3 phase motor wiring...

Hi I have a big 3 phase electric motor. I am reinstalling it as it needed to be removed for transporting the press it was on. In checking the motor conections I am seeing that the wires in the electrical box are not grouped together as the tag says they should be. On the motor is a tag that shows both the proper set up for 240 volt 3 phase and the proper set up for 480 volt 3 phase. It matches neither. So I am wondering if anyone might be able to tell me if there is any way to check the setup with an ohm meter or in any way test the set up to see if it is connected correctly or not. I would think that if it was not correct it would burn up the motor or be shorted out or something? I don't know...... ugh.

Thanks for any help
Reply With Quote

  #2  
Old 10-03-2011, 11:16 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

If the motor was functioning OK with the present wiring and it will be re-installed using the same voltage, then maybe the prudent way may be to write down the present hook-up and reconnect the same way?
Do you have a diagram or list of the present connections #'s?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 10-04-2011, 07:56 AM
 
Join Date: Jan 2007
Location: United States of America
Posts: 33
WCIS is on a distinguished road

Al is right, if the supply voltage is the same at the machine's destination wire it back up the way it was - assuming of course it IS running correctly at it's present location.

I have seen a few 3 phase delta wound motors straight from the factory with incorrect lead markings. These are relatively easy to read with an ohmmeter and correct. If you make a mistake and wire it incorrectly the motor won't live long at all. I use three analog current meters clamped around each phase feeding the motor and monitor the current when energizing for the first time to be sure it is balanced after the initial inrush. This also is best done at the lowest voltage the motor is rated for to avoid over current within one winding and killing it. At the higher voltage the current will be double it's rating and won't take but a second or two to burn out.

If you must re-tap for a different voltage I would say the safest bet would be to find yourself a competent rewind shop and ask them to have a look at the internals. They should be able to remove an end bell and identify the taps. I have also had motors re-wound that were 12 lead motors before the rewind and 9 lead after. Again, I've sent in 9 lead motors and got back 3 lead motors. When the latter happens the motor isn't dual voltage capable anymore. This may be the reason you see something different.
__________________
Some are destined to achieve greatness. Some are destined for failure and disappointment. While others have failure and disappointment thrust upon them. - WayneC
Reply With Quote

  #4   Ban this user!
Old 10-04-2011, 06:12 PM
 
Join Date: Sep 2005
Location: USA
Posts: 221
REVCAM_Bob is on a distinguished road

Thanks guys, the motor was running, however I had the press inspected and the guy who checked it out put an amp meter on the motor and said it had somewhat excessive draw upon start up. It was hooked to 240 3 phase, and I have 480 in my shop so I sort of need to re tap it.... is there any way to tell without tearing the motor apart? i.e. with an ohm meter or something? If there are some documents or schematics on the internet showing how it all works, is it possbile to figure out? Taking it into a shop is not a good option for me as it weighs about 3 or 4 thousand pounds I am guessing (ugh) and is currently mounted about 15 feet in the air on the press......
Reply With Quote

  #5   Ban this user!
Old 10-04-2011, 06:14 PM
 
Join Date: Sep 2005
Location: USA
Posts: 221
REVCAM_Bob is on a distinguished road

I have both the plate on the motor that shows how it should be connected, and the wires are well marked how they are linked together. I could post both if you think it might help....
Reply With Quote

Sponsored Links
  #6  
Old 10-04-2011, 06:42 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

It may help to see how they actually have it right now.
The excessive draw may be normal, an induction motor is essentially a dead short at actual switch on, it is needed is to bring it up to speed or normal load as soon as possible, motors that are already hooked to a load at switch on, exhibit high current due to a longer power up.
This is why motors that have a high load initially have star-delta starting, or other methods to overcome this.
Imagine a 3 phase transformer with a shorted secondary, this is what the supply see's at switch on.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.

Last edited by Al_The_Man; 10-05-2011 at 03:43 PM.
Reply With Quote

  #7   Ban this user!
Old 10-05-2011, 08:19 AM
 
Join Date: Jan 2007
Location: United States of America
Posts: 33
WCIS is on a distinguished road

Again, Al is correct.

Try to write down how it is connected now and post. Also, post the data plate information along with connection diagrams. If the horsepower rating of the motor is 100+ there may be a soft start circuit involved which will make the actual connection differ from the diagram. Most large motors, as Al eluded to, usually have a two stage start to lower the initial inrush current AND reduce the time the motor windings are in this overcurrent state. There are various ways to accomplish this. Without the data plate and diagram information it's just a shot in the dark on my end.

Do you know if there are magnetic starters that switch power to this motor? Be sure you change the overload heaters or adjust after you get the motor taps changed. Going to the higher voltage and not doing so will leave the motor unprotected. This could save you having to remove the motor after it burns out.

Another question could be is there an electronic soft start and bypass contactors? If so, you must be sure the soft start can handle the higher voltage. In most cases they cannot. OL heaters/settings apply here as well.

As a good practice be sure the motor starters are rated for the higher voltage. There have been only a couple times I've seen foreign equipment utilize motor starters that were rated for 380 (not 480) and they didn't live long at the higher voltage.

Try calling your local rewind shop and ask those guys. You will still need the above information. A pair of trained eyes on the situation is sometimes the best. Fewer mistakes are usually made. You may also find what you need on the manufacturer's website if the motor isn't ancient.
__________________
Some are destined to achieve greatness. Some are destined for failure and disappointment. While others have failure and disappointment thrust upon them. - WayneC
Reply With Quote

  #8   Ban this user!
Old 10-06-2011, 09:45 AM
rmcguire's Avatar  
Join Date: Oct 2003
Location: texas,usa
Age: 65
Posts: 5
rmcguire is on a distinguished road

what about control ckts they maybe wired 230 also, check control xformer and starter ratings as 230 will be large in amp capacity. is mtr old nema or newer mtr. manafacturer"s web site may offer info.
Reply With Quote

  #9  
Old 10-06-2011, 09:48 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by rmcguire View Post
.....and starter ratings as 230 will be large in amp capacity. is mtr old nema or newer mtr. manafacturer"s web site may offer info.
He mentions going from 240v to 480v so the current draw will be less.
The overloads should be changed though, as mentioned earlier.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 10-06-2011, 11:43 AM
 
Join Date: Sep 2009
Location: Puerto Rico
Posts: 7
cflas is on a distinguished road

going from 240 to 480 the windings on the motor need to change from parallel to series. if they are number it is a more simple process but make sure you verify as i have not done this in a very long time. Example you have a delta or wye configuration. more than likely if is 240 is delta wye would be 208. think of a triangle. wires would connect t1 -4-7-10-2-5-8-11-3-6-9-12 -back to 0ne were 1,2 and 3 would be your line voltage. Three phase motors are reverse by changing one line make sure the motor is running in the right directionif not exchange one line with any of the others. Hope this will help and look for delta wiring on the internet. The electrician should know how this is done. think safety first and take no risk.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 10-06-2011, 12:09 PM
 
Join Date: Sep 2009
Location: Puerto Rico
Posts: 7
cflas is on a distinguished road

Originally Posted by cflas View Post
going from 240 to 480 the windings on the motor need to change from parallel to series. if they are number it is a more simple process but make sure you verify as i have not done this in a very long time. Example you have a delta or wye configuration. more than likely if is 240 is delta wye would be 208. think of a triangle. wires would connect t1 -4-7-10-2-5-8-11-3-6-9-12 -back to 0ne were 1,2 and 3 would be your line voltage. Three phase motors are reverse by changing one line make sure the motor is running in the right directionif not exchange one line with any of the others. Hope this will help and look for delta wiring on the internet. The electrician should know how this is done. think safety first and take no risk.
found this on the internet probably makes more sense:
The connections are:
LV: L1 to 1, 6 & 7; L2 to 2, 4, &8; L3 to 3, 5 &9
HV: Li to 1, L2 to 2, L3 to 3, Join 4 & 7, 5 & 8, 6 & 9
Reply With Quote

  #12  
Old 10-06-2011, 12:16 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

I usually use this US Motors reference.
Just about all combinations here.
Connections
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Single Phase AC Induction Motor Wiring HELP!!! TheButcher69 General Electronics Discussion 17 11-27-2011 05:05 PM
3 Phase Motor Wiring Trouble PhoenixMetal General Electronics Discussion 14 12-12-2008 03:57 PM
help wiring 1 phase motor ezland00 General Electronics Discussion 7 05-15-2006 04:23 PM
Wiring a relay into my 3 phase motor Bass_Player General Electronics Discussion 6 05-24-2005 09:50 AM
4-phase motor and wiring questions DmitryZ General Electronics Discussion 10 04-13-2004 11:14 PM




All times are GMT -5. The time now is 08:40 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361