Hello All!

I have a friend that recently purchased a Hitachi L200 VFD for use with a Series II Bridgeport. He does not plan on using the VFD for anything else other than to turn the mill's motor on (forward / reverse). In other words, he is not converting it to CNC, nor will he be using a PC to control or operate the spindle.

He simply wants to turn on the power to the VFD, then use the mill's forward / reverse switch (which will be wired to the VFD via the "Intelligent Input Terminals") to control the motor.

Sounds like a simple concept, but we are having a bit of trouble. First of all, let me state that I am not an electrician, an electrical engineer, nor one who knows very much about circuits and logic controls.

I believe that I have configured it correctly per the instructions, but I can not control the VFD via the Input terminals. I have attached the relevant pages from the manual for reference.

I set the SR/SK DIP switch to SK per page 4-9, which I believe is correct.

I am a little confused by the schematic on page 4-10. Can I use the forward / reverse swith from the mill, or do I need some sort of transistorized device to interface with the inputs?

I set the A002 = 01 parameter, per page 4-12, to enable the control terminal (see page 3-10 for options).

Now, if I understand correctly, all I need to do, per page 4-12, is connect the PCS terminal (via the switch) to terminal "1", and the motor should turn on, in the forward direction. If I connect the PCS terminal (via the switch) to terminal "2", the motor should turn on, in the reverse direction.
But nothing happens when i make these connections.

I know that the VFD is working, and wired correctly, because if I turn the VFD on (with the A002 = 02 option set), the motor turn on and runs. I can also adjust the speed with the potentiometer. But I have no way to reverse the motor, without changing VFD parameters.

I do not understand whay it does not work using the Intelligent Input Terminal. What am I missing? Any help or advice would be greatly appreciated.
Reply With Quote

  #2   Ban this user!
Old 05-14-2009, 11:27 AM
 
Join Date: Oct 2006
Location: USA
Posts: 70
robhrzic is on a distinguished road

OOPS! Here are the attachments.
Attached Thumbnails
Click image for larger version

Name:	L200 3-10.jpg‎
Views:	90
Size:	108.7 KB
ID:	81330   Click image for larger version

Name:	L200 4-06.jpg‎
Views:	88
Size:	119.9 KB
ID:	81331   Click image for larger version

Name:	L200 4-09.jpg‎
Views:	79
Size:	122.3 KB
ID:	81332   Click image for larger version

Name:	L200 4-10.jpg‎
Views:	89
Size:	77.4 KB
ID:	81333  

Click image for larger version

Name:	L200 4-12.jpg‎
Views:	65
Size:	98.4 KB
ID:	81334  
Reply With Quote

  #3   Ban this user!
Old 05-14-2009, 11:55 AM
 
Join Date: Jan 2005
Location: USA
Posts: 2,348
mactec54 is on a distinguished road
Buy me a Beer?

Hi Robhrzic

Have you got 24vDC in your switching circuit you have the option to use the internal 24vDC supply or a external supply which you would have to supply & when you get it going do not switch from forward to reverse to quickly to do forward & reverse instant you will need a braking resistor fitted
__________________
Mactec54
Reply With Quote

  #4   Ban this user!
Old 05-14-2009, 11:58 AM
 
Join Date: Oct 2006
Location: USA
Posts: 70
robhrzic is on a distinguished road

Machtec64,

Yes, I have 26.7 VDC across the PCS and L (ground) terminal.
Reply With Quote

  #5   Ban this user!
Old 05-15-2009, 08:19 PM
 
Join Date: Dec 2004
Location: usa
Posts: 1,665
TOTALLYRC is on a distinguished road

I would try using a jumper wire or a couple of temporary switches to see if the bridgeport switch is working correctly.

I have the sj200 using mach3 but the principle is the same.

Mike
__________________
Warning: DIY CNC may cause extreme hair loss due to you pulling your hair out.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 05-16-2009, 08:25 PM
 
Join Date: Jun 2003
Location: USA
Posts: 5
JimP is on a distinguished road

That switch should be on SR i think.
Reply With Quote

  #7   Ban this user!
Old 05-17-2009, 12:40 AM
 
Join Date: Dec 2004
Location: usa
Posts: 1,665
TOTALLYRC is on a distinguished road
Settings, it is alsways the settings!

I just took a look at the manual for the L200 manual and here are what the basic settings should be.

C001=00 gives forward from terminal 1
C002=01 gives reverse from terminal 2
A001=00 uses the onboard pot for frequency control
A002=01 allows use of the terminals instead of keypad for forward and reverse.

Once you get it up and running and if you are only using it for on and off, you should set some acceleration profiles to keep it from tripping out when starting/stopping or changing directions.

Mike
__________________
Warning: DIY CNC may cause extreme hair loss due to you pulling your hair out.
Reply With Quote

  #8   Ban this user!
Old 05-18-2009, 08:58 AM
 
Join Date: Oct 2006
Location: USA
Posts: 70
robhrzic is on a distinguished road

C001=00 gives forward from terminal 1
C002=01 gives reverse from terminal 2
A001=00 uses the onboard pot for frequency control
A002=01 allows use of the terminals instead of keypad for forward and reverse.

TOTALLYRC, JimP, thanks for your time and input.

This is exactly how I set the parameters of the L200. I even double, then triple checked everything, but nothing happens. I've tried the SK and SR settings with the DIP switch, and nothing happens. And yes, I tried using a short jumper wire from the PCS terminal, and terminal #1 (and #2) and nothing happens.

I also have it configured (using the F002 and F003 parameters, I believe) to ramp up acceleration in 3 seconds, and deceleration in 3 seconds. Again, it works fine when using the contol panel Run button, Stop/Reset button and potentiometer (setting A002=02 and bypassing the mill's switch altogether). It's just that you can't reverse the motor very easily, or chane from Hi range to Lo range very easily.

I did find out that if you jumper the PCS terminal to the L terminal (like the manual tells you to do), it trips an error code and the unit resets itself with a loud click. So I know I have voltage at the terminal block.

I also have one of these exact same units installed on my wood cutting bandsaw, to make it a variable wood / metal cutting bandsaw. It works great, though I have mine configured to use the control panel and potentiometer to adjust the speed (Hz) of the motor.

I tried the same thing (configuration and parameter settings) with my inverter, and I get the same (lack of) results. That's why I thought that I must be missing something, or do not have something configured correctly. I find it hard to believe that both units are somehow defective, and / or can not be configured according to the manual.

I was hoping to find someone here, on this forum, that has had success doing what I am trying to do, with the same unit / model, so that I could get some input. I thought about contacting www.driveswarehouse.com, where Ipurchesed the unit, but I found out that Hitachi has discontinued this model. Wonder why?

It doesn't seem like it should be this difficult according to the instructions.
I just can't seem to figure out how to get it to work.
Reply With Quote

  #9   Ban this user!
Old 05-18-2009, 09:44 AM
 
Join Date: Jan 2005
Location: USA
Posts: 2,348
mactec54 is on a distinguished road
Buy me a Beer?

Hi robhrzic

You may have smoked the circuit as the manual tells you not to short PCS to L terminal
it is in section 4-6 that may be the reason that they do not work you may have smoked the circuit on the first try
__________________
Mactec54
Reply With Quote

  #10   Ban this user!
Old 05-18-2009, 10:56 AM
 
Join Date: Dec 2004
Location: usa
Posts: 1,665
TOTALLYRC is on a distinguished road

Hi robhrzic.

It looks easy but it can take awhile to get it dialed in.
The only other thing I can think of is to make sure that c02,c03,c04 and c05 are not at either 00 or 01.

Otherwise it looks like you have it hooked up properly. Just to be safe you could always try an external 24v power supply.

Let us know if you get it sorted out.

Mike
__________________
Warning: DIY CNC may cause extreme hair loss due to you pulling your hair out.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 05-19-2009, 01:50 AM
 
Join Date: Dec 2005
Location: UNITED STATES
Posts: 32
bemfarmer is on a distinguished road

How about a Reset?
Reply With Quote

  #12   Ban this user!
Old 05-25-2009, 05:24 PM
 
Join Date: Oct 2006
Location: USA
Posts: 70
robhrzic is on a distinguished road

I have performed a reset a couple of times already, with the same results. The unit still operates the same way as it did before the reset.

I don't think that the circuitry was damaged, by shorting the PCS terminal to the L terminal. All it seemed to do is trip a breaker, and reset itself. Besides, I did not do that (short PSC to L) on my bandsaw's VFD, and it operates exactly in the same manner as the other one does.

If I were to use an external 24V power supply, what type could I use? How would I make the connection? If I understand it correctly, I would connect the (+) side to the C001 or C002 terminal. Where would I connect the (-) side to? The L terminal?
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Can a 3ph input VFD Hitachi J100 run on 1ph ? maquiza Phase Converters and VFD 9 05-26-2009 10:55 AM
analog input VFD speed Hitachi SJ100 Karl_T Phase Converters and VFD 10 11-22-2008 03:09 PM
Analog Input for Devicenet Hitachi SJ100DN2 SirThadious Phase Converters and VFD 3 02-07-2008 03:58 PM
Pc Port Direct Hitachi L200 Connect Cruiser Phase Converters and VFD 2 12-13-2006 09:54 PM
AC Tech SM230S VFD VS Hitachi L200-022NFU VFD cbucner Phase Converters and VFD 1 06-15-2006 03:10 AM




All times are GMT -5. The time now is 03:42 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361