Fire in the Vacuum System

Another note today on safety.

I have had fire in my dust collector.
The problem was in my material. It was a laminated panel with spruce on the face and multiple plywood layers beneath. The spruce cut nicely so I just let it go. Wether it was the plywood or the adhesive, a hidden staple, I don't know. The vacuum system and hood I made was set to 1/16" from the surface (based on min Z) so no smoke was visible.
The only warning I had was because I was recircurlating air due to outside temperature. Normally I blow the stuff (and the noise) right outside.
All the more incentive to move the blowers (and the 80+ db) to a metal outside shed!

Not really sure how to prevent this, am I alone on this?
Tweet this Post!Share on Facebook
Reply With Quote

  #2   Ban this user!
Old 10-31-2007, 12:22 PM
 
Join Date: Jun 2003
Posts: 1,984
turmite is on a distinguished road
bluejay the commerical units have a detection system and a built in sprinkler system that will mist the dust if a spark is detected. Might be a little messy, but it sure is a lot better than a fire!

Mike
__________________
No greater love can a man have than this, that he give his life for a friend.
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 11-06-2007, 10:08 AM
 
Join Date: Mar 2007
Location: Canada
Posts: 37
bluejay_ca is on a distinguished road
Thanks for the inspiration. Not sure what the best detection means is. I simply used a temp controller mounted on the top of the tank. Before it melts the valve should open and dump 1 gallon of water through a spray nozzle. P.S. please don't laugh, I didn't have an enclosure and it had to be working before I could finish a current routing project.
I brought a 1/4" line into my cnc cabinet to monitor vacuum but the levels are so low I'm having a hard time with it. Anyone seen a sensor which will work in the 1-5 range. Air flow is critical to me because I have removed my router's fan and rely on the vacuum for cooling. Maybe a mechanical flow switch would be better hmmmm.
Attached Thumbnails
Click image for larger version

Name:	vacuum.jpg‎
Views:	183
Size:	122.1 KB
ID:	46409  
Tweet this Post!Share on Facebook
Reply With Quote

  #4   Ban this user!
Old 11-06-2007, 10:41 AM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,419
Geof will become famous soon enough
For your sprayer heads you could look into the heads used in building sprinkler systems. One style is fully pressurized all the time and has a fusible block that melts at a low temperature to automatically start the flow. If you have a water tank pressurized from an air tank then your system will work even if the electricity has been cut.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 11-06-2007, 10:53 AM
 
Join Date: Jan 2006
Location: USA
Posts: 1,490
keebler303 is on a distinguished road
A sprinkler head would be fine, they dump several gallons a minute in a normal system. I don't think its necessary to use air to pressurize the water, after all, if the electricity is cut, the router nor the dust collector will be running.

Matt
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 11-06-2007, 11:14 AM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,419
Geof will become famous soon enough
Originally Posted by keebler303 View Post
A sprinkler head would be fine, they dump several gallons a minute in a normal system. I don't think its necessary to use air to pressurize the water, after all, if the electricity is cut, the router nor the dust collector will be running.

Matt
If the electricity is cut as a result of the fire due to short circuit opening a breaker it could be a problem. I am a believer in overkill and also Murphy's law .

I suppose having watched a fire that started in a dust collector system go from the first spark to flames several stories high through the roof in about 20 minutes my view is a bit biased.

Actually you don't need a separate air tank you can get water tanks with a rubber bladder separating air on one side and water on the other that are used with well pumps. I think Home Depot has them.

I also forgot to mention in my suggestion that a foam system rather than straight water may be better. You can get better fire suppression with a lot less water.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 11-06-2007, 11:34 AM
ImanCarrot's Avatar  
Join Date: Nov 2005
Location: UK
Posts: 1,468
ImanCarrot is on a distinguished road
Isn't there a real risk of explosion with dusts? I recal sometime ago an issue with flour and air dust which exploded quite violently.
__________________
I love deadlines- I like the whooshing sound they make as they fly by.
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 11-06-2007, 11:49 AM
Bubba's Avatar  
Join Date: Mar 2004
Location: LaGrange, GA USA
Posts: 1,303
Bubba is on a distinguished road
The detection systems used in an application like this are usually based on either IR and/or UV (with IR being the preferred one). Be prepared to spend big bucks for the detection system. The sprinklers are usually OPEN head controlled by a valve. The problem with temp setting is the particles (read fire) is traveling at a high rate of speed. Therefore, the ductwork and the collector are usually protected. Sometimes, only the collector is protected due to the high velocity of the particles and the problems associated with the weight of the water in the duct works.
A standard 1/2" orifice sprinkler head will put out about 15 gpm at a pressure of 7 psi at the head!
Yes, foam has been used, but again the equipment to make it work is expensive along with the maintenance required for such a system. Other problems associated with it include:
Protein foam STINKS and after a time if not circulated, will gel up like concrete.
AFFF foam in most cases is now classified as a hazardous material as it contains 1% carbobutal (sp?) and must be dispossed of carfully. Non hazardous foam is available, but very expensive and also requires annual quality testing.
HI-expansion foam, well again the costs are going to be quite high.
Other things to be aware of are other governmental regulations about license requirements for designers of the system, installer, annual inspections, backflow prevention, etc.
For a small home system like we are talking here, best would be just a sprinkler in the dust collector controlled by a valve (most likely a manual ball valve) and some form of tempratue detection in the collector. Some might think a smoke detector will work, but many of them will false trip in dusty conditions.

Sorry to put a damper on some good ideas, but these are the facts of life.
__________________
Art
AKA Country Bubba (Older Than Dirt)
Tweet this Post!Share on Facebook
Reply With Quote

  #9   Ban this user!
Old 11-06-2007, 01:34 PM
 
Join Date: Jul 2004
Location: Canada
Posts: 601
DSL PWR is on a distinguished road
Now for a cheap low tech solution. First get the pressure tank like Geof said, then get some poly tubing and snake it thru your collector in fire prone spots. Cap one end of the tubing and hook the other end up to the pressurized water tank. When you get a fire it will melt the tubing, which will let the water start flowing. This doesn't have the quickest response time, but costs pennies, instead of thousands (uv/ir system). The only reason I wouldn't just hook it on to the water line is if you have a false trip (ie: you didn't fasten the tubing well and it rubbed thru) you will have a large mess. If you get a false trip with a pressure tank, you only have so much water to work with.

Even this is low tech there are many high dollar oil and gas facilities that have a fire protection system built on this principal.
__________________
On all equipment there are 2 levers...
Lever "A", and Lever F'in "B"
Tweet this Post!Share on Facebook
Reply With Quote

  #10   Ban this user!
Old 11-07-2007, 04:47 PM
 
Join Date: Mar 2007
Location: Canada
Posts: 37
bluejay_ca is on a distinguished road
If you look at the picture you will see that I have used a pressurized tank, an expired propane tank to be exact. I have no water source at this location because of freezing. The tank is 1/2 full of a water/glycol mix, under 120 psi air. The temp sensor is located on top of the blue drum, my vacuum collector. The temp sensor's logic was backwards so I added a relay to rectify that. In order for a fire in the vacuum to escape it will have to do so in the upper portion of the drum which will trip the switch and open the valve.
The vacuum exhaust is directed outdoors via a metal pipe (not shown in photo)
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 12-07-2007, 12:54 AM
 
Join Date: Dec 2007
Location: united states
Posts: 2
safeT is on a distinguished road
You could make sure the dust is collected in a bin that has a conductive bag so that you can ground out the collector. Dust traps oxygen and makes a mini grain elevator explosion if you are not careful. Static electricity especially about in places that are heated due to cold temp ( did you not explain that it was cold several times ) is prevalentn due to dry air conditions. Ground everything and read up on Explosion proofing which is NOT necessary about building something that will survive an explosion but something that will not create an explosion.

When I worked at NASA, someone put a wet paper towel in a microwave. Because the paper towel was made of recycled material, it contain iron from staples. The microwave caught the paper towel on fire after it dried somewhat.

The dust in your particle wood or any cheap wood may contain volatile organics and pieces of metal, dust, oxygen, and so on.

Your blue tank could be a bomb for all anyone knows. Get everything up to spec on ASME asap.
Tweet this Post!Share on Facebook
Reply With Quote

  #12   Ban this user!
Old 12-09-2007, 11:21 AM
 
Join Date: Mar 2007
Location: Canada
Posts: 37
bluejay_ca is on a distinguished road
Here's my solution. No collection. Exhausted outdoors. (I have no neighbours).

The aluminum blower housing I got from a scrapyard for free. The square aluminum housing and both flanges I fabricated and welded myself. I added a window of 1/4" lexan to view a 1/4" screen to catch big pieces.
The motor is a 1 hp, s.f. 1.65, 3400 rpm - from princess auto salvage area $69.99.
The turbine I fabricated from research and tweaked fin angles based upon airflow and current draw.
Attached Thumbnails
Click image for larger version

Name:	cnc 030forweb.jpg‎
Views:	100
Size:	80.0 KB
ID:	48184   Click image for larger version

Name:	cnc 029forweb.jpg‎
Views:	95
Size:	83.4 KB
ID:	48185   Click image for larger version

Name:	cnc 028forweb.jpg‎
Views:	104
Size:	99.5 KB
ID:	48186  
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Vacuum table and vacuum pump garagefela DIY-CNC Router Table Machines 19 01-25-2012 11:30 AM
What Fire Precautions Do You Use? diarmaid Polls 27 04-12-2010 11:07 AM
Vacuum system to hold down paper Aan Open Source CNC Machine Designs 2 04-06-2006 11:13 AM
Vacuum system JPMach Work Fixtures and Hold-Down Solutions 8 01-31-2006 02:07 AM




All times are GMT -5. The time now is 08:34 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353