Apparent issue with SJ200 & Leeson 3ph 2HP motor

Hi All,

Prior to the recent holidays, I acquired a Hitachi SJ200-022NFU (capable of accepting 1 and 3 ph line power) and a Leeson 2HP 3ph 3400RPM motor.

I have 240 1ph service into the shop via a subpanel breakered at 60A at the main panel. Until now, the breaker feeding the subpanel has never tripped.

I connected the line and load wiring precisly as defined in the manual (2 legs of the 240 line power going to L1 and L2 and neutral going to the N/L3 lug while the VFD to motor connection is U to U1, V to V1, and W to W1). I also have the chassis ground of the motor connected to the chassis ground of the VFD. As my line power receptacle does not currently have a ground lug, I left the line side of the VFD ungrounded. I'll get a ground wire and appropriate recptacle prior to actual install and operation.

After double checking my connections, I plugged the power plug into the wall socket and shop immediately went black. None of the local subpanel breakers tripped, but the the 60A breaker did. This was an instantaneous, do not pass go event.

I have since looked over everything again, and all connections seem to be preceisly as they need to be. I have checked for shorts in all of my cables and plugs--all are as prescribed. I also checked the 240 circuit and everything checks out voltage wise.

I am stumped and unsure what to do next. I'm reluctant to plug it in again because I have changed nothing since the trip. I could sure use some advice. I am definitely out of my element here.

Thanks,

David
Tweet this Post!Share on Facebook
Reply With Quote

  #2  
Old 02-07-2007, 05:04 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

I have never heard of connecting a VFD up with the neutral when using 1 ph, I think if you check the manual, the L1 & L3 is used for the 240vac, you may need to jumper the L1 & L2 terminals, Also Do you have a jumper in place now?
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 02-07-2007, 05:52 PM
 
Join Date: Oct 2003
Location: US
Posts: 43
haysys is on a distinguished road

Well... that would explain my problem wouldn't it. I feel absolutley stupid.

There is indeed a jumper between L1 and L2 and I heartily questioned that--the idea of connecting the two legs of 240 across the jumper defied my understanding of what made sense. But the docs are quite clear that the Jumper must be in place... and I have opinions about people who blindly follow along without questioning. Duhhh...

And indeed I did not intepret the instructions to hook the 2nd leg to N/L3. There were no examples for connecting 1ph power. I did just reread the docs and it does indeed say (in bold no less):

"...for single phase power, terminal [S/L2] will remain unconnected." Now it makes sense.

One final question then: Is the neutral connected to anything? Or does it just float?

Thanks for your attention Al. You have answered hundreds if not thousands of questions here, and I'm quite certain that we all greatly appreciate the energy and knowledge you so generously share.

Thanks!!!

David
Tweet this Post!Share on Facebook
Reply With Quote

  #4   Ban this user!
Old 02-07-2007, 07:40 PM
 
Join Date: Jan 2005
Location: USA
Posts: 2,165
mactec54 is on a distinguished road
Buy me a Beer?

Hi you sure do have a problem you my have fryed the drive as well
The L1 & L3 are what you have to use for your single PH 240 input
L2 you do not connect any thing to it

Some drives L1 can be jumpered to L3 but I'm not sure with your drive
Yaskawa you can

The neutral was one of your problems as you created a dead short
and do not jumper L1 & L2 that to could be a dead short

You can use the Neutral as a ground wire if you do not have a ground but put some green heat shrink on it

Do not run the drive without a ground to the power source you are just
asking for trouble or Electrocution I'm surprised that AL The Man did not say
this by wiring this way you made your whole machine live with no Ground to
protect you.
__________________
Mactec54

Last edited by mactec54; 02-07-2007 at 10:41 PM.
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 02-07-2007, 08:00 PM
 
Join Date: Oct 2003
Location: US
Posts: 43
haysys is on a distinguished road

Mactek,

Thanks for your response.

Seems like what you and Al said are in contradisction. L1 and L2 have a jumper. As I said in my second post, the docs do say "L2 will remain disconnected".

Anyone else withan SJ200 powered with 1ph?? How did you connect it???

Thanks,

David
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6  
Old 02-07-2007, 09:06 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by mactec54 View Post
You can use the Neutral as a ground wire if you do not have a ground but put some green heat shrink on it

Do not run the drive without a ground to the power source you are just
asking for trouble or Electrocution I'm surprised that AL The Man did not say
this by wiring this way you made your whole machine live with no Ground to
protect you.
I did not allocate using without ground, but you do NOT use neutral as a ground wire, ever, this violates the E.Code.
In fact you do not use neutral at all in VFD installation.
The manual states using L1 & L3 for the 240v 1ph. The L1 & L2 are jumpered to allow a bit of extra DC capacity on 1 ph.
The ground is connected in the usual way to the ground lug.
By having a short circuit across the 240v, you probabally blew the breaker before any damage was done.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 02-07-2007, 10:53 PM
 
Join Date: Oct 2006
Location: USA
Posts: 30
JRaef is on a distinguished road

Connection of the L1 and L2 with a jumper is unnecessary, it gives you no "extra capacity" since all the AC input does is provide the raw power for conversion to DC. The capacity of those 2 diodes will be greater, but the total input capacity is still dictated by the other 1/2 of the circuit anyway, so it makes no difference. They recommend making that jumper connection just to satisfy the people who insist on connecting wires to unused terminals, PRECISELY so that they are not compelled to connect the neutral! Now that you have, you most likely blew the input diodes, i.e. your drive is toast. Sorry for the bad news. The only possible saving grace is if by some miracle, the breaker cleared before the diode popped. Highly unlikely though. In that world, breakers are painfully slow.
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 02-07-2007, 10:55 PM
 
Join Date: Oct 2003
Location: US
Posts: 43
haysys is on a distinguished road

Thanks Al,

Understood and thank you. I'll hook it up tomorrow and let all know if the breaker did the additional job of protecting the unit.

Regards,

David
Tweet this Post!Share on Facebook
Reply With Quote

  #9   Ban this user!
Old 02-07-2007, 11:02 PM
 
Join Date: Jan 2005
Location: USA
Posts: 2,165
mactec54 is on a distinguished road
Buy me a Beer?

Hi I did type it wrong and I changed it to L1 & L3 for these Hitachi drives should be connected for 240 V single PH and AL you can use any wire you want as long as it is correctly colored or marked so it is clear what that wire is, this does not Violate any codes.Also as J Raef has said you do not have
to jumper L1 & L2 for it will have no gain

Yaskawa VFD Drives are L1 & L2 for single PH
__________________
Mactec54
Tweet this Post!Share on Facebook
Reply With Quote

  #10  
Old 02-07-2007, 11:17 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

The blocking action of a 3 phase bridge should cause no conduction from live to neutral if a neutral was so connected to a phase input.
My point about the ground was that you violate the code if you use the neutral as a ground.
The system neutral should be only grounded at source, and this applies to local supplies where a local neutral is set up.
The only reason I mentioned the link was to quote the manual for David's information.
It probabally does not matter what pair you use, as the input usually enters to a 3 phase bridge, the alternative is where there is a 1 phase ac control source connected to a particular pair.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 02-08-2007, 08:53 PM
 
Join Date: Oct 2003
Location: US
Posts: 43
haysys is on a distinguished road

Hi all...

I went to the shop and hooked up everything from scratch, with the two legs of my 1ph 240 to L1/L2 (jumpered) and L3. I clipped and wire-nutted the neutral wire. I also ran a dedicated wire from the VFD ground to Earth ground. The 3ph motor is hooked up as previously stated (U,V & W plus ground).

I plugged the VFD in and... (drum roll) the breaker tripped again.

So unless anyone has any other thoughts, I suspect I cooked the VFD. I think I'll call Hitachi tomorrow, bare my soul, and see what can be done.

Thoughts???

Thanks again,

David
Tweet this Post!Share on Facebook
Reply With Quote

  #12  
Old 02-08-2007, 09:16 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

Doesn't sound good, try powering up without the motor connected, just to confirm if it is the supply input problem.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Issue at low power.... WilliamD Laser Engraving & Cutting Machines 2 12-02-2006 12:44 AM
Homing Issue Moondog Machines running Mach Software 3 07-29-2006 11:23 PM
Help with selector switch wiring issue (***actually a motor issue***) BEDFORD Industrial Hobbies (Support forum) 7 04-07-2006 04:19 PM
Parallel Relay Board & Z-motor brake issue Liv2fish2 Machine Problems, Solutions , Wireless DNC, serial port 0 02-06-2006 12:35 PM
THC Issue Aldoseri CamSoft Products 3 01-31-2006 05:33 AM




All times are GMT -5. The time now is 01:45 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353