Question How to balance voltage on 3 phase?

OK, I finally got the phase converter running. Had the 110v leads hooked up to the wrong wires. I'm currently reading the following voltages:
Lead 111 to 112 = 241 volts
Lead 112 to 113 = 211 volts
Lead 111 to 113 = 224 volts

My CNC calls for 230 volts, so how do I balance these out so the CNC works properly???

I had to connect the 110volt leads to 111 and 112 wires. Now that the phase converter is putting out the higher voltages do I then come off these three leads #'s 111,112 & 113 to feed the machine? I know this sounds dumb, but I had to ask. Do I use caps to adjust the voltages so they are all the same and I've read somewhere about one of the legs being like nutural(for lack of the proper word) and how do I know which one that is? Are there any special ways the three leads get attached to the machine?

I know these all sound dumb, but I have no expereince in phase converters or using three phase.

ben
Tweet this Post!Share on Facebook
Reply With Quote

  #2   Ban this user!
Old 11-02-2006, 12:35 PM
 
Join Date: Mar 2006
Location: USA
Age: 69
Posts: 55
Jack F is on a distinguished road
Use oil filled run capasitors.

Put the capasitors between the two powered legs and the 3rd generated leg. look on this site for several plans showing where to connect them and the starting values for your application. the desired result is to be within 10% on all legs.
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 11-02-2006, 12:54 PM
 
Join Date: Mar 2005
Location: united states
Age: 59
Posts: 4
tonykart91 is on a distinguished road

Inside the phase converter control box are a few capacitors. The capacitors hold a will not pass AC voltage, so they build a charge when the AC sine wave is on the positive side and discharge on the negative side of the wave (very simplistic). The MFD rating of the capacitor determines the rate at which it builds and discharges. So by increasing or decreasing the total MFD rating of the capacitors, you can shift the voltage and to some degree the angle of the manufactured leg.
To adjust the voltage, adjust the number or MFD rating of the capacitors. Load will also effect the voltage some. It's pretty hard to adjust the voltage with an adjustable load or no load. You can get it close though.
Motors can handle about 10% voltage imbalance, but electronics like it alot closer.
Tweet this Post!Share on Facebook
Reply With Quote

  #4  
Old 11-02-2006, 01:00 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

Go here http://www.metalworking.com/dropbox/...retired_files/ and look at all the files that start with FRW- They include a schematic and tuning method.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 11-03-2006, 02:42 AM
 
Join Date: Nov 2006
Location: US
Posts: 3
Powertoolman is on a distinguished road

No, this is not a stupid question. It is refreshing to hear that someone pays enough attention to the concept to even ask about balancing a converter.

Your converter is not that far out of balance, but it can be better. Yes, you tune the converter by changing the capacitors. The best way of doing this is trial and error by changing the capacitance of the two banks of capacitors. The closer you get to all three line-to-line voltages being equal, the better your converter will perform. Here is an image I created for a recent posting on another forum. The values are not the same as yours, but I hope it explains why the voltage balance is important.



The best way to balance the converter is to create a table of the voltage results. As you increase or decrease each bank of capacitors, you can see the results in the table.

My article on building a converter explains this better and shows an example of the table as well as how I chose the best values. I haven't updated my article in a few years, but it is in the works. The graphic above was created for the new re-write.

Building a Phase Converter

Oh, I almost forgot, but you never use the Neutral wire with a phase converter. If anyone ever tells you otherwise, you need to run away fast.

=============
By the way tonykart91, capacitors pass AC and block DC, not the other way around. Changing the capacitance alters the phase angle of the AC signal by tuning the capacitor size to the windings of the motor. This is analogous to tuning a radio because it is tuning an RLC circuit.

Rick Christopherson
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 11-03-2006, 02:49 PM
 
Join Date: May 2006
Location: US
Posts: 201
bherr is on a distinguished road

Rick,
Thanks for the help. I currently only have the phase motor, no capacitors were included, unless they are inside the motor. I copied your article to read and if I can follow your directions I'll proceed. I have found a local company that builds phase converters so maybe I can get them to balance it out for me, as purchasing different capicators could be time and money consuming. Again thanks for the help.
ben
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 11-05-2006, 08:01 AM
 
Join Date: May 2006
Location: US
Posts: 201
bherr is on a distinguished road

got the phase converter up and running and balanced to 234 on t1-t2, 233 on t2-t3 and 224 on t1-t3. got the tables moving now I just need to start reading .
thanks for all the help.
Ben
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 11-05-2006, 12:36 PM
 
Join Date: Nov 2006
Location: US
Posts: 3
Powertoolman is on a distinguished road

Originally Posted by bherr View Post
got the phase converter balanced to 234 on t1-t2, 233 on t2-t3 and 224 on t1-t3
That's a good job on the balance. Your generated leg is only 1-1/2 degrees from ideal. (Or using the diagram I drew previously, the purple line is only 2 degrees below horizontal.)
__________________
Rick Christopherson
Tweet this Post!Share on Facebook
Reply With Quote

  #9   Ban this user!
Old 11-05-2006, 07:49 PM
 
Join Date: May 2006
Location: US
Posts: 201
bherr is on a distinguished road
Talking Thanks

Rick,
thanks, couldn't have done it without your very easy to understand article. got the machine up and running, all axis moving. Haven't tried the spindle yet as far as turning it on. Had the Y axis locked on the limit and it took me awhile to figure out how to get that off, but finally did. Now I've got to learn this Heidenhain 155B control. It doesn't appear too dificult.

Again thanks for the help.

ben
Tweet this Post!Share on Facebook
Reply With Quote

  #10   Ban this user!
Old 12-25-2010, 12:28 PM
 
Join Date: Dec 2010
Location: usa
Posts: 2
precise cabinet is on a distinguished road
balancing my phase converter

Hi All,
Powertoolman (Rick)

I have also built a 20 hp phase converter and have it starting and running but my voltages are way off. L1= 120 volts to ground, L2= 121 vtg, and L3= 240 vtg. Also the idler motor starts very loud and vibrates stuff off shelves. I hooked up the idler according to the nameplate for 220 V i.e. L1 connected to motor wires 1-7-6, L2 to 2-8-4, and L3 to 3-9-5. One article I found said to hook op the idler differently. Please Help!
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11  
Old 12-25-2010, 12:53 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

First, you never read the voltages to ground, the only useful reading is between phases.
You need to make sure the motor is connected in the 220 volt mode if it is dual voltage.
Here is a link to the different configurations of motors, your is most likely a wye connected dual voltage, see B109144 here.
Connections
See the link in post #4 for tuning.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #12   Ban this user!
Old 12-26-2010, 04:26 PM
 
Join Date: Dec 2010
Location: usa
Posts: 2
precise cabinet is on a distinguished road
balancing my phase converter

Thanks Al
Well that didn't work. I was not able to read voltage because the motor made such a loud noise I shut it down. I'm thinking that perhaps I have a bad motor. I bought it from a reputable dealer so I wonder if maybe it was re- wound in the past. Also the voltages that I noted earlier are consistent if you go phase to phase. Phase 1-2 =241, 1-3 = 351, 2-3 =350.
Thanks
Chris
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 07:03 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353