Delta to wye 3 phase

I was told i needed a transformer to run my cnc machine. I have a 230v 3 phase delta service and they told me i needed to get a $3k+ transformer to convert the delta to wye. I am not electric savoy and would like to see if there is an electrical geek out there that can help me. The reason i ask is because everything runs fine and the manufacturer told me i needed it but could not give me a reason other than they have installed a machine befor on delta and had problems with it.

Any Takers?
Reply With Quote

  #2  
Old 07-02-2008, 07:47 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

For ground referenced supply a Star or Wye supply is usually used and the star point grounded, rather than one leg of a Delta.
I assume yours is ground referenced and not isolated?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 07-03-2008, 12:33 PM
 
Join Date: Jun 2007
Location: usa
Posts: 18
StephenSebastia is on a distinguished road

I am not sure what you mean but it is refered to as delta, or grounded b phase by electricians.
Reply With Quote

  #4   Ban this user!
Old 07-03-2008, 08:58 PM
 
Join Date: Jun 2008
Location: SE Wisc, USA
Posts: 8
midlf is on a distinguished road

You have the three phase system that Al the Man referred to as the delta referenced to ground. Grounded B phase Delta is what I have always called poor mans 3 phase. The grounded B phase system only requires a 2 pole circuit breaker for each circuit rather than a 3 pole CB. The voltage to ground on the A phase and C phase is 240 volts each with the B phase wire being grounded. The voltage between the A, B and C phase wires is 240 volts each. A full 3 phase system also has 240 volts between each phase wire but all 3 phase wires show approximately 138 volts to ground. Your machines manufacturer may have had problems with a machine on a grounded B phase system before and the transformer "fixed" the problem. If it is running OK I don't see a problem however it may void your warranty if not wired the way the mfr specifies. Also the machine mfr will probably blame any problem you have in the future on the grounded B phase system. I'm not familiar with modern CNC machines or their control systems so I can't comment on any specifics of their wiring that could cause a problem with grounded B phase.
Reply With Quote

  #5   Ban this user!
Old 07-04-2008, 10:03 AM
 
Join Date: Apr 2005
Location: US
Posts: 411
Kevin Taylor is on a distinguished road

midlif
I have 230V three phase with a wild leg leg to leg is 230V and two of the three to ground are 125V and the one is 200V give or take I always make shure that the wild leg dosen't get into a control voltage that requires 120v. Haven't had a lot of proublems over the years but my old BPT CNC seem's to have voltage isues from time to time . I started working on a lathe that came with a transformer on it and I think the voltage seem's to get averaged out on the output side will have to check. Kevin
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 07-07-2008, 12:22 PM
 
Join Date: Oct 2006
Location: USA
Posts: 205
123CNC is on a distinguished road
why you might need the transformer

From phaseconverterinfo.com,


"If the three-phase equipment has 120V phase-to-neutral circuits that cannot be isolated and connected to either leg 1 or leg 2, the output of the phase converter must be passed through a 240V delta to 120/208V wye isolation transformer. This transformer will establish ground and neutral at equal distance from all three legs and deliver the power in a wye configuration.
This is especially important when operating some newer CNC machines that have certain Fanuc or Siemens controls. These controls handle regenerative power from the spindle motor by putting the regenerative power back onto the line utilizing a phase-to-neutral connection on all three legs. If these machines are powered by a phase converter with delta configured power, the regen circuit on the leg manufactured by the phase converter will operate at a voltage that is too high. An isolation transformer must be used to convert the power from delta to wye configuration."

Basically, with regenerative power your wild leg would go REALLY wild.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Can I convert single phase motor to three phase? Jim Estes Phase Converters and VFD 30 01-24-2009 02:41 AM
1 phase Vs 3 Phase power what is the difference????? KustomKoncepts Commercial CNC Wood Routers 12 11-17-2007 10:34 PM
Wye-delta, delta-wye configurations? mackeym Phase Converters and VFD 10 09-27-2006 05:02 PM
3 phase transformer on single phase? jevs General Electronics Discussion 4 03-19-2005 11:25 AM
2 phase vs 4 phase stepper motors Don C General Electronics Discussion 1 05-26-2004 01:40 PM




All times are GMT -5. The time now is 08:45 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361