I'm beginning to think that this device doesn't exist, yet it seems to me that it should. Been web searching and asking questions, but no luck so far. What I have is an ordinary e-stop mushroom switch. You press the button, and it latches in the down position. You have to twist and lift to make it release. What I want is exactly like that, but with the addition of a solenoid inside so that the switch can also be operated from an electrical signal. In either case, it would require the manual twist and lift to reset it. Anyone ever seen such a thing, or care to speculate why it might be a really bad idea? Neil |
|
#3
| |||
| |||
|
But what I'm describing is mechanically actuating the switch. How can you mechanically actuate the switch without mechanically actuating the switch? |
|
#5
| |||
| |||
| No it does not. NFPA, OSHA, and CE all require the button to ONLY open the safety chain. All safety circuits are required to have a latching circuit, and and buttons in the chain must be able to open the circuit. Further more, just FYI, all Emergency stop buttons MUST be twist to release OR pull to release. They also require a separate "operator" to start the equipment back up, and MUST have a yellow ring around the push button. Basically, to do what you want only requires the addition of a relay. |
| Sponsored Links |
|
#6
| |||
| |||
| I guess I didn't explain myself properly. I'm not just looking for another way to break the safety circuit. Obviously, I could put any number of NO contacts in series to achieve this. They could be relay contacts, limit switches, or whatever. I understand that. The machine will stop if the computer detects a fault condition, or if the operator presses the e-stop button. If the computer detected a fault condition, the operator has to take some action to resume operation.. clear an obstruction, or whatever. If the operator presses the e-stop button, he also must take some action, and then twist or pull up the e-stop button. What I want is that when the computer stops the machine, the operator must twist/pull up the e-stop button in order to resume. I.e., I want that to be necessary regardless of whether it was the computer or the operator that caused the machine to stop. So, I thought a way to achieve this would be if the computer could press the e-stop button when it detected a fault. This would require an e-stop button with a solenoid. Note that the computer would not need to operate the e-stop button in order to stop the machine. That would happen however it already happens, by removing power, applying brakes, or whatever. As an extra step, what the computer would do when stopping the machine due to a fault would be to also operate the e-stop button. I'm a total newbie at this, so please excuse me if I'm being ignorant. This just seems to me how it should work in general. Anyway, it does seem that such a device does not exist. I have a spare mushroom switch, and I'll see if I can modify it to do what I want. |
|
#7
| ||||
| ||||
| Traditionally E-stop circuits have either been the Mushroom push button that latches down and twist to release, or a two button setup that is a N.O. push to arm/engage in series with a N.C. E-stop push button, a control relay is picked up and the a latching contact is wired across the N.O. arming P.B. A variation that is seen on imported R.O.C. equipment is a unit that combines both of these methods, it is a relay that has two buttons mounted to it, the start button actually pushes the armature of the relay and engages the latch contact so the relay stays in, the E-stop just cuts the power to the coil, dropping it out again. If you want to conform to electrical code, one of the first two methods would be accepted, but the prevalent method now is to use what has been mandatory in Europe for some time and this is a Safety Relay, these can come in all kinds of configurations that allow controlled shut down with internal timers and switching combinations etc. The bottom line is that E-stop circuits should be hardwired and not be Primarily dependant on software actions. Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
|
#8
| |||
| |||
| OK, just have the computer break the estop chain, the operator would have to press control on to re-engage. Thats what the secondary operator is for. Per any code now, e-stop can not be self re-starting by simply releasing the e-stop switch. You must have a start or power on button to re-start the e-stop chain. |
|
#9
| |||
| |||
|
Yes, I agree. I'm not proposing to change that. I'm proposing that, in addition to whatever else the operator must do to clear a fault detected by the computer, he must also twist the red knob and pull it up. For this to happen, the knob must be down, in the latched position, even if the operator didn't press it. |
|
#10
| |||
| |||
| I'm not proposing this as a new code, or a rule that anyone else must follow. It's just how I want my machine to work. But if this causes a safety issue I'm unaware of, I won't do it. |
| Sponsored Links |
|
#11
| |||
| |||
| Don't know why it would create any safety issues. My only concern would be if you have employees running the machine and you changed a factory E-stop circuit. If anyone should happen to get hurt and blame it on the switch, you'd be up for lots of explaining. |
|
#12
| ||||
| ||||
| Frankly reading your explanation again, I don't see what the difference would be between what you describe and the typical control relay E-stop circuit, where a N.O. contact is used as a retaining contact across the Control ON P.B. any thing ANDED in the relay coil string will cause the E-stop to drop out and it requires the single P.B. by operator to reset it, which would be no different from releasing any other type you described. A button with a solenoid or a contactor to have the same effect? Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
![]() |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
| Display Modes | |
| |
Similar Threads | ||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Remote Cylce Start and stop button | R.DesJardin | Tormach PCNC | 22 | 04-09-2009 08:09 PM |
| E-Stop Button | widgitmaster | General Electronics Discussion | 3 | 05-19-2008 02:41 PM |
| Help with e-stop button | Astroguy | Xylotex | 2 | 05-31-2007 07:23 AM |
| Where do I install an emergency stop button? | alexccmeister | Stepper Motors and Drives | 36 | 04-21-2007 06:40 PM |
| Arcade Button Emergency Stop | mikkojay | Gecko Drives | 5 | 06-07-2006 12:30 AM |