  #1   Ban this user!
Old 11-20-2010, 11:20 AM
 
Join Date: Jul 2006
Location: USA
Posts: 72
Dubliner is on a distinguished road
Connecting the on off switch...

Ive assembled a rotary phase convertor, and regenerative pump, its all wired and I'm getting 240 out of each leg so no problems there. What I'm having trouble with tis the on/off switch on top on the contactor case. It was not there when I got the units so I have no idea what goes to what. I have a red/blue & white coming from the low voltage side of the contactor. Not sure if its clear in the pics, but red goes to 21nc and 13no, Blue goes to 14no and 22nc, white (110 neutral) goes to 95-96 nc and is jumpered to back lug on 14no=21nc. Hot leg of 110 goes to switch I imagine but no idea which lug. I have the switch to install and this is all I'm lacking from firing up this nice vac for a cnc router, can you help? tx Dubliner in Texas
Attached Thumbnails
Click image for larger version

Name:	DSC02903.JPG‎
Views:	39
Size:	147.4 KB
ID:	119550   Click image for larger version

Name:	DSC02905.JPG‎
Views:	40
Size:	145.7 KB
ID:	119551   Click image for larger version

Name:	DSC02904.JPG‎
Views:	38
Size:	148.8 KB
ID:	119553   Click image for larger version

Name:	DSC02907.JPG‎
Views:	40
Size:	148.8 KB
ID:	119554  

Click image for larger version

Name:	DSC02906.JPG‎
Views:	40
Size:	140.3 KB
ID:	119555   Click image for larger version

Name:	DSC02908.JPG‎
Views:	38
Size:	137.4 KB
ID:	119556  
Reply With Quote

  #2  
Old 11-20-2010, 12:09 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

What prints or drawing were/are you working from? Presumably you bought parts for self assembly?
That is obviously the main contactor, the two white wires on #5 is the overload contacts.
The push button usually engages a start capacitor, as soon as it is up to run, then the P.B. is released, but there are other methods, some use a timer.
Here is a drawing that may help somewhat in the MetalWorking drop box.
metalworking.com - /dropbox/_1998_retired_files/
Look for Fitch Williams files FRW- etc.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 11-20-2010, 01:02 PM
 
Join Date: Jul 2006
Location: USA
Posts: 72
Dubliner is on a distinguished road

Well I'm not working from any drawings actually. The pump came with the contactor already wired to it, and the Phase convertor did have a drawing with it, so I just copied what was already there. I have 1ph in, 3ph out, and as I said I just need to wire the switch. This contactor does have a timer on it so I presume thats the method here. I looked in the pics from FRW I'm afraid either I dont understand it or its not specific to my situation. If anyone needs better pics of a specific point I'll be delighted to post whatever might help. TIA Dubliner
Reply With Quote

  #4  
Old 11-20-2010, 01:10 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

Are you trying to get the RPC wired or the pump?
I had assumed it was the RPC, If a 3 phase motor is what you are trying to control then there are plenty of simple stop start circuits to Google
e.g. Motor Starter Wiring Diagrams - OWWM Knowledge Base (Wiki)
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 11-20-2010, 02:17 PM
 
Join Date: Jul 2006
Location: USA
Posts: 72
Dubliner is on a distinguished road

The vacuum. There is a cap bank starter for the RPC. RPC & Vac are wired, now just need to momentary on switch to kick the vac on after RPC is running.
Attached Thumbnails
Click image for larger version

Name:	DSC02911.JPG‎
Views:	31
Size:	145.7 KB
ID:	119560   Click image for larger version

Name:	DSC02913.JPG‎
Views:	32
Size:	151.7 KB
ID:	119561   Click image for larger version

Name:	DSC02912.JPG‎
Views:	31
Size:	151.6 KB
ID:	119562   Click image for larger version

Name:	DSC02914.JPG‎
Views:	28
Size:	147.7 KB
ID:	119563  

Reply With Quote

Sponsored Links
  #6  
Old 11-20-2010, 02:22 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

It looks like you have a stop/start button there, Telemecanique by the look of it.
Also looks like you have the N.O. N.C. contact pair?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 11-20-2010, 02:30 PM
 
Join Date: Jul 2006
Location: USA
Posts: 72
Dubliner is on a distinguished road

Yes pic 2 is all Telemecanique, pic 3 is the starter for the RPC. I looked at the switch that came wired(pic 3) and it has three wires in, and one jumper between two lugs so I presume I should mimic this. I'll put a meter on the switch and see what I have. Sorry I couldnt really understand the wiring diagram in the link. I've tried to get 2 electricians over here, but no joy and I really think this is the simplest part but the NO/NC thing is baffling me. Sorry to be a pest.
Reply With Quote

  #8  
Old 11-20-2010, 03:12 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

I will see if I can describe it, the P.B.s are wired from the supply with voltage suitable for the coil voltage is, yours could be 120v or 240vac?
If you wire the two P.B.'s in series feed the supply into one PB and out the second into the overload on the contactor, out the other N.C. terminal on the overload and then to the coil, the other side of the coil is of course the neutral or other 240v feed.
The last thing left is to wire the N.O. auxiliary contact on the contactor to the N.O. P.B. so that it is in parallel with the N.O. P.B.
In other words all are in series which each other except the N.O. contacts, which are in parallel with the N.O. on button.
A way to save on the number of wires is to start with the feed, to the NC PB jumper out to the NO PB out of the NO PB to the O/L out of the O/L to the coil.
From the wire that comes from the NO PB to the O/L.
OK I have made a DXF for clarity.
Al.
Attached Files
File Type: dxf sTOPsTART.dxf‎ (18.0 KB, 28 views)
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #9   Ban this user!
Old 11-20-2010, 04:16 PM
 
Join Date: Jul 2006
Location: USA
Posts: 72
Dubliner is on a distinguished road

They dont call you Al the Man for nothing do they :-), thanks a million Al, that makes it easier to understand.
Reply With Quote

  #10   Ban this user!
Old 11-22-2010, 03:33 PM
 
Join Date: Jul 2006
Location: USA
Posts: 72
Dubliner is on a distinguished road

Al, its me the pest again. I hooked it up and when I held the green button in, ***hurray, vacuum***, when I let it go it stopped. So I figured I had the wiring backwards/mixed up, but no other configuratation would close the contactor. I'm wondering if it might be bad & not hold, or do you think I have to have some of the wiring mixed up. I followed your diagram as closely as I could, but all I have for reference on the block in nc/no or position numbers. Would it be possible to id what you mean on the contactor if I got a better picture & wrote in what the position, and closure(nc/no) type was? tx Neville
Reply With Quote

Sponsored Links
  #11  
Old 11-22-2010, 04:11 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,544
Al_The_Man is on a distinguished road
Buy me a Beer?

It sounds like you do not have the (N.O.) normally open auxilliary contact on the contactor connected across the start button?
This is what holds it in when you release the start PB.
Looks like 13 & 14 on the contactor?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #12   Ban this user!
Old 11-23-2010, 09:44 AM
 
Join Date: Jul 2006
Location: USA
Posts: 72
Dubliner is on a distinguished road

Al, hopefully you can see more clearly in these pics. Where the wires are connected to the switch & back to the contactor positions. The black wire is a 110v and neutral is connected to 95/96 NC on contactor beside timer/reset dials.
Attached Thumbnails
Click image for larger version

Name:	DSC02925.JPG‎
Views:	38
Size:	139.5 KB
ID:	119877   Click image for larger version

Name:	DSC02927.JPG‎
Views:	32
Size:	133.4 KB
ID:	119878   Click image for larger version

Name:	DSC02926.JPG‎
Views:	30
Size:	152.3 KB
ID:	119879  
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Replacement for master switch/reversing switch on HF 8x12? novahobbies Benchtop Machines 5 06-29-2010 08:05 AM
Limit switch replacement with proximity switch? Normsthename Bending, Forging,Extrusion... 3 07-11-2009 10:38 AM
limit switch and home switch setup Runner4404spd General Electronics Discussion 0 12-15-2005 07:58 AM
Limit Switch / Home Switch in Software Sanghera General Electronics Discussion 6 11-01-2004 05:58 PM




All times are GMT -5. The time now is 08:36 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361