VFD and EMI

Looking for help in finding the 'best/quickest' fix. Added a vfd to a knee mill and when the spindle powers on getting a fairly steady interference signal into the z-axis encoder signal. The encoder wiring is shielded back to the replacement PC controller in a cabinet separate to the vfd. The vfd motor output lines do parallel the encoder wiring a good distance, but this was factory and worked OK on normal 3-phase line power and original controller, is now a problem with vfd and PC retrofit.

Should I try to get shielded motor cabling, and any good source (3hp spindle)? Or reroute new shielded encoder signal cable away from motor leads? What is the most common/typical problem with VFD and signal noise? I'm counting on some 'been there, done that' experience to fix the 'real' problem, cheapest, fastest, and effectively. Especially since sheilded power cables seem a little harder to find.
Reply With Quote

  #2  
Old 10-28-2008, 08:51 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

What kind of cabling is the motor wired up with?
Belden make a special VFD cable, but it is very expensive.
Many are wired up with single conductor stranded TEW or close, the three 3 phase conductors should be tightly twisted for the full length and the ground conductor run with them but not twisted. Liquid seal metallic flexible conduit is a good choice to run the conductors in, this acts a shield when also grounded properly.
How does the Z encoder noise manifest itself?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 10-28-2008, 09:11 PM
 
Join Date: Oct 2006
Location: USA
Posts: 205
123CNC is on a distinguished road

The motor wiring, from what is visible, doesn't have any markings. It is four separate conductors (not cable and notmanually twisted either), stranded wire, and I would guess MTW, run through liquid-tite PVC conduit from cabinet to motor, with a fairly long open run in the cabinet.

With the spindle off multi-axis moves and encoder feedback all checkout OK. When on, the Z axis is clearly having a problem in that it will move to a commanded static position yet proceed to drift up and hit the max-Z limit all the while maintaining a (fairly) static feedback position. The interference seems to be fairly constant as the drift/controller's response is fairly constant, not erratic or ramped.

I thought about the metal flex conduit, but don't know where the biggest source or contributor is, vfd and in cabinet, or wiring/signals to devices.
Reply With Quote

  #4  
Old 10-28-2008, 10:09 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

I prefer Metallic flex conduit, twisted conductors is also important.
Also I would ensure all grounds are taken back to a common ground point together with the Service ground, also it may pay to look at grounding the encoder supply to this plate.
If the encoder is supplied from the PC power supply, the grounded common point for it can wend its way back to the PS ground through the MB screws etc, instead if a sound point external, for example, the ground bus, together with all shields.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 10-29-2008, 01:21 AM
 
Join Date: Oct 2006
Location: USA
Posts: 205
123CNC is on a distinguished road

Al,

Thanks for the suggestions, I will give it a go when I can allot enough time and pickup some flexible metallic conduit. The encoders are on a separate power supply, but I need to verify its grounding path. I may try to run the encoders, or at least the z-axis, from the PC PS on the remote chance it provides better isolation.

You continue to live up to your moniker, you are 'The_Man.' Although smoking has clearly stunted your growth some.

Thanks again and I will try to remember to post my findings later.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 10-29-2008, 01:52 AM
 
Join Date: Dec 2004
Location: usa
Posts: 1,665
TOTALLYRC is on a distinguished road

Originally Posted by 123CNC View Post
Looking for help in finding the 'best/quickest' fix. Added a vfd to a knee mill and when the spindle powers on getting a fairly steady interference signal into the z-axis encoder signal. The encoder wiring is shielded back to the replacement PC controller in a cabinet separate to the vfd. The vfd motor output lines do parallel the encoder wiring a good distance, but this was factory and worked OK on normal 3-phase line power and original controller, is now a problem with vfd and PC retrofit.

Should I try to get shielded motor cabling, and any good source (3hp spindle)? Or reroute new shielded encoder signal cable away from motor leads? What is the most common/typical problem with VFD and signal noise? I'm counting on some 'been there, done that' experience to fix the 'real' problem, cheapest, fastest, and effectively. Especially since sheilded power cables seem a little harder to find.
The reason it worked with real three phase power and not with the vfd is that the vfd output generates noise in way that can be picked by sensitive devices.
I believe that my hitachi manual specifically states that control wiring must cross at 90 degrees and not run parallel for any distance.
My btc-1 which came factory with a vfd, had almost all the wiring twisted.
When I did the retrofit, I made sure that the wire twisting was replicated.

I used to have similar problems with my rc cars and just twisting the servo wires going from the servo to the reciever would solve most problems.

My understanding of the problem is that wires act as antenae and when you twist them you make the antenae lenght so short that any signal it picks up is well beyond the range where it makes any difference. I am sure there are other reasons why it works but work it does.Twisting the wires from the VFD to the motor will also be helpful.

Consider running the vfd wires in grounded metalic conduit if physically possible.. This way you have contained the noise and it won't affect anything that you add in the future.
Shielding the encoder wire just protects that wire.
Of course somtimes you have to shield both wires.

Mike
__________________
Warning: DIY CNC may cause extreme hair loss due to you pulling your hair out.
Reply With Quote

  #7  
Old 10-29-2008, 08:15 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by 123CNC View Post
The encoders are on a separate power supply, but I need to verify its grounding path.
I normally take all my power supply commons to a single ground plate.

Originally Posted by TOTALLYRC View Post
My understanding of the problem is that wires act as antenae and when you twist them you make the antenae lenght so short that any signal it picks up is well beyond the range where it makes any difference. I am sure there are other reasons why it works but work it does.Twisting the wires from the VFD to the motor will also be helpful.
Twisting conductors have a mutual cancellation effect of adjacent conductors.
Both VFD supply and motor wires should be twisted, but the VFD to motor are the most important.
Many VFD manuf supply and recommend a 3phase choke on the VFD output for suppression also.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 10-29-2008, 07:42 PM
 
Join Date: Oct 2006
Location: USA
Posts: 205
123CNC is on a distinguished road
Choke this, Choke that

Al,

Thanks for yet more info. My main goal was to attack from the most troubled area, i.e. most effective single fix, and thus

"...but the VFD to motor are the most important."

Is exactly what I was hoping to hear. If it doesn't completely fix it, I will move to the next best fix, line to vfd, then maybe chokes, then ....

I know you are a bigger fan of the higher quality industrial grade VFD's, but aside from the added bells and whistles are there designs much better in the way of EMF emissions?
Reply With Quote

  #9  
Old 10-29-2008, 08:24 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by 123CNC View Post
Al,
I know you are a bigger fan of the higher quality industrial grade VFD's, but aside from the added bells and whistles are there designs much better in the way of EMF emissions?
I am not sure whether one make has any more emission problems than another.
Just that the procedures I have followed, I have never yet experienced a real problem with interference , and this is with up to 3 10hp VFD's in one enclosure.
It's something I have never cut corners on.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 08:46 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361