Huanyang Chinese VFD settings and manual here! - Page 31


Page 31 of 41 FirstFirst ... 2128293031323334 ... LastLast
Results 601 to 620 of 808

Thread: Huanyang Chinese VFD settings and manual here!

  1. #601
    Member
    Join Date
    Feb 2012
    Location
    US
    Posts
    43
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Got it, thanks man!!



  2. #602
    Member
    Join Date
    Feb 2012
    Location
    US
    Posts
    43
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Ok, got most of everything input as suggested except I hit one single snag.
    In your instructions, P11.01 is to be 110, and in the instruction booklet included with the VFD, this falls under "output voltage" but when I click on that section, my options are 0,1,2, or 3..
    One again, China throws a wrench in it. ????
    Otherwise all other settings are programmed in.
    Thanks for any and all help!



  3. #603
    Member
    Join Date
    Feb 2012
    Location
    US
    Posts
    43
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Ok, scouring the net I found this link to a yl620-a vfd programming guide I think.
    Apparently voltage is supposed to stay at 0. (?)

    Link:
    https://www.google.com/url?q=http://...3GhyzVAb9__CrS



  4. #604
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by SpyderHelix View Post
    Ok, scouring the net I found this link to a yl620-a vfd programming guide I think.
    Apparently voltage is supposed to stay at 0. (?)

    Link:
    https://www.google.com/url?q=http://...3GhyzVAb9__CrS

    The PDF is incorrect the very first Parameter tells you that this wrong 60Hz

    No you need to set the Parameters that I have given you I will look at the P11 it may not even be needed

    Mactec54


  5. #605
    Member
    Join Date
    Feb 2012
    Location
    US
    Posts
    43
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    So the main frequency isn't the input power frequency? (Not arguing, trying to learn)
    In the US that's 60hz isn't it? (I know nothing of power frequencies, just voltage.. This is way above my paygrade lol)



  6. #606
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Ok looked at it does not give an explanation of what 1 2 3 means so just leave it at 0 and if it all runs ok then it is a Parameter that is not needed for your operation

    Mactec54


  7. #607
    Member
    Join Date
    Feb 2012
    Location
    US
    Posts
    43
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by mactec54 View Post
    Ok looked at it does not give an explanation of what 1 2 3 means so just leave it at 0 and if it all runs ok then it is a Parameter that is not needed for your operation
    Aye sir! Will do



  8. #608
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by SpyderHelix View Post
    So the main frequency isn't the input power frequency? (Not arguing, trying to learn)
    In the US that's 60hz isn't it? (I know nothing of power frequencies, just voltage.. This is way above my paygrade lol)
    No not at all, the supply frequency has nothing to do with what type of motor you are driving, Regluar Ac motor or Spindle a regular 3Ph Ac motor would run and may be programed using 60Hz but normally different numbers are used depending on what speed you want to run it at , your spindle is 400hz so if you try and run it set at 60hz then most times the smoke come out before you have time to turn it off

    Mactec54


  9. #609
    Member
    Join Date
    Feb 2012
    Location
    US
    Posts
    43
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Got it, thank you sir! This should be the last time I bug you lol



  10. #610
    Member
    Join Date
    Feb 2012
    Location
    US
    Posts
    43
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Plugged in, turned on and pressed go - no magic smoke and spindle ran up pretty good. Not sure if I'm getting 24,000 rpm (no tach) but it sounds pretty good! Much faster than when I tested it before.
    Thanks for all the help mactech!



  11. #611
    Member
    Join Date
    Apr 2005
    Location
    usa
    Posts
    23
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Huanyang Chinese VFD settings and manual here!-img_4497-2-jpg


    Huanyang Chinese VFD settings and manual here!-img_4034-jpg

    I have been working on a new CNC lathe build. Have a spindle setup from and old pneumatic controlled lathe.

    I have had problems with getting the Haun Yang VFD working with the Baldor 5HP motor.

    Motor was set to high voltage mode and I rewired for low voltage mode. The motor has a Brake and Clutch, runs the lathe spindle through v belts

    With the VFD the motor spins but when the clutch is turned on the lathe spindle spins a second or so then the VFD errors with E.OC.n

    Error is over current so I wonder if the VFD is too small. It is the 5HP one advertised to run a 5HP motor

    Baldor motor 5HP

    208-230 volts
    15-13.2 amps
    rpm 1725
    hz 60
    3 phase

    I was hoping to be able to set it to the optimal programmed parameters. Would someone post a set of parameters for this specific motor? I have it set up with the set of parameters from page 10 of this thread.

    How do I know if the VFD is too small for the motor.

    Huan Yang VFD model:
    HY04D023B
    3PH 0~220AC 4.0KW 18A 0.50-400.00HZ

    Last edited by minitech cnc; 05-03-2019 at 08:13 PM.


  12. #612
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by minitech cnc View Post
    Huanyang Chinese VFD settings and manual here!-img_4497-2-jpg


    Huanyang Chinese VFD settings and manual here!-img_4034-jpg

    I have been working on a new CNC lathe build. Have a spindle setup from and old pneumatic controlled lathe.

    I have had problems with getting the Haun Yang VFD working with the Baldor 5HP motor.

    Motor was set to high voltage mode and I rewired for low voltage mode. The motor has a Brake and Clutch, runs the lathe spindle through v belts

    With the VFD the motor spins but when the clutch is turned on the lathe spindle spins a second or so then the VFD errors with E.OC.n

    Error is over current so I wonder if the VFD is too small. It is the 5HP one advertised to run a 5HP motor

    Baldor motor 5HP

    208-230 volts
    15-13.2 amps
    rpm 1725
    hz 60
    3 phase

    I was hoping to be able to set it to the optimal programmed parameters. Would someone post a set of parameters for this specific motor? I have it set up with the set of parameters from page 10 of this thread.

    How do I know if the VFD is too small for the motor.

    Huan Yang VFD model:
    HY04D023B
    3PH 0~220AC 4.0KW 18A 0.50-400.00HZ

    There could be different Parameters needed than what is on page 10 that should be close but may need some changes for yours

    Can you post a photo of the VFD Drives Terminals and how do you have the input power connected ???

    Are you using Single Phase or 3 Phase Power Supply???

    For a lathe there is a lot of inertia so a VFD should be sized the minimum of 2 Hp bigger than the motor rating you also want a Braking Resistor

    For any VFD that is not rated for Single Phase then they need to have a Hp rating higher then the motor/spindle they are driving

    Mactec54


  13. #613
    Member
    Join Date
    Apr 2005
    Location
    usa
    Posts
    23
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    It is single phase 220 through the VFD to three phase

    VFD is rated for single phase

    Huanyang Chinese VFD settings and manual here!-img_4500-jpg

    Thank you very much for the help!



  14. #614
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Here is a Parameter list for your motor, I may change some of the settings once you get it running

    Need to Know your wiring configuration??? Photo is needed

    Mactec54
    60Hz 230v 5Hp Ac 3Ph Motor

    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock ( Must be 0 to do a Reset )

    PD001=0 (1 For Remote Control)

    PD002=0

    PD003=100

    PD004=100

    PD005=100

    PD006=50

    PD007=20

    PD008=230

    PD009=115

    PD010=9

    PD011=40 (Minimum Setting Speed )

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014=15 ( Adjust to suit Acceleration )

    PD015=15 (Adjust to suit Deceleration )

    PD141=230 ( Motor Rated Voltage )

    PD142=13 ( Motor Max Amps)

    PD143=4 ( Motor Number of Poles)

    PD144=3000 (Max Motor RPM)

    For Remote Pot use

    PD002=1

    PD70=0

    PD72=100

    PD73=40

    Mactec54


  15. #615
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by minitech cnc View Post
    It is single phase 220 through the VFD to three phase

    VFD is rated for single phase

    Huanyang Chinese VFD settings and manual here!-img_4500-jpg

    Thank you very much for the help!
    Your power supply is 240v, not 220v

    So Ground is Green

    You need to connect the R Hot wire and T Hot wire terminals for the Input Power supply and you need to cover the White wire at both ends, Black or Red it can not be White as White is for Neutral

    You have Terminals R S T input for this VFD only connect R and T and Ground

    Mactec54


  16. #616
    Member
    Join Date
    Apr 2005
    Location
    usa
    Posts
    23
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Huanyang Chinese VFD settings and manual here!-img_4501-jpg

    Ok moved the "S" to "T" and now ground "R" and "T" are connected.

    Wire configuration is 220 volt single phase coming from house supply, it has a ground and two hot wires only, no fourth wire. I put that to a breaker box with all 3 going through separate 15 amp fuses, ground is grounded before the fuse to the machine. From there to a non fuse on off switch that was on the machine when I got it. From that to the VFD

    From VFD to the Baldor 5HP motor 3 wires with the motor wired as low power per the motor tag.


    I put in the parameters after changing to R and T. The VFD starts and says F100.0. Push run and the motor spools up but then dies when the clutch is powered on.

    The spindle on the lathe moved freely by hand so the load on the start up doesn't seem like it is high.

    The VFD was new when I got it and I only changed parameters that are on this thread. Should I do a factory reset and start over?

    Last edited by minitech cnc; 05-04-2019 at 09:54 AM.


  17. #617
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by minitech cnc View Post
    Huanyang Chinese VFD settings and manual here!-img_4501-jpg

    Ok moved the "S" to "T" and now ground "R" and "T" are connected.

    Wire configuration is 220 volt single phase coming from house supply, it has a ground and two hot wires only, no fourth wire. I put that to a breaker box with all 3 going through separate 15 amp fuses, ground is grounded before the fuse to the machine. From there to a non fuse on off switch that was on the machine when I got it. From that to the VFD

    From VFD to the Baldor 5HP motor 3 wires with the motor wired as low power per the motor tag.


    I put in the parameters after changing to R and T. The VFD starts and says F100.0. Push run and the motor spools up but then dies when the clutch is powered on.

    The spindle on the lathe moved freely by hand so the load on the start up doesn't seem like it is high.

    The VFD was new when I got it and I only changed parameters that are on this thread. Should I do a factory reset and start over?
    Ok do these changes and this will just make it as a standard 60Hz 3Ph motor it is

    A Reset is only needed if you did other changes before that could be affecting how it is running now if you only set the Parameters I list then you would not have to do a Reset

    Recheck the motor Low Voltage wire connections are correct


    Your Power supply is 240V for NA not 220v yours may read 220v because you supply is low but the NA supply is 240v


    Do you have a Ground from the motor to the VFD Drive Ground ???


    Huanyang Mactec54
    PD000=0 ( For Parameter unlock ( 1 ) for Parameter Lock )

    PD001=0 (1 For Remote Control)

    PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )
    ( J1 Also May Need to be set for Terminal Control )
    PD003=60

    PD004=60

    PD005=60

    PD006=15

    PD007=5

    PD008=230 (Motor Rated Voltage )

    PD009=15

    PD010=8

    PD011=60

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014=15 ( Adjust to suit)

    PD015=15 (Adjust to suit)
    ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD141=230 ( Motor Rated Voltage )

    PD142= 13 ( Motor Max Rated Amps)

    PD143=4 ( Motor Number of Poles)

    PD144=1725 ( Max motor Speed ) ( 3000 Can be used )

    PD72=60

    PD73=60

    Last edited by mactec54; 05-04-2019 at 10:42 AM.
    Mactec54


  18. #618
    Member
    Join Date
    Apr 2005
    Location
    usa
    Posts
    23
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Ok did that.

    Screen flashes F60.00 and it does spool up and turn but again with clutch powered it spins for a second and gives the E.OC.n error.

    Also the pot on the front panel doesn't do anything, can't adjust the frequency with it anymore. (Did it with the last set of parameters too)

    The whole machine frame is grounded with same earth ground and the motor is bolted to it. I could run a specific ground to the motor.

    Just checked the motor low power wiring and it is intact.

    And again, thank you very much for working this through with me



  19. #619
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by minitech cnc View Post
    Ok did that.

    Screen flashes F60.00 and it does spool up and turn but again with clutch powered it spins for a second and gives the E.OC.n error.

    Also the pot on the front panel doesn't do anything, can't adjust the frequency with it anymore. (Did it with the last set of parameters too)
    The Pot is a separate setting, when everything is set at 60Hz it won't change any speeds this was just a test to see if you could run it or not with a basic setting

    How was it being run before or is this a new install for you


    How much supply Amps do you have you will need around 35A to 40A

    Something you could try put a meter on the input power supply and read what the power drop is when you engage the clutch

    Attached Thumbnails Attached Thumbnails Huanyang Chinese VFD settings and manual here!-eoc-n-drive-fault-png  
    Mactec54


  20. #620
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Huanyang Chinese VFD settings and manual here!

    Quote Originally Posted by minitech cnc View Post
    Ok did that.

    Screen flashes F60.00 and it does spool up and turn but again with clutch powered it spins for a second and gives the E.OC.n error.

    Also the pot on the front panel doesn't do anything, can't adjust the frequency with it anymore. (Did it with the last set of parameters too)

    The whole machine frame is grounded with same earth ground and the motor is bolted to it. I could run a specific ground to the motor.

    Just checked the motor low power wiring and it is intact.

    And again, thank you very much for working this through with me
    There still should always have a motor Ground wire connected either as at a star Ground point or directly with the Main supply Ground

    Mactec54


Page 31 of 41 FirstFirst ... 2128293031323334 ... LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Huanyang Chinese VFD settings and manual here!

Huanyang Chinese VFD settings and manual here!