Auto or Isolation transformer for Mori Seiki AL2 fed by rotary?

I have a 1990 Mori Seiki AL2 lathe, which I have an american rotary phase converter system to create 3 phase power.

Because the machine expects 600volts, I need to run my 240 3phase created power into a transformer in order to step up the voltage.

The machine has a small internal transformer for the controls to step the voltage back down, and I believe the motors run at the supply voltage, but I'm not entirely sure. There seems to be only one small transformer inside the machine, which appears to be an isolation delta transformer as there are 3 coils there, and not one which would indicate an auto transformer.

So... the main question is do I use an Auto or Isolation 15KVA transformer for the machine. Do I need the "protection" of the auto transformer, or is it not really beneficial since I am running on generated power anyways and the controls already have another transformer internally?

My understanding is that isolation transformers are not quite as efficient as auto transformers, which is of concern to me because I am run at the edge of available amps to run the machine before tripping the breaker.

Auto transformers are 1/3 smaller and more affordable, but isolation transformers protect from voltage spikes, etc.... however since I am on residential power anyways is that even a concern to me?

My thought is that the control is already protected by the internal isolation transformer on the control side, so I should be fine with an auto transformer either way.

Thanks for your help!
Reply With Quote

  #2  
Old 03-29-2011, 02:50 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Personally I would look at seeing if you can bypass the whole of the 600?
Why transform up to 600 when in all probability the machine converts it all back down to
240v 3 phase anyway, unless there are 460 only item.
Most drives are at 240v, the exception could be the spindle drive which if DC may have a 460/240v star secondary with the star used as common for the SCR controller.
But it may be worth the check to see what you can actually run on 240.
In some case you may have to confirm fuse and wire rating.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 03-29-2011, 07:04 PM
 
Join Date: Sep 2010
Location: usa
Posts: 839
mike_Kilroy is on a distinguished road
Buy me a Beer?

Al has great idea to check out. If you do find you need a transformer, I'd like to comment on some of your perceptions of auto vs iso.....

Originally Posted by pld0vr View Post
......There seems to be only one small transformer inside the machine, which appears to be an isolation delta transformer as there are 3 coils there, and not one which would indicate an auto transformer.
a 3ph auto xfmr will look exactly like a 3ph iso xfmr - still 3 coils they just have one tapped winding per phase instead of 2 separate windings per phase.

Do I need the "protection" of the auto transformer, or is it not really beneficial since I am running on generated power anyways and the controls already have another transformer internally?
Not sure what you mean by 'protection?' that is the one thing a buck-boost or auto xfmr does not give you

My understanding is that isolation transformers are not quite as efficient as auto transformers, which is of concern to me because I am run at the edge of available amps to run the machine before tripping the breaker.
Both auto xfmr and iso xfmr should be around 95% efficient. There should be no difference in efficiency between them.

Auto transformers are 1/3 smaller and more affordable, but isolation transformers protect from voltage spikes, etc.... however since I am on residential power anyways is that even a concern to me?
Yes! the iso xfmr does provide a level of protection against spikes transferred thru the magnetic field between pri and secondary while the autoxfmr.s pri and sec being the same winding let it thru easier. Should you not be concerned cuz u r residential? Not sure this has any bearing on it. The same spikes come down the power lines to my house from close by lightning strikes at go to the machine shop in town. These are 7200v lines out our way in the country and I believe they are often 3ph and they just split them down 1ph to the houses or run all 3 to the businesses needing them.

My thought is that the control is already protected by the internal isolation transformer on the control side, so I should be fine with an auto transformer either way.
Fair enough thought.
Reply With Quote

  #4   Ban this user!
Old 04-01-2011, 10:16 PM
 
Join Date: Feb 2008
Location: canada
Posts: 106
pld0vr is on a distinguished road

Okay.. I had another look inside cabinet. The cabinet says "input voltage 550volts 60hz/ 600volts 55hz.

However, on the transformer there are a number of voltage taps. It has suggested connections for input of 220volts to 600volts.

Now, does that mean that I can feed the machine with 220 volts directly? I am going to assume that this is only for the control unit, so would the machine correct load on the spindle and axis motors for a different feed voltage?
Reply With Quote

  #5  
Old 04-01-2011, 10:26 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

If the taps are on the primary then it would point to being capable of 220v 3 phase input.
Check the cable sizing from disconnect to transformer to ensure the higher current capability.
BTW what controller does it have? Fanuc? if so what model?
The 6 etc expects the correct phase rotation at hook up.
Also if it is a DC spindle, there is most likely a transformer for it with a 3 phase star common for the SCR drive.
This should be checked.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 04-01-2011, 11:02 PM
 
Join Date: Feb 2008
Location: canada
Posts: 106
pld0vr is on a distinguished road

Originally Posted by Al_The_Man View Post
If the taps are on the primary then it would point to being capable of 220v 3 phase input.
Check the cable sizing from disconnect to transformer to ensure the higher current capability.
BTW what controller does it have? Fanuc? if so what model?
The 6 etc expects the correct phase rotation at hook up.
Also if it is a DC spindle, there is most likely a transformer for it with a 3 phase star common for the SCR drive.
This should be checked.
Al.
It's a fanuc 10t. There is also a second transformer, but it's quite different looking and has no taps. I'll try and trace the wiring, but with only 3.5kva that can't feed the entire machine. The spindle is 7.5/10 hp.
Reply With Quote

  #7   Ban this user!
Old 04-02-2011, 09:40 AM
 
Join Date: Sep 2010
Location: usa
Posts: 839
mike_Kilroy is on a distinguished road
Buy me a Beer?

pictures are worth a thousand words? why not post a picture of this transformer?

Why not call Mori S. and ask them if you can simply change the taps on that xfmr and make everything then 220? You might get the answer; worse case they will tell you to go take a hike?

"Small transformer inside" with 3 coils is not a control transformer for nc and stuff; 3 coils tend to be the main input power to a machine so you are likely going to be able to retap that puppy and be good to go - but you should be sure...
Reply With Quote

  #8  
Old 04-02-2011, 09:41 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

I have all the prints for a Hitachi-Seiki 1985 lathe with a 10T and interestingly they do not show any main power transformers, just 220v into the breaker for everything, including the spindle .
It is almost as if the end user supplies the matching transformer.
Do you have prints for your model?
Also If you do not have all the parameters saved or hard copy including the 9000 option parameters, I suggest you save them ASAP after you get it going.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #9   Ban this user!
Old 04-02-2011, 01:52 PM
 
Join Date: Feb 2008
Location: canada
Posts: 106
pld0vr is on a distinguished road

Originally Posted by mike_Kilroy View Post
Not sure what you mean by 'protection?' that is the one thing a buck-boost or auto xfmr does not give you
Sorry, that was a typo. I meant protection of the iso transformer.
Reply With Quote

  #10   Ban this user!
Old 04-02-2011, 02:07 PM
 
Join Date: Sep 2010
Location: usa
Posts: 839
mike_Kilroy is on a distinguished road
Buy me a Beer?

i sorta figured that the next day
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 04-02-2011, 02:12 PM
 
Join Date: Feb 2008
Location: canada
Posts: 106
pld0vr is on a distinguished road

Originally Posted by Al_The_Man View Post
Do you have prints for your model?
I wish. When I bought it I was told it came with manuals, but it came with nothing. They also lost the coolant tank and wouldn't replace it. If you know where to get one, let me know.

Originally Posted by Al_The_Man View Post
Also If you do not have all the parameters saved or hard copy including the 9000 option parameters, I suggest you save them ASAP after you get it going.
Al.
I've heard this, and I'll get on it for sure. The main board was replaced in 2003 already.
Reply With Quote

  #12   Ban this user!
Old 04-02-2011, 02:16 PM
 
Join Date: Feb 2008
Location: canada
Posts: 106
pld0vr is on a distinguished road

Originally Posted by mike_Kilroy View Post
pictures are worth a thousand words? why not post a picture of this transformer?
Good point. Here are the photos... best I could do with my big camera.



On the right it says control 110v



Look at those tiny wires. Are you seriously telling me that runs the machine? I can't see that being possible. Besides only 3.5kva? I was recommended a 15kva transformer to run this thing.



Notice the second bus bar on the rear with what looks like small voltage corrections? Not sure.





That black thing labeled T2 is the second transformer.

Thank you for your help. Appreciate the effort either way.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Problem- Did Mori Seiki Buy Hitachi Seiki? Billet Sean Mori lathes 6 05-04-2011 10:12 PM
Mori Seiki GV 503 zf_line Mori Mills 3 12-13-2010 04:12 PM
G203v witih auto transformer for testing outside the case? Wolfesmetalfab Gecko Drives 7 12-16-2008 09:30 AM
Need Help!- DO YOU HAVE TO USE AN ISOLATION TRANSFORMER racer652 HURCO 4 02-29-2008 10:00 AM
PCB Trace Isolation - Minimum Track and Isolation ahoodlum General Electronics Discussion 11 09-25-2006 11:02 PM




All times are GMT -5. The time now is 08:37 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361