480v Vfd

Can I use a VFD that normally accepts 480V in and use 240v instead?
Tweet this Post!Share on Facebook
Reply With Quote

  #2   Ban this user!
Old 10-18-2006, 09:51 AM
 
Join Date: Aug 2006
Location: USA
Posts: 16
z28tt is on a distinguished road

hoju1301 - Have you found any more info on this? I've seen many more 400V class inverters on Ebay, which would be an inexpensive way to get started. Are most 400V units strictly 3 phase input, and need to be derated appx 50% for single phase? Any units (sized 2-10 hp) that have phase loss monitoring that can't be disabled that we should stay away from?
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 10-18-2006, 07:17 PM
 
Join Date: Mar 2006
Location: USA
Posts: 21
hoju1301 is on a distinguished road

Originally Posted by z28tt View Post
hoju1301 - Have you found any more info on this? I've seen many more 400V class inverters on Ebay, which would be an inexpensive way to get started. Are most 400V units strictly 3 phase input, and need to be derated appx 50% for single phase? Any units (sized 2-10 hp) that have phase loss monitoring that can't be disabled that we should stay away from?

yep. there are a ton of 400-500v vfd's on ebay that are cheaper than the 240v ones. i may end up buying one just to try it out. im probably in the same boat you are. the only snag right now is i need one that can do a high frequency (400hz) for a machine spindle.

what hp rating are you looking for? ac tech has a model with 5hp with a single phase 240v input. i got quoted around 400 for it and it has a ton of features.

there is also automation directs new line of vfds that are very competivly priced. current deration is i believe 1/3 if you use single phase but im not sure. a few have posted here using a 3ph vfd on single phase input.

ill let you know what i find out if i do end up buying one to try out.
Tweet this Post!Share on Facebook
Reply With Quote

  #4   Ban this user!
Old 10-18-2006, 10:03 PM
 
Join Date: Aug 2006
Location: USA
Posts: 16
z28tt is on a distinguished road

I'm looking at the Hitachi SJ200's and L200's, as well as the Teco FM100's, or possibly a GS something from Automation Direct. They all seem to be about $200-$300. This is for a 2hp lathe motor... I'd be happy with "cheap and works" and give up the features for now, and treat it like a simple phase converter.

Andris
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 10-20-2006, 06:28 PM
michaelvw's Avatar  
Join Date: Aug 2004
Location: Netherlands
Posts: 26
michaelvw is on a distinguished road
Don`t try it

Hello,

You can not use 230 V single fase for the input as the input should be 480 volts 3 fase. Don`t try it because it will not work.

Cheers,

Michael
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 10-20-2006, 11:22 PM
 
Join Date: Jun 2003
Location: Boalsburg PA
Posts: 844
unterhaus is on a distinguished road

I don't think it will work, but really there isn't any reason why the manufacturer couldn't make it work. Just a matter of software. It would have to be a very crudely designed machine not to have problems.
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 10-21-2006, 02:13 AM
michaelvw's Avatar  
Join Date: Aug 2004
Location: Netherlands
Posts: 26
michaelvw is on a distinguished road

Hello,

Also don`t try 480 volts on a 240 volts VFD, I`ve seen VFD were this is tryed and the will explode. The capicitor in them will explode, at my work i`ve seen this because poeple use wrongly conected power source. Even a 240 volts models only conected to 1 fase and no neutral conected can lead to a explosing.

Michael
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 10-21-2006, 04:43 PM
 
Join Date: Jun 2003
Location: Boalsburg PA
Posts: 844
unterhaus is on a distinguished road

high voltage caps are expensive, and nobody is ever going to design that much margin in. But putting in lower volts is safe.
Tweet this Post!Share on Facebook
Reply With Quote

  #9   Ban this user!
Old 10-28-2006, 07:07 PM
 
Join Date: Oct 2006
Location: USA
Posts: 30
JRaef is on a distinguished road

Theoretically you can apply 240V to a 480V VFD, but why?

First off, you cannot go by HP, you can only go by current because a 240V motor is going to draw twice as much current as a 480V motor at the same HP. So if you compare prices based on current ratings, you will see that 480V drives are more expensive; they have more expensive components (only 10% or less of each transistor production run will pass muster for the peak voltages seen in 480V systems).

Secondly, since there really isn't such thing as 480V 1 phase power (except in some far flung farms), VFD manufacturers don't go to the expense of oversizing the capacitors for 1 phase operation, even on small HP drives as they do in 230V versions. Not only does that mean you must buy a VFD rated for twice the motor current, but since there is less margin for error, most 480V drives then need to have phase loss protection built-in in case a fuse blows and overloads the diode front-end. So if you supply 1 phase power, it will trip on phase loss. Some are available with that feature defeatable, some are not.

Third; most 480V drives have under-voltage protection set for -20% of the DC bus voltage based on their lowest input range of 380V. At 230V input the DC bus will not be high enough to satisfy that. Most VFDs do not allow you to defeat that feature.

Bottom line, even if you can get one cheap on eBay, the average seller will not be able to check these issues out for you, so you may end up buying a VFD that you cannot use. That makes them a lot more expensive!
Tweet this Post!Share on Facebook
Reply With Quote

  #10   Ban this user!
Old 10-28-2006, 09:48 PM
lgalla's Avatar  
Join Date: Jul 2006
Location: canada
Posts: 1,179
lgalla is on a distinguished road
Buy me a Beer?

Why not use a 240 to480 transformer?
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 10-29-2006, 12:38 AM
 
Join Date: Oct 2006
Location: USA
Posts: 30
JRaef is on a distinguished road

That would work as long as the motor was 460V too. But most 460V motors can be connected for 230V, so the only reason would be what?

Again, why not just buy a 230V drive?
Tweet this Post!Share on Facebook
Reply With Quote

  #12   Ban this user!
Old 10-29-2006, 11:26 AM
 
Join Date: Aug 2006
Location: USA
Posts: 16
z28tt is on a distinguished road

Originally Posted by JRaef View Post
Again, why not just buy a 230V drive?
earlier...

Originally Posted by Z28tt
I've seen many more 400V class inverters on Ebay, which would be an inexpensive way to get started.
After attempting to win something on Ebay for 2 weeks, I gave up and bought a Hitachi SJ200-015-NFU, so yes, I bought a 230V single phase drive.
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 05:46 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353