VFD for 3 phase supply

Hi,

I am wondering if I can use an appropriately size VFD to take 240 VAC single phase input and output pure (?) 240 VAC 3 phase to a 3 phase motor
which would become the RPC. If this would work then I would not have to
mess with starting or running capacitors to balance the legs. I would then hook this up as the power supply, to a Bridgeport EZTRAK-SX. I would want the ability to plug (instantly reverse the spindle motor) the spindle motor switch for tapping.

Thanks,

Ernie
Reply With Quote

  #2  
Old 07-01-2011, 02:34 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

I assume you want to do floating tapping? as rigid tapping requires an encoder on the spindle and a controller to gear the Z axis to it.
You cannot plug a motor the way you would do it with contactors, the VFD must have control at all time.
Depending on the HP and the size of inertia of the spindle, you may find you need brake resistors to dissipate the reverse energy of rapid decel.
Output of a VFD is not 'pure' sine wave as it is composed of a PWM signal.
Also you did not mention if the machine is manual or under CNC control?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 07-01-2011, 07:10 PM
 
Join Date: Sep 2010
Location: usa
Posts: 839
mike_Kilroy is on a distinguished road
Buy me a Beer?

ernie,

yes you can.

as al said u may need db resistor for quick reversal.

pm me if u want quote on hitachi units that will do this.
Reply With Quote

  #4   Ban this user!
Old 07-02-2011, 08:46 AM
 
Join Date: Aug 2005
Location: USA
Age: 78
Posts: 197
ErnieD is on a distinguished road
VFD/RPC

Mike,

PM sent.

Ernie
Reply With Quote

  #5   Ban this user!
Old 07-02-2011, 12:19 PM
 
Join Date: Jan 2005
Location: USA
Posts: 2,348
mactec54 is on a distinguished road
Buy me a Beer?

ErnieD

You can not do what you want to do, Mike is incorrect or miss read what you want to do, The VFD can only power the spindle motor, you need another source of power for the rest of the machine which 120/240V should be all you need, you will have to check the transformer to see what you need to power the rest of the machine, But the right size VFD will take care of your spindle
__________________
Mactec54
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 07-02-2011, 04:17 PM
 
Join Date: Sep 2010
Location: usa
Posts: 839
mike_Kilroy is on a distinguished road
Buy me a Beer?

Originally Posted by mactec54 View Post
ErnieD
You can not do what you want to do, Mike is incorrect or miss read what you want to do, The VFD can only power the spindle motor, you need another source of power for the rest of the machine which 120/240V should be all you need, you will have to check the transformer to see what you need to power the rest of the machine, But the right size VFD will take care of your spindle
Ernie,
I am not sure what is going on. your question on practical machinist was about running the whole machine: I said unequivocally NO you cannot.

ur pm said:
Hi Mike,
Over on the Practical Machinist site you gently chastised me for wanting to use a VFD to provide 3 phase to my Bridgeport EZTRAK-SX machine. Are you now saying that I can use the VFD to start an idler, let the idler make the third leg and then connect to the input on the mill?

NO.

mactec54 is correct; i must have mis understood ur rephrased question here.

I am sorry for miss understanding you Ernie. it is still true you cannot run a WHOLE machine on the vfd - just the motor. If I misunderstood ur request here I apologize. You can run the machine MOTOR ONLY on the vfd, NOT the machine.
Reply With Quote

  #7  
Old 07-02-2011, 06:25 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

If the rest of the machine runs on 1 phase, just use the VFD for the spindle and feed the rest, control, servo's etc with 240 1 phase, if this is what it takes at present..
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 07-02-2011, 08:54 PM
neilw20's Avatar  
Join Date: Jun 2007
Location: Australia
Age: 63
Posts: 2,343
neilw20 is on a distinguished road

Regardless of all of that you CANNOT put contactors or any switching on the output of a VFD (Variable Frequency Drive) and it needs to be used closely following the VFD user manual.
The (3 phase) motor wires go DIRECTLY to the VFD.
If there are any 2 speed/reversing switches in the path to the motor they must NEVER be changed until the power to, and in the VFD has discharged, which maybe even MINUTES.
Generally one VFD, one motor, and you control the low voltage input logic to the VFD to control the motor. Also see the application information in the manual.

Breaking the rules often means the smoke gets out (of the VFD) and can't be put back. It mightn't even smoke, but still might die silently.

Trying to run a single phase motor with a centrifugal switch breaks the rules of NOT switching motor wires, and the single phase motor won't like running below it's design frequency in most cases.
__________________
Super X3. 3600rpm. Three ways to fix things: The right way, the other way, and maybe your way, which is possibly a faster wrong way.

Last edited by neilw20; 07-02-2011 at 08:56 PM. Reason: typo
Reply With Quote

  #9  
Old 07-03-2011, 09:29 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by neilw20 View Post
If there are any 2 speed/reversing switches in the path to the motor they must NEVER be changed until the power to, and in the VFD has discharged, which maybe even MINUTES.
That is not quite true, it is not necessary to wait until the Power Supply has discharged only that the output is at zero freq.
It is done all the time by usually setting one of the outputs as 'At Zero speed' when this bit is detected, the output can be contactor switched, I did this in one instance on a dual motor set up, when swapping motors was desired.
As mentioned in post two, contactor plugging Cannot be done.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 07-03-2011, 09:38 AM
neilw20's Avatar  
Join Date: Jun 2007
Location: Australia
Age: 63
Posts: 2,343
neilw20 is on a distinguished road

Sorry Al, but I can show you some VFD manuals that specify this.
Depends on internal biasing etc whether it is safe.
Just because it works doesn't mean it wont fail.
Not really the disconnection, unless it bounces, but is when the connection is made, and it probably will have some bounce in it too,
which upsets internal biasing and very much depends on the high side drive method used. This can cause transients.
If the high side drive is a true isolated drive, then most likely OK, but if charge pump method is used for high side drive then beware.
If internal inspection makes it obvious each high side drive has an isolated floating supply then that is a good sign.
Always refer to the application details before doing this.
Some OK, others not.

!!!Safety Precautions
★ Live dip setting or measurement for the driver is not permitted.
★ Connection, installation and dip setting must be carried out after three-minute
power-off.
★ Three-minute interval must be carried out between the first and second
power-on and power-off to avoid fault alarming.
★ Input voltage of the driver shall meet the technical requirement.
★ Make sure that power supply cable, motor cable and signal connection cable are
connected correctly and solidly before plugging in.
★ After complete connection of cables and before plugging in, the resistance
measured between terminals A, B, C of the driver and grounding terminal, using
the millimeter’s resistance gear, shall be infinite. Every two-phase resistance
value measured at terminals A, B, C of the driver shall be the same, avoiding
shorted circuit among phases of the motor or any damage caused by insufficient
phase of the motor.

Pasted straight out a manual.
That's one I won't use.
__________________
Super X3. 3600rpm. Three ways to fix things: The right way, the other way, and maybe your way, which is possibly a faster wrong way.

Last edited by neilw20; 07-03-2011 at 11:08 AM. Reason: the red bit
Reply With Quote

Sponsored Links
  #11  
Old 07-03-2011, 11:03 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Well I guess the bottom line is if faced with an application such as this then just select a VFD that will do it.
Of the failed VFD's that I have cannibalized for parts consists of a mains fed 3 phase bridge, which feeds directly to the switching devices.
The only isolation is usually the switching supply for the logic, allowing earth ground reference or common gnd if needed.
Not all VFD's have configurable logic outputs, I prefer the type that do, I use mainly Mitsubishi, WEG and Telemecanique Altivar, all high end VFD's.
I would add, the failed ones I stripped were not from any of my installations..
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
power supply to choose for 5 phase steppers?? patriciooholegu Stepper Motors and Drives 3 11-13-2010 07:40 PM
160V DC 12 Amps from 240V AC single phase supply ftkalcevic General Electronics Discussion 3 04-26-2010 11:07 PM
three phase power supply questions twombo General Electronics Discussion 2 02-27-2009 09:21 AM
current per phase for power supply? FLUTE HEAD General Electronics Discussion 3 07-31-2004 12:41 PM
Egads! 3 Phase power supply? samualt General Electronics Discussion 5 10-02-2003 08:37 PM




All times are GMT -5. The time now is 08:39 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361