Question AB 1336-IMPACT "GROUND FAULT"

Hi All,

I have an AB 1336-IMPACT drive, 460v 3ph 10HP. It will run fine for various periods of time but then trips-out with a "ground fault" #12018. The vfd and the motor and wiring have all been checked numerous times and no ground has been found. Incoming power is fine and I have 5 other identical vfd's running the same type of machinery with no problems. Any ideas? Thanks.

Matt
Reply With Quote

  #2   Ban this user!
Old 11-30-2011, 03:13 PM
 
Join Date: Sep 2010
Location: usa
Posts: 839
mike_Kilroy is on a distinguished road
Buy me a Beer?

does your motor power cable move (like in a wiretrack)? If so, check again for a metal chip or frayed area that only shorts at a certain location of the track.... not uncommon....

another thing we have found is a loose screw on a terminal strip in series somewhere between the motor and drive, in case u may have any connections between the two....

lastly it is not uncommon if motor has a connector on it, to have it fill with cutting fluid, or have a short that comes and goes....

the bad news is that the vintage of that drive is such that if you don't find it soon you probably will be buying a replacement drive as the ground fault protection works like 60% of the time (60 times out of a hundred - that 61rst blows the output IGBTS), the good news is a lot of folks say you can buy this drive on ebay for $ 50 most anytime (in other forum threads on here).....
__________________
Mike (at) KilroyWasHere.com -- machine tool servo repair, retrofit
Reply With Quote

  #3   Ban this user!
Old 12-01-2011, 06:18 AM
 
Join Date: Dec 2009
Location: United States
Posts: 10
mkovac is on a distinguished road

Thanks for the reply. Unfortunately, our application of this drive is in a very dry environment, none of the cabling moves and this thing will trip out without the motor even connected. We use this drive to build coils for large power transformers. The really bad part is I just received the drive back from Rockwell Automation for repair at almost $2,000. I'll start watching ebay. Thanks again.

Matt
Reply With Quote

  #4  
Old 12-01-2011, 10:07 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by mkovac View Post
The vfd and the motor and wiring have all been checked numerous times and no ground has been found.
Matt
Has the motor been checked with an insulation Megger to ground?
This instrument places a high voltage on the stator in order to detect ground leakage that may not show up with a low voltage VOM.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 12-01-2011, 10:52 AM
 
Join Date: Dec 2009
Location: United States
Posts: 10
mkovac is on a distinguished road

Our megger has been on loan but is due back this afternoon/tomorrow morning. Will definitely run this test upon arrival. Thanks.

Matt
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-01-2011, 04:50 PM
 
Join Date: Sep 2010
Location: usa
Posts: 839
mike_Kilroy is on a distinguished road
Buy me a Beer?

Originally Posted by mkovac View Post
..... this thing will trip out without the motor even connected....
Matt
Matt, if it trips w/o the motor even hooked up, why megger the motor?
__________________
Mike (at) KilroyWasHere.com -- machine tool servo repair, retrofit
Reply With Quote

  #7  
Old 12-01-2011, 07:32 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

I missed that bit?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 12-02-2011, 06:08 AM
 
Join Date: Dec 2009
Location: United States
Posts: 10
mkovac is on a distinguished road

Good point, but could a problem with the motor or wiring have caused another failure in the drive?.... Probably, but the the failure would not be intermittent, right? We will megger the motor this morning for piece of mind if nothing else. Thanks again.

Matt
Reply With Quote

  #9  
Old 12-02-2011, 10:40 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

There is also a possibility that one of the IGBT's in the drive output could have a weak insulation problem that flashes over due to the high harmonic spikes that are inherent in these type of drives.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 01-04-2012, 06:51 PM
 
Join Date: Nov 2008
Location: United States
Posts: 9
Foogl is on a distinguished road

If you have identical drives, I would swap it with other one to see, what will happen. Same VFD will fail => bad VFD, VFD on same machine will fail => cables or motor.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 01-05-2012, 05:57 AM
 
Join Date: Dec 2009
Location: United States
Posts: 10
mkovac is on a distinguished road

I did have an identical drive and we installed it in the machine once we were sure that the machine itself was ok. With this second drive installed we had no motor movement at all. Both of these drives are currently at Rockwell being re-evaluated. I hope to have an answer soon and will post the result to help anyone else who may run into this situation. a very long and frustrating process. Thanks for the input.

Matt
Reply With Quote

  #12   Ban this user!
Old 02-21-2012, 07:06 AM
 
Join Date: Dec 2009
Location: United States
Posts: 10
mkovac is on a distinguished road

Hi all,
The local Allen-Bradley Rep stopped by and personally verified the problems we are having. He gave us a completely different drive to replace the one with the ground fault problem. This machine is now up and running. The other drive was determined to have a weak onboard 10 vdc supply. This drive is being sent back to Rockwell for repair again. Thanks.

Matt
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
allen bradley impact 1336. najnielkp Phase Converters and VFD 3 04-18-2010 07:25 AM
Need Help!- GECKO G540 - Stuck in "FAULT" mode.. HELP!?! CNC74 Benchtop Machines 5 02-06-2010 02:37 AM
Need Help!- Fanuc 18i-T "1114 main spindle orient fault" Jeff_Mezzo Fanuc 3 01-28-2009 08:30 PM
"amplifier fault on axis" on fadal VMC 15 siquedude Machine Problems, Solutions , Wireless DNC, serial port 0 11-20-2007 05:11 PM
V2XT error message "DRIVE FAULT detected (0,z,y,x) check log" rfdoyle Bridgeport and Hardinge Mills 4 10-08-2007 03:35 PM




All times are GMT -5. The time now is 08:41 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361