If the VFD is capable of running off of 1ph then you should be OK, you may not be able to get the maximum power from the motor, as usually there is some de-rating, there are makes out there that claim no de-rating on 1ph, the deciding limitation in a VFD is maximum current, and you can usually limit that by parameter.
If the DC Buss voltage is not sustained as much as on 3phase then the derating applies.
Al.