Hi guys I just joined today but have been reading about RPC's on here for awhile. Let me tell you what I have Duplex air compressor 1-3hp (9amp) pump and 1-5hp (13.6amp) pump 10hp (idler motor) RPC My questions go out to guys that run compressors off a RPC or maybe any other high load machine I am trying to balance the run caps. I have been able to get voltages closer then 5% with no load. problem I am having is under load. Both motors will draw over there rated amps when pumping around 100 psi of air. the 3-hp has a standard pulley the 5-hp has been reduced by 25% both motors are kicking out on the heaters 3hp is set at 10 amps (high as it will go) 5-hp is set at 16 amps (high as it will go) I think the 5 hp is very close as it will run for a period before it kicks out. But seems odd that amps are over name plate with a reduced pulley. anyways here is what I have under a load (3hp maintaining 100 psi) L1-L3= 105MF L2-L3= 80MF L1-L3= 213V L2-L3= 232V L1-L2= 242V L1 Amps = 10 L2 Amps =12 L3 Amps = 2 or 3 Im sure my problem is the low generated leg, my question how do I fix it (keep adding run caps?) or did you find that you had to oversize your heaters? Thank you for any input you may have Knick |
|
#2
| |||
| |||
I found this article here in the Phase converters and VFD Forums here on CNCzone.com http://www.cnczone.com/FitchWConverter.pdf I will trying this soon and post how it worked for me |
|
#3
| |||
| |||
Ok I got this finished. Here is how I did it. I balanced the RPC with just the Idler running and no load. Idler is 10 hp L1-L3 = 70 MFD Volts = 257 L2-L3 = 90 MFD Volts = 244 L1-L2 Volts = 258 L1 = 14.3A L2 = 13.3A L3 = 13.7A When the compressor starts then the following run caps are added the following reading were taken @ 130 to 140 PSI L1-L3 50 MFD (total on L1-L3 120MFD) Volts = 248 L2-L3 40 MFD (total on L2-L3 130 MFD) Volts = 229 L1-L2 Volts = 253 L1 = 17.2A L2 = 13.5A L3 = 9.5A I would have liked to have gotten the amp reading (with compressor running) a little better but that the best I got. It seems to be working so far, but it does not have a lot of run time on it. This compressor also has another pump (duplex Compressor)powered by a 3hp. When I get some time I am going to do the same set up. once I find what run caps work best. My reason for doing this was to reduce the voltage when the compressor was not running. this way if the RPC is running for a hour and no air is being used I don't have high voltage like I would if all the run caps were wired together. |
![]() |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
| Display Modes | |
| |
Similar Threads | ||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| DIY air compressor | joecnc2006 | Hobby Discussion | 17 | 01-29-2011 03:09 PM |
| Air Compressor Questions for CNC Plasma | slammedxonair | DynaTorch | 22 | 06-21-2010 01:34 PM |
| Problem- compressor help | advt001 | General Metalwork Discussion | 1 | 04-07-2010 10:04 AM |
| New Compressor Help | 1ctoolfool | Haas Mills | 1 | 01-31-2007 05:52 PM |
| Compressor | Crazycorkey | Jet Engines and Ram Jets | 8 | 01-30-2007 03:02 AM |