Sounds like you may have a noise spike on the line going to the VI terminal. A meter will sometimes read a value with only one probe attached if there is high frequency on the one probe.
How do you have the G540 connected to the VFD? Make sure your analog wires do not run near the motor leads, and use twisted pair sheilded wire for the analog wires if possible.