several time to set PD0013 to 8 and factory setting won't restore

    Any help is appreciated



  9. #409
    Member Azalin's Avatar
    Join Date
    Mar 2014
    Location
    Turkey
    Posts
    1131
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Factory reset is PD013 = 01 on some versions.

    Suat
    Proud father, C# developer, Model heli pilot, newbie free time machinist for hobby


  10. #410
    Member
    Join Date
    Dec 2014
    Location
    United States
    Posts
    46
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Thanks Got it reset, it now can control with the panel arrow keys but not the pot on the panel any advice on the pot?

    Thanks



  11. #411
    Member ger21's Avatar
    Join Date
    Mar 2003
    Location
    Shelby Township
    Posts
    35538
    Downloads
    1
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Make sure the jumper is on pins 2-3.

    I wouldn't recommend running with the default parameters, unless you are 100% certain that they are correct for your spindle.

    Gerry

    UCCNC 2017 Screenset
    [URL]http://www.thecncwoodworker.com/2017.html[/URL]

    Mach3 2010 Screenset
    [URL]http://www.thecncwoodworker.com/2010.html[/URL]

    JointCAM - CNC Dovetails & Box Joints
    [URL]http://www.g-forcecnc.com/jointcam.html[/URL]

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)


  12. #412
    Registered
    Join Date
    Sep 2017
    Location
    Belgium
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Hello,

    I receive my VFD and spindle few days ago and I have some problem to set it up.

    All wire have been check twice but when I put more than 100Hz, the spindle stop and and I have the following error message : E.LU.A
    According to manual, it's a low voltage problem but no idea where it could from.

    VFD is a HuanYang HY02D223B (2.2KW) and the spindle is HuanJiang 0.8KW water cooled.

    Does someone has any idea of the problem?



  13. #413
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by davels View Post
    Hello,

    I receive my VFD and spindle few days ago and I have some problem to set it up.

    All wire have been check twice but when I put more than 100Hz, the spindle stop and and I have the following error message : E.LU.A
    According to manual, it's a low voltage problem but no idea where it could from.

    VFD is a HuanYang HY02D223B (2.2KW) and the spindle is HuanJiang 0.8KW water cooled.

    Does someone has any idea of the problem?
    What terminals do you have wired for the input power supply to the VFD, and have you checked the Ground / Earth wire connection in the spindle motor ( Pin 4 )

    Mactec54


  14. #414
    Registered
    Join Date
    Sep 2017
    Location
    Belgium
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    What terminals do you have wired for the input power supply to the VFD, and have you checked the Ground / Earth wire connection in the spindle motor ( Pin 4 )
    I wired R & T (I'm in Belgium, 240V). How can I check the Earth? I wired Earth to VFD and VFD to spindle. (See picture below)



    Attached Thumbnails Attached Thumbnails Huanyang Chinese VFD settings and manual here!-20170913_014112-96-jpg  


  15. #415
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by davels View Post
    I wired R & T (I'm in Belgium, 240V). How can I check the Earth? I wired Earth to VFD and VFD to spindle. (See picture below
    Your Hot wire ( Phase ) is Brown if this is the case then your Brown wire needs to be on the ( R Terminal ) and the Blue wire ( Null ) on the T terminal

    You check the spindle Earth wire, with a meter, check the Pin 4 to the Body of the Spindle, if this is not connected it also needs connecting inside the cap so the spindle is Earthed

    Mactec54


  16. #416
    Registered
    Join Date
    Sep 2017
    Location
    Belgium
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    Your Hot wire ( Phase ) is Brown if this is the case then your Brown wire needs to be on the ( R Terminal ) and the Blue wire ( Null ) on the T terminal

    You check the spindle Earth wire, with a meter, check the Pin 4 to the Body of the Spindle, if this is not connected it also needs connecting inside the cap so the spindle is Earthed
    I try to switch wire but it doesn't change anything.

    Well, I have try to check Earth with a multimeter but not sure I did it well. On the multimeter, I have to set V-... and not ~, it's right?



  17. #417
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by davels View Post
    I try to switch wire but it doesn't change anything.

    Well, I have try to check Earth with a multimeter but not sure I did it well. On the multimeter, I have to set V-... and not ~, it's right?
    No it most likely did not change anything, but this is the correct way to have it wired, disconnect the spindle and see if you still get a low voltage Fault

    What parameters do you have set in the VFD Drive

    Yes you use your multimeter, and do a continuity check

    Mactec54


  18. #418
    Registered
    Join Date
    Sep 2017
    Location
    Belgium
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    No it most likely did not change anything, but this is the correct way to have it wired, disconnect the spindle and see if you still get a low voltage Fault

    What parameters do you have set in the VFD Drive

    Yes you use your multimeter, and do a continuity check
    The seller ask me to set the following parameters :
    • PD005 = 400
    • PD004 = 400
    • PD003 = 400
    • PD072 = 400
    • PD144 = 3000


    As the VFD is 2.2KW and spindle is 0.8KW, don't I have to set it in the VFD?

    I'm sorry but my knowledge in electricity is near zero.. :/
    So I check the ground between Pin 4 and the body spindle in direct current. I got random numbers changing all the time. But is it direct or alternating ?



  19. #419
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by davels View Post
    The seller ask me to set the following parameters :
    • PD005 = 400
    • PD004 = 400
    • PD003 = 400
    • PD072 = 400
    • PD144 = 3000


    As the VFD is 2.2KW and spindle is 0.8KW, don't I have to set it in the VFD?

    I'm sorry but my knowledge in electricity is near zero.. :/
    So I check the ground between Pin 4 and the body spindle in direct current. I got random numbers changing all the time. But is it direct or alternating ?
    The best way for you to see how to use your multimeter for continuity test is YouTube

    Ok there are more parameters that need to set, this list will help, what they gave you are some of the main important Parameters

    Huanyang Mactec54

    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock

    PD001=0 (1 For Remote Control)

    PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control ) ( J1 Also Needs to be set for Terminal Control )

    PD003=400

    PD004=400

    PD005=400

    PD007=20

    PD008=220 (Motor Rated Voltage )

    PD009=15

    PD010=8

    PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014 Acceleration=12 ( Adjust to suit)

    PD015 Deceleration=12 (Adjust to suit)

    ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD141=220 ( Motor Rated Voltage )

    PD142= 4 ( Motor Amp Rating ) " Check your Spindle Motor Rated Amps that's What this Should Be Set To "

    PD143=2 ( Motor Number of Poles)

    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )

    PD72=400

    PD73=120 ( 100 Minimum Setting )

    Mactec54


  20. #420
    Registered
    Join Date
    Sep 2017
    Location
    Belgium
    Posts
    8
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by mactec54 View Post
    The best way for you to see how to use your multimeter for continuity test is YouTube

    Ok there are more parameters that need to set, this list will help, what they gave you are some of the main important Parameters

    Huanyang Mactec54

    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock

    PD001=0 (1 For Remote Control)

    ...

    PD72=400

    PD73=120 ( 100 Minimum Setting )
    I just set all these parameters but nothing change. The spindle start faster but this time stop earlier too.

    I have check continuity between ground and spindle body but not beep. Is it normal?



Page 21 of 41 FirstFirst ... 111819202122232431 ... LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Huanyang Chinese VFD settings and manual here!

Huanyang Chinese VFD settings and manual here!