Question Phase convertor needed for 3 HP CNC milling machine (rotary or electronic)?

Getting ready to purchase a CNC milling machine that uses a 3 HP 220 V (3 phase) motor. What type of convertor do I need?

I've done some reading and searching and it seems like a rotary phase convertor with some sort of voltage conditioning is preferred?

Can an electronic phase convertor work as well?

The milling machine uses stepper motors and the control cabinet uses 120V. The spindle has a variable dial on the front for speed selection (no changing belt positions). Is this the same as a VFD?

If a rotary convertor is the way to go, can you go too large? Someone local has a 20 hp rotary convertor he wants to get rid of...

Thanks for any help...
Reply With Quote

  #2  
Old 01-21-2009, 11:59 PM
Gold Member
 
Join Date: Oct 2004
Location: USA
Posts: 176
freak_brain is on a distinguished road

I think as a general rule static phase converters are not recommended for CNC machines. However, it sounds like all you are looking to do is power the spindle motor with the phase converter. I would think a static phase converter would be just fine for that.

The variable speed spindle is not a VFD. VFD is a variable frequency drive.

I'm farrrrrrrr from an expert on this stuff so wait for the "smart people" to confirm all of this.

Allen
Reply With Quote

  #3  
Old 01-22-2009, 09:33 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

If the mill uses a standard 3 phase motor and is not presently electronically controlled, It sounds like you have a vari-speed pulley, which is mechanical speed adj.
If so, would go with a 5hp VFD on 240v 1 phase.
Set up the rest of the machine on 120v 1 phase, most likely there is a 120v control transformer in the enclosure for this already.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #4   Ban this user!
Old 01-22-2009, 11:02 AM
 
Join Date: Aug 2008
Location: USA
Posts: 77
radioactive is on a distinguished road

Originally Posted by Al_The_Man View Post
If the mill uses a standard 3 phase motor and is not presently electronically controlled, It sounds like you have a vari-speed pulley, which is mechanical speed adj.
If so, would go with a 5hp VFD on 240v 1 phase.
Set up the rest of the machine on 120v 1 phase, most likely there is a 120v control transformer in the enclosure for this already.
Al.
I believe that is correct, a varispeed pulley (will confirm this weekend).

I can't seem to find any VFD's rated for 5 hp that can be powered from single phase. Does a VFD need to be overrated as compared to the hp of the motor?

It seems that most the rotary convertor manufacturers all have a special product for CNC machines. Why does a CNC machine require something different? I'm thinking it is to ensure you have a consistant voltage level for the PC. If this is the case, I can just power the control cabinet from standard 120V and get any 'ol rotary convertor for the motor.

Can you go too large on a rotary convertor? Any disadvantages?

Sorry for all the questions... Thanks for the info...
Reply With Quote

  #5  
Old 01-22-2009, 11:32 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Usually there is a derating factor when using VFD on 1 phase input, most manuf. top out at 5hp for 1ph and this should be OK for 3hp motor.
Usually whether using a rotary or static, the 120/240 1phase will come off the main 240v single phase legs, which are passed through the convertor, the manufactured phase is avoided for control puposes, for normal 3ph induction motor, static or rotary should be OK.
Too large is just overkill, otherwise no ill effects.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 01-22-2009, 12:42 PM
 
Join Date: Aug 2008
Location: USA
Posts: 77
radioactive is on a distinguished road

Originally Posted by Al_The_Man View Post
Too large is just overkill, otherwise no ill effects.
Al.
I'm thinking if I just get a large one now, it will be able to be used for any other 3 phase large equipment purchased in the future (possibly a welder) and I won't be needing to buy another convertor a year from now. Thanks...
Reply With Quote

  #7   Ban this user!
Old 01-22-2009, 10:18 PM
KIMFAB's Avatar  
Join Date: Nov 2006
Location: U S A
Posts: 152
KIMFAB is on a distinguished road

I'd be a little leery of using it for a welder. Most VFD's tell you to only switch them with the input not the output. With the welder you are abruptly varying the load and could cause problems.
__________________
I used to be appalled, now I'm just amused.
Reply With Quote

  #8   Ban this user!
Old 01-23-2009, 09:09 AM
 
Join Date: Aug 2008
Location: USA
Posts: 77
radioactive is on a distinguished road

Right, I was speaking about using a large rotary for the welder later down the road.

I thought I read that you don't have to derate a VFD (only static convertors need derated since they essential run the motor on 2 phases instead of 3, and therefore have to be derated 1/3 of the amount). If this is true, then a 3 hp motor would require a 3 hp VFD. Hitachi makes one for about $250. Not too bad.

The 20 hp rotary I found was $450 and may require too much starting current to get going without a pony motor.
Reply With Quote

  #9  
Old 01-23-2009, 09:26 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by dsl-pwr View Post
I thought I read that you don't have to derate a VFD (only static convertors need derated since they essential run the motor on 2 phases instead of 3, and therefore have to be derated 1/3 of the amount). If this is true, then a 3 hp motor would require a 3 hp VFD. Hitachi makes one for about $250. Not too bad.
Check the VFD manuf. spec's, they should mention if derating is required, some manuf. also design models that use no derating.
The reason for derating a VFD is that on 1ph the resulting DC supply is reduced in capacity.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 01-23-2009, 09:55 AM
 
Join Date: Aug 2008
Location: USA
Posts: 77
radioactive is on a distinguished road

Here's the VFD I'm considering:

http://www.driveswarehouse.com/Drive...4f74f7374e7d7b

I've looked thru the manuals and there is no mention of derating it. The 3hp model is the largest for a single phase input and is rated at 96% efficient at 100% rated output.
Reply With Quote

Sponsored Links
  #11  
Old 01-23-2009, 09:58 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

It appears to be a non-derated model, so you should be OK!.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #12   Ban this user!
Old 01-25-2009, 01:57 PM
 
Join Date: Dec 2005
Location: USA
Posts: 37
sparkness is on a distinguished road

No derating is required on currently available VFD's A 3HP VFD is designed for 3HP regardless , download some manuals and get fimilar with them
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Phase convertor Cadbob Phase Converters and VFD 1 10-11-2008 11:43 PM
VFD or Rotary Phase Convertor??? mgb1974 Phase Converters and VFD 4 06-04-2008 04:00 PM
VF 2 phase convertor? BBRC Haas Mills 15 02-22-2008 08:11 AM
Help Needed Phase Balancing a Rotary Converter Tayloned Machine Problems, Solutions , Wireless DNC, serial port 8 02-05-2008 01:34 PM
Rotary phase convertor for Fadal3016 bluecon Phase Converters and VFD 4 08-22-2007 07:36 PM




All times are GMT -5. The time now is 08:47 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361