I am having some noise issues on my VFD. I just wired it in using the factory Hurco wires for the spindle motor. The noise is leaving diagonal/interference lines on my Mach 3 tool path screen. The listings on shielded cable for driving the motor from a VFD, they want to sell me 100ft or 250 foot. I need probably 12 or 15 foot. Thanks for the help, JAckal
__________________ Everything is bio-degradable, if you run over it enough times with the lawnmower. |
|
#2
| ||||
| ||||
| Have you followed good grounding practice? How are you running the cable from VFD to motor? Normally you can get away with twisting the VFD to motor 3 conductors tightly and run in liquid seal flex conduit. Make sure you have run the ground from VFD to motor. Is your PC case grounded? Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
|
#3
| |||
| |||
| Jackal66 Igus will sell what you want by the foot, They also have the best sheilded cable http://www.igus.com/default.asp?PAGE...FYiW7QodGWhURw
__________________ Mactec54 |
|
#4
| |||
| |||
| Right now the factory wires are just (3) 12 ga stranded wire in some rubber coated flex conduit. the motor is grounded from housing to the machine with a ground wire, the VFD is grounded on the power coming in and the cabinet ground star connector. I will run a dedicated ground wire from VFD to motor. I will double check the PC to ground for sure. For the control from the Spindle control board to the vfd I used some ribbon cable just to see if I could wire it right. Tomorrow that will be changed to a shielded cat-5 type cable. If I have to run new wire, that Igus CF31 Chainflex looks like what I need. This mill is close to running. ![]() Thanks guys, JAckal
__________________ Everything is bio-degradable, if you run over it enough times with the lawnmower. |
|
#5
| ||||
| ||||
| Fortunately in all the installations I have done on PC based systems, I have always used the Liquid Seal Flex and had no problems. It is very important to ground from VFD GND to Motor frame. Also it is best to set up a star point ground systems, this has been outlined many times before. http://www.automation.siemens.com/do.../emv_r.pdf?p=1 Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
| Sponsored Links |
![]() |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
| Display Modes | |
| |
Similar Threads | ||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Shielded cable for stepmotors? | mkuivamaki | Stepper Motors and Drives | 2 | 10-31-2008 12:08 AM |
| Shielded versus not shielded cable.....? | REVCAM_Bob | General Electronics Discussion | 1 | 05-23-2007 07:55 AM |
| Shielded cable help please. | Oldmanandhistoy | General Electronics Discussion | 13 | 04-02-2007 07:05 AM |
| Source for shielded cable? | Alex_Cole | Servo Motors and Drives | 1 | 03-25-2007 11:16 AM |
| Shielded Cable | PEU | DIY-CNC Router Table Machines | 5 | 06-13-2006 10:00 PM |