    1 leg of a motor pulls 10% less current than the other two legs? U20A, V20A, W16AI measured the winding resistance with a milliohmeter and did not find any appreciable dif. The Voltage on each leg is within .5 volts. If the Voltage is even and the amperage is different the prob should be with the motor? By ohms law current draw=Volt/Res. True resistance of an AC motor is reactance? How do I measure this?? Please jump in on this think tank! Thanks for any help. "Al the Man" had mentioned the wave form and I am going to scope it Friday.
    This is a new thread because I am curious on how other techs perform motor checks

    Similar Threads:


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24221
    Downloads
    0
    Uploads
    0

    Default

    Is this the motor that is on a VFD? As I believe it may be that particular phase output that may be the problem, if so swap two of the phases temporarily to see if the lower current stays on the same phase.
    Or if on a VFD supply, hook it up to 3 phase direct, if possible, and recheck
    If it is on a fixed 3 phase supply, then the ammeter should be a simple indication of the health of the motor.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered
    Join Date
    Oct 2007
    Location
    usa
    Posts
    56
    Downloads
    0
    Uploads
    0

    Default

    What is your opinion on the I inrush if i connect The 75HP directly to the Line? Any precautions? The machine is a Screw compressor. I don't want the motor to go backwards but I could swap U & V then V & W And I would still Be going the right direction ?



  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24221
    Downloads
    0
    Uploads
    0

    Default

    It may be a problem without reduced voltage start, what about swapping the vfd motor phases and see if it stay on the same phase?
    If the opposite direction is a problem, you would have to change all three phases instead of the usual two.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  5. #5
    Registered
    Join Date
    Oct 2007
    Location
    usa
    Posts
    56
    Downloads
    0
    Uploads
    0

    Default

    Gotcha, This will isolate either the drive or the motor. Also I am going to use your suggestion of scoping the phases. I have to re-program the unit to run at a constant Hz. Thanks for your help Al and I will post my results 3/14/8.
    These VFD's are intriging! They can amplify EMI and create ringing and I have found that with out proper shielding they can effect(false trigger) old TTL CPU,PLC systems, What are your thoughts on this comment? EX: I was working on a Heald 2EF Grinder with the Acramatic 700G and when I upped the carrier frequency on 150HP VFD the The Acramatic would malfunction with a multitude of errors. I disconnected the motor shield and the problems were amplified. I did not have time or the equipment to experiment further but it was interesting. We moved the machine away from the VFD and no more wierd shut-downs



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Testing an AC 3ph motor

Testing an AC 3ph motor