    i have a delta 1hp vfd that i am using to run a 3 phase 1HP motor. The motor rotates, the pot and keypad on the vfd works very well. The parameters are also working but the motor is giving poor torque. If i put my hand on the motor pulley it just stops at any rpms. Even at 1400rpms. I also tried going from 0 to high rpms while holding the pulley but the motor is still very weak. I can hear some noise from the motor but it is not getting hot.

    What is wrong with it? the motor has problem or the drive? I am using single phase for power in and three phase out. The motor is running without loads (no belts) with just a small puley.
    please help,
    jasminder singh
    It is better to die for something than to live for nothing.


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,955
    Downloads
    0
    Uploads
    0
    Do you have the correct motor details entered from the motor label?
    Does the drive have auto tuning?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered M250cnc's Avatar
    Join Date
    Sep 2007
    Location
    England
    Posts
    359
    Downloads
    0
    Uploads
    0
    I think the problem is the way the motor if wired.

    There should be some links where the cables connect on the motor.

    They have two ways of being connected either STAR or DELTA

    Maybe Al can even explain it better ?

    Phil

    Sent from my HTC Desire using Tapatalk


  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,955
    Downloads
    0
    Uploads
    0
    That might be a point if the motor details were listed and what the connection possibilities are, some are Star/Delta and other dual voltage motors are two sets of star windings, either series or parallel for each voltage supply.
    Al.
    Last edited by Al_The_Man; 12-21-2010 at 11:33 PM.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #5
    Registered
    Join Date
    Jul 2008
    Location
    india
    Posts
    193
    Downloads
    0
    Uploads
    0

    vfd

    friends,
    thanks for the support. The motor is wired in delta ( i confirmed it by using a multimeter and checking the continuty of the wires).
    the drive does not has auto tuning.
    I am surprised that the motor runs with full torque if i run directly on a 3phase power supply and the drive is also giving all the 3 phases ( i checked using a filament bulb that runs on ~60Hz).
    I have called the seller of the drive and he says that he will send an expert in few days.

    let's see. what's wrong with it
    jasminder singh
    It is better to die for something than to live for nothing.


  • #6
    Registered
    Join Date
    Jul 2008
    Location
    india
    Posts
    193
    Downloads
    0
    Uploads
    0

    got the VFD working. Now how to get stable rpms with mach3 turn

    friends,
    The seller has replaced the VFD with a 3phase in/out VFD and i am able to run lathe with it now.
    Now i need some assistance about controlling the speed of the spindle. I have a proximity sensor hooked up to the spindle that works fine (giving active low output). the speed of the spindle is stable within ~4rpms when no load is applied. But when i put my hand on the chuck to put some load (i know it is dangerous a bit) it wents down to ~50 rpms and takes 3 or 4 seconds to recover. I have set the acelleration delays in the VFD to its minimum settings (o.1 second).
    Can anybody tell me how to configure pulleys and that PID to get demanded rpms using the "S" word.
    Also let me know how many rpms less or more are okay while threading.
    i have already tried the mach3 turn manual for help but no luck.

    with thanks,
    jasminder singh
    It is better to die for something than to live for nothing.


  • #7
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,955
    Downloads
    0
    Uploads
    0
    Without a feedback from motor to VFD there can be no PID loop.
    What modes are available in the VFD? if only speed and torque mode is avail, try it in torque mode.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #8
    Registered
    Join Date
    Jul 2008
    Location
    india
    Posts
    193
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by Al_The_Man View Post
    Without a feedback from motor to VFD there can be no PID loop.
    What modes are available in the VFD? if only speed and torque mode is avail, try it in torque mode.
    Al.
    sir,
    here is the link to the manual of the VFD. Hope you can help setting up the right parameters.
    http://www.delta.com.tw/product/em/d...N_20100514.pdf
    I will try using the spindle calibration wizard again hoping for better results this time.

    with thanks,
    jasminder singh
    It is better to die for something than to live for nothing.


  • #9
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,955
    Downloads
    0
    Uploads
    0
    It looks like a very comprehensive unit, apparently it does have a loose form of PID loop, they appear to detect the resultant rpm internally?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #10
    Registered neilw20's Avatar
    Join Date
    Jun 2007
    Location
    Australia
    Posts
    3,424
    Downloads
    0
    Uploads
    0
    Look at Pr.57 and see if the motor current is set high enough.
    Set the display to to show current.
    How much is it drawing?
    Display is A x.x where x.x is the current being drawn.
    What is the rated motor voltage on the name plate?
    What model VFD are you using?
    What is your mains supply voltage?
    The manual is quite comprehensive.
    Have you read it?
    There are many parameters to set up to make it work correctly.
    You need to follow the the manual, and it should work, providing the motor matches what the VFD is set for.
    The default VFD settings may not match your motor requirements.
    Some configuration is usually required, and from the number of parameters you can set, you will realize it is not trivial.

    Good luck.
    Super X3. 3600rpm. Sheridan 6"x24" Lathe + more. Three ways to fix things: The right way, the other way, and maybe your way, which is possibly a faster wrong way.


  • #11
    Registered
    Join Date
    Jul 2008
    Location
    india
    Posts
    193
    Downloads
    0
    Uploads
    0

    pid loop issue

    Quote Originally Posted by Al_The_Man View Post
    It looks like a very comprehensive unit, apparently it does have a loose form of PID loop, they appear to detect the resultant rpm internally?
    Al.
    sir,
    I have absolutely no knowledge about VFD (i saw one first time in my hands).
    I know how they work but i have no idea about how fast they response to the given input of 0 to 10V.
    I have nothing to do with the PID also. i just want to thread on my lathe. Currently i can control the RPMs within +-10 to the demanded rpms but i want to know if this is good for thread cutting. The rpms keeps increasing and decreasing than the demanded number of rpms and it never holds the rpms even at no load (for example if i enter 1234 in the rpm tab of mach, my spindle runs arround 1225 to 1245)

    that's the problem. i have ordered a cnc4pc vfd card today that will be on its way. lets see if it works. Till now i was using my home made ir sensor to convert PWM to volts for the VFD input.

    my guess is that the sensor i made is working properly because the freq on the display of the VFD was very stable but i don't know why the rpms were changing (i can fell that from the motor and spindle noise and the rpm tab of mach shows the same).

    Gotta wait for a month till the card reaches me after custom clearances ( i hate that word now)
    with thanks,
    jasminder singh
    It is better to die for something than to live for nothing.


  • #12
    Registered
    Join Date
    Jul 2008
    Location
    india
    Posts
    193
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by neilw20 View Post
    Look at Pr.57 and see if the motor current is set high enough.
    Set the display to to show current.
    How much is it drawing?
    Display is A x.x where x.x is the current being drawn.
    What is the rated motor voltage on the name plate?
    What model VFD are you using?
    What is your mains supply voltage?
    The manual is quite comprehensive.
    Have you read it?
    There are many parameters to set up to make it work correctly.
    You need to follow the the manual, and it should work, providing the motor matches what the VFD is set for.
    The default VFD settings may not match your motor requirements.
    Some configuration is usually required, and from the number of parameters you can set, you will realize it is not trivial.

    Good luck.
    sir,
    i was also thinking if the VFD were easy to use things ( i mean so many parameters)
    The problem was in my motor. the motor was replaced and drive was changed to a 3phase with 2HP rating (motor is still 1 HP , i wanted to be on safe side this time and may upgrade the motor to 2hp later).
    getting a stable rpm with mach3 turn for threading is an issue now.
    thanks for help.
    jasminder singh
    It is better to die for something than to live for nothing.


  • Page 1 of 2 12 LastLast

    Similar Threads

    1. BF20 (G0705) Power Draw Bar Build (Poor, poor mans drawbar)
      By zerodegreec in forum Benchtop Machines
      Replies: 6
      Last Post: 09-14-2010, 04:01 AM
    2. slo-syn motor - no torque.
      By sliptonic in forum Stepper Motors and Drives
      Replies: 1
      Last Post: 06-20-2010, 01:40 PM
    3. delta dynapath 20 is giving me fits
      By js412000 in forum General CNC (Mill and Lathe) Control Software (NC)
      Replies: 3
      Last Post: 01-03-2008, 06:32 PM
    4. Motor Torque?
      By bearwen in forum Stepper Motors and Drives
      Replies: 3
      Last Post: 02-26-2006, 07:47 AM
    5. oz-in torque on dc motor
      By thejoe in forum General Electronics Discussion
      Replies: 13
      Last Post: 09-08-2005, 01:14 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.