Transformer question Wye/Delta

I recently bought a used SWI Prototrak DPM mill for my garage. This particular mill requires 440VAC 3 phase power. There is no separate power entry for 115VAC to power the electronics; all 115V power is handled by a small internal transformer. My garage has 240V single phase power. I am planning on building a 7.5 hp RPC. The manual specifies 5KVA for RPC. Fine so far.

I have found a 3 phase transformer that I want to wire in after the RPC (I’ll keep the RPC at 240VAC). Below is a picture of the ID plate on the transformer. I need a multi tap transformer that can output close to 440V with 240V input. I just don’t understand the impact of the Wye/Delta wiring. It appears that the Wye is on the low voltage side.

I’ve also posted a picture of the power entry in the electrical cabinet of the mill. As you can see, there are 3 hots and a ground; no neutral.

My question:
Will this transformer work as I need? The Wye thing has me stuck. Should I hold off and find a transformer that is Delta/Delta? Thanks for the help.
Reply With Quote

  #2  
Old 03-03-2009, 09:42 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

I would look closer into the 440 requirements, it is very likely that this is only required for any 3 phase motors, which upon inspection, may have the option to reconnect for 240.
The control power, or other 1 phase power in the machine is most likely either 240 or 120 1 phase.
The wire gauge for the the motors at lower voltage may be ok, only the fusing and over loads may need adjusting or replacing.
This would be a better option than installing a transformer.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 03-03-2009, 10:02 AM
 
Join Date: Sep 2007
Location: USA
Posts: 7
kentucker237 is on a distinguished road
Let's try those pictures again :)

Al, Thanks for the quick reply. These mills ordinarily have separate power entry for 3 phase to the spindle motor and 115VAC single phase for the electronics, servos, etc. This particular mill was wired 440VAC 3 phase with no separate 115 VAC power entry. The spindle motor can easily be switched to 220VAC. However, the 115 single phase is done internally off of the 440, and I’m unsure how to power that correctly with external source. I don’t want to fry stuff. Since this machine spent its first 12 years happily on 440VAC 3 phase, I’m thinking this is the way to go. Transformers can be had for about $100 used, plus whatever wiring necessary.

If someone has a picture inside of their Prototrak’s electrical cabinet with separate 115 single phase, that could help. Mine is a 1997 model Trak DPM with AGE3 control. Thanks all.
Attached Thumbnails
Click image for larger version

Name:	Trak DPM power entry.jpg‎
Views:	52
Size:	70.6 KB
ID:	76777   Click image for larger version

Name:	transformer wye delta 15kva.jpg‎
Views:	67
Size:	77.9 KB
ID:	76778  
Reply With Quote

  #4  
Old 03-03-2009, 10:12 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

As far as the present single phase in the panel, it is most likely set up with a 440/120 or similar isolation transformer, however one side of the secondary is probably connected to panel ground for local neutral, this is easy to check, if this is how it is, it is easy to replace the control transformer with a 240/120 1 phase, or the existing one may even have the 240v taps on the primary.
It is your choice, but I would look at this avenue first.
Running the transformer 'backwards' will work, although heating may occur as often they are fitted with a compensation winding. Do not connect the star connection.
The voltage may be lower running it this way.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Transformer Question Bimmerkc1 General Electronics Discussion 16 01-15-2007 03:15 PM
Transformer question need help! northernmach DIY-CNC Router Table Machines 23 11-30-2006 04:51 PM
Transformer question need help! CNCadmin DIY-CNC Router Table Machines 0 11-27-2006 10:00 AM
Transformer question pstockley General Electronics Discussion 2 04-04-2006 11:13 PM
Transformer Question SJ781 General Electronics Discussion 1 11-05-2003 07:39 AM




All times are GMT -5. The time now is 03:41 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361