RPC idler motor won't run

I'm in the process of building a 5hp RPC, based on the examples given by Christopherson, Isserstedt, and Hanrahan. Two 120v legs (L1 & L2) coming into a disconnect switch, fused (20a on each leg), and continuing on to the 5.5HP, 3 phase Bauknecht motor. A jumper off of L2 goes to another switch (momentary), which goes to a 250VAC 480 MFD start cap, and on to L3 of the motor. Motor is wired for 220v (L1+T1&T7, L2+T2&T8, L3+T3&T9, T4-T5-T6 COM). After checking with a voltmeter, no continuity exists between the motor housing and any of the wires. I've also verified my connections & fuses from the disconnect switch.

With the momentary switch closed, the disconnect switch is switched on (closed) and nothing happens. I quickly shut it back off. I also tried spinning the motor shaft with a rope and then applying power with no luck. I'm suspecting the motor, although I'm not sure since I couldn't find a short. Any ideas?

Thanks,

Robert
Reply With Quote

  #2  
Old 09-14-2009, 04:52 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

What do you mean by 'nothing happens' normally if the 240 is ending up at the motor and nothing is turning, you would hear a loud hum, a few seconds later the fuses would blow.
At the point of connecting the start cap, the 240vac should be connected to the motor via a three phase contactor.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 09-14-2009, 05:41 PM
 
Join Date: Sep 2009
Location: USA
Posts: 11
ls2005019227 is on a distinguished road

"What do you mean by 'nothing happens'"

When I close the DPST (disconnect) switch to energize L1 & L2 (and also have the switch closed to jump from L2 through the start cap to L3) absolutely nothing happens; no pops, sparks, smoke, or correct functioning. I also spun the motor with the rope and then closed the disconnect switch (to energize L1 & L2 only) and still nothing happens.

After what I have read and me probably being chicken, I've only left the disconnect switch closed for 2 seconds max. I didn't want to see what a start cap exploding is like first-hand.

Does three phase contactor=three pole contactor? What would be different about the momentary switch being closed when the disconnect is switched, so that all three are energized at the same time?

Thanks for the help.

Robert
Reply With Quote

  #4  
Old 09-14-2009, 05:48 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Take a look at the files by Fitch Williams, this is what I based mine on.
http://metalworking.com/dropbox/_1998_retired_files/
Look for the ones starting with FRW.
All three are connected through the 3 pole contactor.
If the 240v 1 phase is getting through to the motor and not the start cap/circuit, the motor will not turn and the result the motor will hum loudly and excessive current will flow if the motor does not turn at all.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 09-14-2009, 07:41 PM
 
Join Date: Sep 2009
Location: USA
Posts: 11
ls2005019227 is on a distinguished road
Finally! Something!

Now I remember where I got that schematic from = Fitch's plans. While driving home, I wondered if swapping two of the wires (from incoming L2/start cap) would make any difference; voila! I've found the HUM! The motor will now run (relatively loud, and seems slow) when the shaft is spun with rope. Once out of several tries it started turning by using the starting cap, but mostly the shaft just shudders. Also some weird voltages:

L1-L2=243v
L2-L3=121v
L1-L3=111v

Do I need to swap the incoming wires, or do I have other problems? Shouldn't a 480mfd start cap be enough for this 5.5HP motor?

Thanks,

Robert
Reply With Quote

Sponsored Links
  #6  
Old 09-14-2009, 08:00 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

I found the start cap only needs to be connected momentarily, and it should start to spin right away.
Unless it gets up to speed, your 3rd phase is going to be very low.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 09-14-2009, 10:11 PM
 
Join Date: Dec 2004
Location: usa
Posts: 1,665
TOTALLYRC is on a distinguished road

Originally Posted by Al_The_Man View Post
I found the start cap only needs to be connected momentarily, and it should start to spin right away.
Unless it gets up to speed, your 3rd phase is going to be very low.
Al.
To back up what Al is saying, on mine the start cap needs to be in the circuit for less than one second and if it is in any longer the motor makes a lot of strange noise and it doesn't turn very well.
__________________
Warning: DIY CNC may cause extreme hair loss due to you pulling your hair out.
Reply With Quote

  #8   Ban this user!
Old 09-14-2009, 11:45 PM
 
Join Date: Jun 2003
Location: Phoenix, AZ
Posts: 57
bocko912 is on a distinguished road

Your voltages will be off until motor reaches its full RPM. It sounds like you are not coming up to full RPM you need to add your run caps between L1 and L3 until your voltage is around 255 to 260volts. With a 5.5 hp you should have about 40 to 60 MFD run caps and 480MFD for starting is fine. Your motor should come up to full RPM in about 1-2 seconds then start caps should come off line. When you apply a load to the idler your L1-L3 voltage should drop to about 230 volts. The only problem is that your phases will not be balanced so you will only be able to run other 3ph motors like manual lathes and mills no CNC. Balancing is pretty easy to do if you need it. You just need to add run caps between L2-L3 to balance phases. If you need I can help. Also I would not run the motor too long if its making a loud noise and turning slow you are out of phase and your motor will get hot quick.

John
Reply With Quote

  #9   Ban this user!
Old 09-15-2009, 12:34 AM
 
Join Date: Sep 2009
Location: USA
Posts: 11
ls2005019227 is on a distinguished road

First of all, I really appreciate you guys taking the time to help.

I haven't ran the motor much under these conditions; after watching a friend's converter work (to full speed in under a sec), I can tell that it's not right and don't want to damage anything. I have the run caps (2 @ 60mfd), I just haven't wired them in yet. I didn't realize that they could affect start up. I was planning on adding them after I had confirmed that things were going to work. I just bought a manual Tree 2UVR which is 3 phase so at this time, a simple rpc should work. CNC would be awesome in the future.

Does the lack of run caps sound like my only problem; or is there something else that I should be looking at? I'm not pessimistic, but I am a bit concerned about the motor (although from my testing thus far [no shorts], it appears to be ok).

Thanks again,

Robert
Reply With Quote

  #10   Ban this user!
Old 09-15-2009, 01:56 AM
 
Join Date: Dec 2004
Location: usa
Posts: 1,665
TOTALLYRC is on a distinguished road

Originally Posted by ls2005019227 View Post
First of all, I really appreciate you guys taking the time to help.

I haven't ran the motor much under these conditions; after watching a friend's converter work (to full speed in under a sec), I can tell that it's not right and don't want to damage anything. I have the run caps (2 @ 60mfd), I just haven't wired them in yet. I didn't realize that they could affect start up. I was planning on adding them after I had confirmed that things were going to work. I just bought a manual Tree 2UVR which is 3 phase so at this time, a simple rpc should work. CNC would be awesome in the future.

Does the lack of run caps sound like my only problem; or is there something else that I should be looking at? I'm not pessimistic, but I am a bit concerned about the motor (although from my testing thus far [no shorts], it appears to be ok).

Thanks again,

Robert
I don't think the run caps are your problem as I don't run any at all.

I would verify your wiring and make sure you are getting 240v across L1/L2 as you incoming power.
I would also take an ohm reading across L1/L1, L2/L3, L1/L3 WITH THE POWER OFF and all the caps out of the circuit. All three readings should be close. A large difference will indicate problems with the motor windings.
__________________
Warning: DIY CNC may cause extreme hair loss due to you pulling your hair out.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 09-15-2009, 03:36 PM
 
Join Date: Sep 2009
Location: USA
Posts: 11
ls2005019227 is on a distinguished road

I will ohm it out when I get home from work. Is it correct then that I will be checking the resistance between T1&T7 (L1) and T2&T8 (L2)......?

Also, here is some info on the motor:
Bauknecht (sp?)
5.5 HP
1740 RPM
In addition to having T1-T9, I believe that there is a T10-T12. I'm trying to research 12 lead motor wiring diagrams. I will have to see how leads T10-T12 are connected. When I bought the motor a week ago, it was wired in the standard L1-T1&T7, L2-T2&T8...... and I didn't think anything about it. Should T10-T12 be included in some way?

I would appreciate any information that anyone may have about this configuration for a 220v system.

Thanks
Reply With Quote

  #12   Ban this user!
Old 09-15-2009, 10:42 PM
 
Join Date: Sep 2009
Location: USA
Posts: 11
ls2005019227 is on a distinguished road
It's official....the motor does have twelve wires...

I guess that this makes it pretty obvious that this is my first three phase experience.... When looking at the motor to buy, I noticed T10, T11, & T12, but they weren't connected to any of the other wires, and I remembered the nine lead wiring diagram (L1-T1&T7, L2-T2&T8, L3-T3&T9, T4-T5-T6) which is the way it was wired so I didn't expect any different. It may not have worked well for someone else either. Does this explain the groaning? Has irrepairable damage been done? I used the ohm meter to test each lead for a short to the motor housing; none were. I printed out a two-delta wiring diagram (is this correct for 220v?), and have now connected:

L1-1&6&7&12
L2-2&4&8&10
L3-3&5&9&11

I closed the start cap switch, closed the disconnect switch, the shaft started to turn (without any obnoxious noises).... and then nothing. Apparently I blew both 20a "general purpose" fuses, on L1 & L2. Are my fuses just too small, or is there something else going on?

Thanks for the help (and patience)

Robert
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need Help!- Changing Fanuc AC servo driver and motor for a regular VFD and async motor Bordaco Servo Motors and Drives 4 09-08-2011 05:41 PM
Problems with motor stalling due to motor/lead screw alignment Bimmerkc1 DIY-CNC Router Table Machines 3 01-24-2010 06:12 PM
What Size Idler motor? split63 Phase Converters and VFD 4 07-27-2006 09:47 AM
spindle belt idler yeepman2 Fadal 6 05-21-2006 07:05 PM
3 phase with idler and draw string only gtslabs General Electronics Discussion 2 06-19-2004 04:11 PM




All times are GMT -5. The time now is 03:44 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361