F04 is telling u the resolver is not wired correctly; are u going into the right fdbk connector? there are 3 to choose from.... resolver is X2 is for resolver. if u dont have resistance (20-100 ohms say) between pins 4&8 and also 3&7 u will get F04 if resolver picked in software...
likewise if resistance is not close to 0 ohms between pins 2&6 for thermistat then you will get F06.
i strongly suspect u r plugged into X5 instead of X2... x2 is 2nd from BACK on top; x5 is second from FRONT.... also I bleieve x2 is female and x5 is male as u state....
s300/600 are good drives that work well but if u r starting out new for new equipment consider the new AKD drive instead; it will increase ur performance probably 30% over the older s300/600 series - which are still probably 15-30% higher performance than most other equivalent servo drives IMHO too. unless u r using the macro interface then u gotta use the s300/600/700(newer and higher performance than the s300) series. even so, consider using the new ethernet/IP delta tau output into the new akd for top of the line and probably lower cost performance.....