Hey guys I've all but finished my very first cnc build but... Im tring to work out how to wire up a Commander SK VFD for 220v single phase input and was hoping that someone could help point me in the right direction to get my spindle spindlizing... The model number is SKCD200220 (it's 1+3 phase) so far I've worked out; mains+ goes to VFD L1 mains- goes to VFD L3/N (for 220v single phase) Where does mains ground go? or not?? Sorry if this is a stupid question. I'd also love to learn how to hook it up to mach3 if anyones done that before? I have a dmm-tech DMB4250-8B break out board thanks for tyour help firstyear |
| It doesn't make any sense to me that they show a ground connection (ground symbol) as well as a PE Service ground connection and a motor frame ground, they should all be the same? OK I see a link over from one to the other, so that makes sense now. Al.
| Hi Al thanks for the reply - That had/has me stumped too. the "ground symbol" goes to the motor so Im guessing that one's ruled out? Which leaves 2 x PE. Do you think I should wire it to the '1st' PE which loops to the "ground symbol"? |
| They should all be linked and common to each other, I assume the optional ground shown on the motor is a ground stake. The frame of the motor should go to the service ground connection. Al.
Hi, Page 7 of the DMB4250 User manual looks to be a good reference. I'm assuming that VFD spindle drive is the Commander SK. You need to cross reference this with the diagram on the rear cover of the Commander SK getting started guide. Terminal T3 is the 10V Terminal T4 is the analog volt input Terminal T1 is the analog ground (0V) Terminal B5 is FWD / STOP Terminal T1 is also the digital ground Power wiring can be found on page 13 of the getting started guide. I've got an issue 8 manual. You then need to follow the quick start commissioning section to set up the drive for the motor - see page 42 This is assuming that the motor is an induction type motor. Regards Jon A |
| firstyear Were you have the question mark just make sure that terminal is ground to the chassis/mounting frame of the VFD, if it is then you can use it/them for your input AC ground Check the PE Terminals as well it looks like you can use one of those as well for a ground
__________________ Mactec54 |
| firstyear The first thing you want to do once you have it wired, is put all your motor parameters in, then you will be able to test run the spindle before you, wire to the breakout board Attached are the Breakout Board & Mach setup
Hi Mactec, Jon and Al thanks so much for your help I just heard back from Craig at Control Techniques America who confirms what we found... -Connect the mains ground to the first PE terminal, the PEs and earth are all connected together. Use terminals L1 and L3 for your mains input - I'l try and keep it simple just incase someone else wants to go down this road.. To wire up a Commander SK to mains 220v single phase input: -for the SKCD200220 use 10mm wire (AWG8) - Mains + goes to VFD L1 Mains - goes to VFD L3/N Mains ground/earth goes to the first VFD PE terminal (first from the left) - Now put all your motor parameters in the VFD, then you will be able to test run the spindle before you wire to the breakout board - Thanks Mactec, Al and Craig To Wire a connection from a Dmm-tech DMB4250-8B Breakout board to a Commander SK VFD: -for the SKCD200220 use 6mm wire (AWG10) - For the AV_OUT (used for spindle speed) +Vin goes to VFD Terminal T3 A goes to VFD Terminal T4 G goes to VFD Terminal T1 DOUT_16 (used for VFD on/off or spindle FWD / STOP???) D16 goes to VFD Terminal B5 S16 goes to VFD Terminal T1 - Now follow the Dmm-tech instructions for setting a VFD/spindle in Mach3 - Thanks Mactec and Jon Guys Please let me know if this sounds about right.. Last edited by firstyear; 01-19-2012 at 11:25 PM. |
#10
| Hi guys in terms of wiring and shielding would you all reccomend that I use; * 2 core Shielded wire from mains to vfd, using the Shield as the ground/earth connection at both ends? (mains ground to VFD PE) * 3 core Shielded wire from vfd to spindle, using the Shield as the ground/earth connection at both ends? (VFD ground "ground symbol" to motor ground) In both cases I would be using the shield as the ground wire... is this ok? Or should I just wrap the shielded wire ends around my ground wire; * 3 core Shielded wire from mains to vfd, winding the Shield around the ground/earth connection at both ends? (mains to VFD) * 4 core Shielded wire from mains to vfd, winding the Shield around the ground/earth connection at the VFD end only? (VFD to spindle motor) Hope this makes sense?? Thanks firstyear Last edited by firstyear; 01-19-2012 at 06:14 PM. |
#11
| firstyear No that is not ok to use the shield as a Ground, even though they both go to the same place You need 3 core plus the shield if you are using shielded cable You can use flexible conduit that is plastic on the outside & metal on the inside,the metal on the inside if properly installed works just like a shield, but most of the time the right cable can be easier to use For your AC Input 220v to the VFD the conduit will work well, from the VFD to the spindle motor Cable would be best
#12
I would have thought 4 wire or 4 core, 3ph and ground? Saves running a separate ground. Also offers good protection. Going this route you would use common TEW or MTW single conductor stranded, 3 conductors tightly wound and the ground ran alongside the 3. Al.
| Emerson AC servo driving | triag | Servo Motors and Drives | 6 | 03-26-2011 10:16 AM |
| EB-205 Emerson Servo Drive | marcelomorton | EBAY ADS | 0 | 02-24-2011 04:21 PM |
| Help with wiring! | SatanKlawz | DIY-CNC Router Table Machines | 4 | 04-12-2010 08:40 AM |
| Need Help!- Wiring a 220v DOERR/Emerson Compressor Motor | Thazul | General Electronics Discussion | 5 | 01-14-2010 02:29 PM |
| Mill Commander | rcazwillis | General CNC (Mill and Lathe) Control Software (NC) | 0 | 05-28-2005 08:16 PM |