Moving Shop 3 phase converter ?s

Hello, and thanks for looking.

I am going to be moving my small CNC shop and not going to have an option for 3 phase power. I was wanting to find out what converter would be sufficient in powering it without problems? What service would I need at the shop? I'm not an electrician, just a machinist, so I don't know much about it. Thanks for any help.


The machines power specs are as follows:

Haas VF3

14 kVA;
200-250 VAC @ 50A, 3-phase;
50-60 H

Thanks

Jimmy
Reply With Quote

  #2  
Old 07-21-2007, 10:20 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

You did not say if more than one machine.
But you need a 220 v 100amp 1 phase minimum, if just the one and to allow for other accessories etc.
If you are looking to expand in the future and you are putting a new service go for a 200amp service.
This should offset the chance of brown-outs & voltage drop due to sudden current demands.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 07-21-2007, 10:56 PM
 
Join Date: Nov 2006
Location: US
Posts: 45
conceptmachinin is on a distinguished road

Al,

thanks for the help. It is just for the one machine, but I will also need to run a air compressor to supply air for the machine. I was wondering, what size of a Phase Perfect I would need for the mill? I may one day put another mill in also, so that is in the picture too.

Thanks again.

Jimmy
Reply With Quote

  #4  
Old 07-22-2007, 09:25 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

If you still have the machine connected to 3ph supply, you could take a current reading of the machine with a heavy spindle load to see what the machine typically draws on heavy load and then request a recomendation from phase perfect, of course if you are thinking of expanding then you need an estimated load figure of what you may be looking at in the future.
Also what the compressor draw is.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 07-22-2007, 10:04 AM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,565
Geof will become famous soon enough

Originally Posted by conceptmachinin View Post
......but I will also need to run a air compressor to supply air for the machine.....Jimmy
If you have scanned through various threads you might have seen mention of compressors causing problems to other machines when they kick. It might be worth thinking about a separate unit for the compressor; or get one sized for two machines and when the second machine is installed then move the compressor to its own unit.

Regarding measuring the spindle load as Al suggests taking a reading under cutting conditions may give a value that is below the peak. On Haas machines there is a Parameter (or Setting) called Spindle No Wait.

When this is turned on and the line following the M03/M04 command has a G00 the controller does not wait for the spindle to come to speed it overlaps the spindle acceleration with the rapid move.

This is your peak load when the spindle motor and up to three servos may be drawing 195% of full load. On a VF0 where the machine specs called for a 40mps maximum draw with a biggest single load of 35amps I measured 50amps.

It is possible to turn off Spindle No Wait and it is also possible to set the maximum spindle acceleration lower than 195% but both these work arounds for an inadequate electric supply have an effect on cycle time.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Reply With Quote

Sponsored Links
  #6  
Old 07-22-2007, 10:49 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

One thing I forgot to mention, if the Haas has any single phase source wired across two phases e.g. control power, servo or other power supply power, make sure these are across the two main 240v 1 phase feeds, that enter and exit the Phase Perfect. These provide two of the phases that are relatively stable compared to the artificial phase by the PP.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 07-22-2007, 12:23 PM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,565
Geof will become famous soon enough

Originally Posted by Al_The_Man View Post
One thing I forgot to mention, if the Haas has any single phase source wired across two phases e.g. control power, servo or other power supply power, make sure these are across the two main 240v 1 phase feeds, that enter and exit the Phase Perfect. These provide two of the phases that are relatively stable compared to the artificial phase by the PP.
Al.
Yes, coolant pump at least 1hp, may be more.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Reply With Quote

  #8   Ban this user!
Old 07-22-2007, 01:02 PM
 
Join Date: Oct 2006
Location: usa
Posts: 36
awright is on a distinguished road
3-phase power issues

In your situation, I'd consider shedding off the locally generated 3-phase line all equipment that does not REQUIRE 3-phase power for proper operation. This, of course, depends upon the function and power demand of each piece of equipment.

Before people react negatively, I fully realize the advantages of 3-phase power over single-phase in such equipment as compressors, especially as the power exceeds about 2 HP and goes into the region where single-phase motors are hard to find and expensive. However, when you are generating your own 3-phase power locally, peak demand becomes a serious limiting factor.

I'd look first at your coolant pump and air compressor to see if it is practical to convert them to single phase power. The start cycle of an air compressor is an especially large instantaneous current draw that would be beneficially removed from the phase converter. It will draw even larger instantaneous current off the single-phase line, but that is much more easily handled by your direct line power feed than by your phase converter. If your compressor is large enough that it requires a 3-phase motor, do you actually require that much air delivery? Can you go with a smaller compressor or even two smaller ones that will cycle at different instants of time, thereby reducing the peak demand and allowing single-phase power?

Just a thought.

awright
Reply With Quote

  #9  
Old 07-22-2007, 01:09 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by awright View Post
I'd look first at your coolant pump
I think Geof just indicated it was already 1ph
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 07-22-2007, 10:47 PM
 
Join Date: Oct 2006
Location: usa
Posts: 36
awright is on a distinguished road
3-phase power

Well, Al_The_Man, I didn't and still, in rereading the thread, don't see where there is mention of the air compressor being either 3-phase or single-phase or where there is any mention of the power of the compressor. I do see where Geof seemed to be recommending a "separate unit" for the air compressor, by which I assumed he was referring to a separate phase converter. Frankly, I don't see the economics of buying a phase converter dedicated to an air compressor alone, as opposed to buying a single-phase motor for the compressor unless it is a relatively high powered compressor (above about 2 HP).

Remember in evaluating the power demand of a compressor that the industry has gotten away with rating modest sized compressor motors that draw current equivalent to an honestly rated 2 or 3 HP motor as a "5 HP compressor-rated" motor. In my opinion, this is pure hokum that has evolved as a competitive gambit in compressor marketing. Look at the actual current draw and "LRA" (Locked Rotor Amps) of the motor you are considering. The LRA is the instantaneous current draw when power is first applied to the motor with a stationary rotor. It only lasts only a fraction of a second until the rotor picks up some speed and begins generating back-EMF to reduce the current toward operating current, but it can play havoc with a phase converter or a weak power source.

I am a strong advocate of VFD phase converters for the home shop and have used a 3 HP converter for several machine tools in my home shop for about 30 years. But I'm not sure that the economics work out for running a moderate size compressor alone, as Goef appears to recommend. As far as I see, we never did hear back from Jimmy on the phase or power of his compressor or coolant pump or other accessories. I admit that I have never used a rotary phase converter and have never required 3-phase power for more than a 2 HP motor.

awright
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 07-22-2007, 11:03 PM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,565
Geof will become famous soon enough

I mentioned the compressor in one post and the coolant pump in a different one. The pump control is internal to the machine so if you were trying to put it across the main 240 phases you would likely need to trace some wires.

Regarding the compressor surely moving it to a single phase motor would, if it was originally three phase, be more expensive than getting a larger phase convertor or a separate one.

Although thinking further I would expect putting the compressor on a VFD with a soft start capability would be best and probably in the same cost region as a single phase motor for any decent size compressor.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Reply With Quote

  #12   Ban this user!
Old 07-25-2007, 09:52 AM
 
Join Date: Nov 2006
Location: US
Posts: 45
conceptmachinin is on a distinguished road

hey guys, sorry it took me so long to get back. The air compressor is currently running off single phase 220. I hope that helps. I don't know the amp draw but I'm sure I can ask my partner to check it for me. I'm debating selling the mill then buying new....maybe a mill that doesn't require airblow, as the thing darn near runs all the time and is annoying. I found out from the electric supplier that I can get up to 1000 amp service. I talked to him about 3 phase and it seems it would be a bunch of money somewhere around 10,000 just to get it by the land, then I would run the wire from the shop underground to the pole. Hmmm...

Its kinda strange. My shop right now is on a gravel road about 1/2 mile off the same highway that I'm moving too. Its just really funny because There is service off the gravel road, but none 1 mile down the main highway. What a complete drag

Last edited by conceptmachinin; 07-25-2007 at 09:56 AM. Reason: wanted to add more
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
phase converter contractdesign Bridgeport and Hardinge Mills 8 05-30-2007 03:39 PM
VF-2 on a phase converter? Dugg Haas Mills 33 03-04-2007 12:06 PM
DIY phase converter? wyobmf Phase Converters and VFD 9 07-26-2006 04:37 PM
RF from phase converter ? DieGuy Phase Converters and VFD 1 10-20-2005 07:14 AM
3 phase converter? jevs General Metal Working Machines 5 02-16-2005 01:40 PM




All times are GMT -5. The time now is 08:43 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361