Will a VFD output single phase?

Page 1 of 2 12 LastLast
Results 1 to 20 of 25

Thread: Will a VFD output single phase?

  1. #1
    Member vladdy's Avatar
    Join Date
    Feb 2004
    Location
    Perogie Flats, Canada
    Posts
    361
    Downloads
    1
    Uploads
    0

    Default Will a VFD output single phase?

    Dumb question to some maybe, but I never did much with VFD's..
    anyways, VFD in question is a Delta B series 3-5 hp rated, I know I can input single phase , but never tried output as single phase...
    Motor that I would like to run on output end is a Baldor 3 hp single phase on an old Gisholt converted turret lathe..
    be nice to have a choice of more than six speeds...
    tia..

    Similar Threads:


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24221
    Downloads
    0
    Uploads
    0

    Default

    The ability to control a single phase motor with a VFD is prone to stall at the lower speeds, the only type that I know of has been Capacitor-run motors, Motor that are capacitor start only, suffer from the problem above.
    IOW I would put a three phase motor on if you really want Variable speed drive.
    In any case, you may have to search a bit to find a VFD that even attempts to run a 1ph motor.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Member vladdy's Avatar
    Join Date
    Feb 2004
    Location
    Perogie Flats, Canada
    Posts
    361
    Downloads
    1
    Uploads
    0

    Default

    when you say 'stall' is that below an approximate speed percentage, power draw , or??
    I was basically looking to get [hopefully] +15 / -35 % on rated speed..

    ..



  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24221
    Downloads
    0
    Uploads
    0

    Default

    I have never used one but have read reports of dismal performance, apparently if base speed is reduced only marginally and a load is placed on the motor it can fall out of run.
    I would think that the absence of any but one or two products that can be found for this type of motor speaks to the popularity and success.
    Also, the majority of 1 ph motors used in MT spindles etc, use capacitor start motors, If you were to use one of these motors, with the reduction of RPM, the start windings would come into operation again, and I believe these are not continuous rated.
    Al.

    Last edited by Al_The_Man; 04-23-2007 at 01:07 AM.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  5. #5
    Member vladdy's Avatar
    Join Date
    Feb 2004
    Location
    Perogie Flats, Canada
    Posts
    361
    Downloads
    1
    Uploads
    0

    Default

    ok..I know the motor on there has start windings, so I 'assume' capacitor start, definitely would not want it to drop down to the point where those start winding cut in again, from previous experience I know that shortens the life span quite drastically [ they warm up quite noticably in less than 30 seconds]...
    I was hoping that around a 35% reduction in speed would still keep the starter plate flipped out...maybe, don't really know for sure when they cut back in normally,
    so at this point, as far as I can tell, is to look around for a three phase motor of equivalent capacity, failing that, the VFD will go up for grabs on ebay I imagine..
    I have no three phase machinery [except for air conditioner at another building], so not sure how much time I want to spend, but it would be nice to have more variable speed ranges on this old lathe..most of the time it runs around 500-700 rpm with fairly aggressive cuts.. basically 'rough' work..trimming down flywheels or cutting the weld out of driveshafts and such..
    the Delta VFD was fairly cheap as the plant was updating some of the conveyors, and I rescued it from the scrap bin...it's value ws directly comparable to it's weight...

    thanks



  6. #6
    Registered
    Join Date
    Feb 2007
    Location
    USA
    Posts
    424
    Downloads
    0
    Uploads
    0

    Default

    AL is correct if you were to drop a cap start, or cap start-run( two caps) motor down to start winding(around 60% of nameplate rpm) you would both fry the motor but more then likley the drive also. The currrent draw would go through the roof, torque would be unstable and things would get hot fi they don't explode first. Similiar would happen with any motor that has a start winding cutout switch, be mechincal(most) or electrical. I have run permanant split capcitor motors with mitsbushi drives(with the hopes of using it on a taig), the preformance was less the stellar, not even worth the while to do. There are some purpose built single phase drives poping up now but again they are being used on fans primarily, and thats were PSC's work the best. Best to go with either DC or 3 phase AC, the psc route is pretty much a waste.

    chris



  7. #7
    Member handlewanker's Avatar
    Join Date
    Sep 2006
    Location
    Australia
    Posts
    6463
    Downloads
    0
    Uploads
    0

    Default

    Hi all, one thing must be realised and that is the reason that single phase motors were/are so popular is because they can be driven directly from the mains.
    The only problem is they don't like to slow down , for the reasaons already stated.
    Now there are TONS of 3ph motors out there that no-one looks at because to have 3ph in the home is going big time.
    These 3ph motors usually go for A$50 for a 1hp job and up to A$150 for 3 hp.
    You can drive these motors from the 240volt mains, probabvly 110volt as well, I don't know, we don't have 110V in OZ, if you have a VFD that converts 1ph to 3ph.
    I recently bought a 1 HP VFD brand new, on Ebay, for A$250, to drive my bandsaw, which means that the motor can be controlled from 15% to 200% of it's rated speed without having to change belts on pulleys.
    You just have to make sure not to load it too much at the lower speeds or it will overheat due to loss of fan speed.
    To overcome this I belted the motor down to give a primary reduction of 1:8 and this lets the motor still run fast enough while the final output speed is as low as required.
    The beauty of a VFD is that you can get ramp up and down and dynamic braking and also jogging.
    The other way is to make a rotary phase converter, using a 3ph idler motor rated above the HP of the motor you're going to drive.
    You don't get speed control, but you do get a lot of cheap motors available.
    I'm going to use the latter method for my Bridgeport mill, as it's cheap and the mill's got adequate speed control already.
    There's a big market for oil filled run capacitors, in the 400volt 10 - 20 Uf range, that are used for this purpose,and to buy them new probably cost more than the motor, so when you come across any at junk sales or scrap yards, you grab them.
    Start capacitors are only used for a second or two to get the motor up to speed, and are in the range of 400volt 100-150 UF and are much cheaper and easier to get hold of.
    Ian.



  8. #8
    Registered
    Join Date
    Feb 2007
    Location
    USA
    Posts
    424
    Downloads
    0
    Uploads
    0

    Default

    Theres a secondary market for the oil filled caps?
    Seems to me that my disposal department seems to think that they are next to nuclear waste here, can't ship, can't get ride of them, again thats in a blown condition also.
    Then again I use, large ones, in 15-20 mic range across the primary of a ballast transformer.
    chris



  9. #9
    Member vladdy's Avatar
    Join Date
    Feb 2004
    Location
    Perogie Flats, Canada
    Posts
    361
    Downloads
    1
    Uploads
    0

    Default

    I did a bit of checking today to see what was available for 3ph motors [again from the fellows doing the updates at the milling plant here, and there's nothing left under 5hp, so the VFD update on the lathe will have to wait a bit..
    There apparantly were a few in the 2 to 3 hp range, but as there is no industrial recycling depot in this area, they went to get melted down as scrap..oh well..the scrap yard already had them trucked out to Winnipeg with the loads last week,
    but I did manage to scrounge some load cell display units, a gallon pail of AB switches, a half dozen older slo-syn [appx 34 size] steppers, for less than $10 so it's definitely not a total loss...
    I'll put the VFD on the shelf 'just in case'..I may never use it, but someone else might make use of it later on.
    The old gisholt will stay a six speed for a while, but I'm used to it, so it's not like I'm 'missing' anything at this point..

    thanks



  10. #10
    Registered alipavsky's Avatar
    Join Date
    Jan 2005
    Location
    United States
    Posts
    55
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by vladdy View Post
    I'll put the VFD on the shelf 'just in case'..I may never use it, but someone else might make use of it later on.
    Are you saying you might be willing to part with your VFD? I need a single-phase VFD for a small (3A) motor.



  11. #11
    Registered
    Join Date
    Feb 2007
    Location
    USA
    Posts
    424
    Downloads
    0
    Uploads
    0

    Default

    I hope you know a majority of single phase motors cannot be run on a VFD, only ones without a switch(either mechincal or solid state), which about 99.9% of those are permanet split capcitor, which are pretty bad doing anything esp if it only draws 3 amps. They also at that power level tend run hot as it is, and some PSC motors don't run on VFD's anyway(my mitsubushi VFD manual states that they may not run at all) as they eliminate the capcitor.
    chris



  12. #12
    Member handlewanker's Avatar
    Join Date
    Sep 2006
    Location
    Australia
    Posts
    6463
    Downloads
    0
    Uploads
    0

    Default

    Hi all, one of the problems with single phase motors is the HP to physical size factor.
    The duty cycle of the motor will give you the run time for it.
    For instance, if you check on the electric specs plate on the motor and it states continuous run, you can be safe in thinking that it can be used at it's stated HP capacity to run a machine all day long, but if the plate states int. or intermittent run, then you have a whole different ball game.
    Here we have a motor, that rated at 3/4 Hp, will for a short time, usually 1/4 hour or less, act like a 3/4 HP motor, but soon gets too hot to use.
    You can pump in the amps to get the wattage out of a small motor package but in the end the current drawn has got to go somewhere and that is in the form of heat.
    I use to see 1/3 HP motors from washing machines driving small lathes on the home workshop circuit.
    They work fine up to a point, as most of the work is cut and try, with the lathe being switched off for longer than it runs as the operator battles with the mysteries of turning etc.
    Which brings me to another point, not mentioned before by anyone, and that is the number of start cycles per hour for single phase motors, usually about 4 or 5, after that the start windings just add to the miseries as the whole motor gets hotter and hotter.
    You just can't get the heat away quick enough, and as it follows an exponential curve, with every switch on cycle, you get that familiar smell of hot insulation.
    I was told once that the "modern" single phase motors have insulation that is designed to run hot to improve the insulation properties, crap!
    Incidently if you do come across a 1 ph motor that won't start but only gives a loud humming sound, then 10 to 1 it's the start windings or centrifugal switch that has gone west.
    It's also vital to test for a short to the frame of the motor.
    NEVER touch a motor frame when it's running, unless you want a nasty surprise with a shorted out winding.
    Also NEVER run a motor without an earth connection.
    Last but not least, before running a motor test it with a meter to see if you have a high resistance between the live input wire and the frame.
    If the resistance is low then ten to one you will blow something at start up.
    If you do get a start problem, it doesn't mean the motor is dead.
    If you isolate the start windings by disconnecting them from the switch plate, then the motor can be used by wrapping a cord round the shaft and giving it a pull.
    The old familiar phrase "Don't try this at home" would probably fit in here.
    As soon as the cord is free the motor is switched on and if you get enough revs with the " cord starter" it will run, and quite happily too, in any direction, as it is the start windings that determines the direction the motor will run in.
    Some 1 ph motors can't be reversed, due to inaccesibility of the wiring connections etc, but for the majority it's only necessary to swap over the start winding connections to effect reversal.
    I once bought a practically new 3/4 hp motor with the centrifugal switch burnt to a crisp.
    It was a 2,800 rpm job from a circular saw, and I paid about 1 pound back in 1975 from a scrap yard in UK.
    I cleaned out the innards of the motor and reinsulated the wiring connections.
    The centrifugal switch was on a Tufnol board that had burnt out and was totally unrepairable, so I just brought the two start winding wires out and connected them to a momentary contact switch that was used to get the motor going. One quick press for a split second and the motor was up and going.
    Later I rewired the input connections and added a relay with a time delay, to effect the start up requirements.
    By adding a relay to the start circuit in place of the start switch meant that if the motor was overloaded it could even stall, and as there was no centrifugal switch present to switch the start windings back in with speed drop, no catastrophic burn down can happen.
    This also works to reclaim a motor if the start windings are actually burned out.
    I use a 1 HP motor on my Colchester Bantam lathe, but to avoid switching the thing on and off all the time, I added an electric clutch from a car's airconditioner.
    Now the motor runs continuously, with the electric clutch being switched on and off for as many times as you want, and never gets hot.
    The bonus is that the clutch gives a softer start, as opposed to the jerk when a motor is switched on, even without a load.
    The clutch is designed to be switched on and off continuously, and only consumes 2 amps at 12 volts DC, so a battery charger of 4 amps output will power it quite well.
    It is activated with an ordinary car type toggle switch, mounted in a conveniant position on the headstock, rated at 12 volt 4 amps, and fused accordingly.
    I'm adding an electric brake as well, so that when the clutch is deactivated the brake will come on for a second or two to stop the lathe quicker, very necessary when your'e using a turret lathe on short run cycles, and beats having a foot type mechanical switch.
    I think I'd be right in saying that all of the Chinese and other foreign import lathes have motors that are connected directly to the drive train and so get switched on and off all the time as required.
    They're designed to do this, but I dislike the thump in the drive train when the motor starts up.
    An electric clutch and brake here would not add too much to the cost, but would extend the usefullness a hundredfold.
    Ian.



  13. #13
    Member handlewanker's Avatar
    Join Date
    Sep 2006
    Location
    Australia
    Posts
    6463
    Downloads
    0
    Uploads
    0

    Default

    By the way, a single phase motor is tied to the incoming mains frequency of 50, or over the pond, 60 cycles per second.
    As soon as you load the motor to the point when the synchronisation causes it to go out of synch, you get a condition that is like hiccups but electrically orientated.
    When you use a VFD on ANY motor, single or three phase you are injecting a frequency that is synthetic, almost sine wave, but good enough to power the motor in the manner that it is designed to work at, and that is in pulses at a certain frequency, any frequency, the frequency rate and the number of poles will determine the RPM of the motor.
    The subject of motor drive is vast and too technical for me to delve into except at the level I have learned over the years.
    One thing is for sure you cannot use a 1 ph motor with speed control if you have start winding present, also if you have capacitors to effect phase shift for running.
    It would be interesting to know, if it is possible, what a VFD will do for a 1 ph motor, providing the start winding was disconnected.
    3 ph motors have an inbuilt phase shift in the power supply, by nature of the 3 input waveforms, but 1 ph on the run cycle won't run below a certain speed.
    With this in mind, I would try using a motor rated at 2,800 rpm, and pushing the speed UP not DOWN to effect speed control.
    The armature of a 1 ph motor is solid metal, a composite of metal stampings that rotate in the stator core, and provided the balance is good, shouldn't disintergrate at the raised rev range.
    Motors with wound armatures and consisting of copper wire in insulated slots run at 10,000 rpm, as in angle grinder motors, do not have a problem in this respect.
    This way you would get a rev range above the motor speed and to a certain extent below it, but to all intents and purposes a rev range.
    This would suit a machine with a belt drive as the pulley sizes can be changed to allow for the new high RPM range, but if the motor is built in with no access to the gear train or drive mechanism, then the drive train will have to be worked out.
    Whether or not it can be got from a VFD, designed to output 3 phases, but only using one output I couldn't say.
    That's why I prefer 3 ph for speed control, so much simpler and cheaper.
    Ian.



  14. #14
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24221
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by handlewanker View Post
    By the way, a single phase motor is tied to the incoming mains frequency of 50, or over the pond, 60 cycles per second.
    As soon as you load the motor to the point when the synchronisation causes it to go out of synch, you get a condition that is like hiccups but electrically orientated.
    .
    Actually a standard 1ph or 3 phase squirrel cage induction motor can never run at synchronism, if the rotor catches up to the rotating field, there is nothing induced into the rotor & hence no rotor field.
    They will always run somewhat lower frequency due to this 'slip' otherwise they would run at exactly 3600rpm (2 pole 60hz) or 1800rpm (4 pole 60hz).
    There is a way to create synchronism, a circuit detects when the slip frequency is approaching and injects a DC field into the rotor, hence locking the rotor to the rotating field, but not in your average motor.
    A 1 ph motor will never start without a phase-shifted start winding, due to no rotating field at switch on.
    Also a Standard motor rotors appear to be a solid chunk of metal, but actually has windings, these are conductive bars embeded in the rotor and connected with shorted turns at the end of the rotor, they used to comprise of copper many years ago, but now are generally aluminum composition.
    Hence 'Squirrel Cage' motor
    This is also why the high current is caused by a stalled motor, there is full current reflected back from the shorted turns on the rotor to the stator.
    Al.

    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  15. #15
    Registered
    Join Date
    Feb 2007
    Location
    USA
    Posts
    424
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by handlewanker View Post
    It would be interesting to know, if it is possible, what a VFD will do for a 1 ph motor, providing the start winding was disconnected.
    With this in mind, I would try using a motor rated at 2,800 rpm, and pushing the speed UP not DOWN to effect speed control.

    The armature of a 1 ph motor is solid metal, a composite of metal stampings that rotate in the stator core, and provided the balance is good, shouldn't disintergrate at the raised rev range.

    This way you would get a rev range above the motor speed and to a certain extent below it, but to all intents and purposes a rev range.

    Whether or not it can be got from a VFD, designed to output 3 phases, but only using one output I couldn't say.
    That's why I prefer 3 ph for speed control, so much simpler and cheaper.
    Ian.
    Ian,
    If you connect a single phase motor to a VFD and disconnected the start winding it would just sit there and hum, like I said most motors won't work, in the case of PSC motors the the windings are typicaly the same size of wire and number of windings, so if the flux is strong enough a VFD outputing on single phase may make a PSC motor spin, it also depends upon how much phase shift the motor was designed to run with(the cap strength if you will). This is one of the reasons that a PSC motor can quick reverse if the manufactor allowed for it on the wiring end, some cannot however I have seen caps blow when this is tryed(these seemed to be bigger caps) .

    If you speed up any induction motor, be it 3 phase , 2 phase(4 wire) or single phase it will not work as well above its rated speed, the torque flat lines, and eventually you will stall, its been my exeperince that around %150 or greater output for your average run of the mill 3 phase motor. The best place for most polyphase motors to run is at there nameplate speed.
    In motor lingo when you say armature you are referering to a motor who has brushes or slip rings. If you refer to a induction motor then they have a rotor, no conections to the outside power. Asyncrounous motors have a shorted rotor core, they are made of laminations held together with alum. cores, only seen one come apart and that was a prototype, they act as one sold piece of metal but if it were the eddy currents would fry the stator in matter of minutes. Stators also have lams, and again the idea is to fool the eddy currrets from frying the motor just like a transformer.
    Syncrounous motors have an armature, which can be shorted or run through ressitance grids to provide varying levels of slip, or connected to another motors stator core to provide a cascade connection.
    Some VFDs are now able to produce a single phase signal with causeing an error, there are also specialty single phase drives, they all can only run motors with no start winding or more correctly motors with the same size windings, or PSC motors. Agreed that 3phase motors are best run for a vfd, you are other wasting 73% of your capacity for work.

    chris



  16. #16
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    24221
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by in2steam View Post
    Syncrounous motors have an armature, which can be shorted or run through ressitance grids to provide varying levels of slip, or connected to another motors stator core to provide a cascade connection.
    I think you are referring to Wound rotor motor for non-synchronous speed control, as is often used in Crane applications etc.
    A synchronous motor does not, or should not run with any slip, as the idea is to run in perfect synchronism with the supply frequency.
    The AC induction motor with DC injection to the rotor type were a very popular synchronous motor, 50hp and up for many years, these would run at exactly 3600/1800 or 3000/1500 rpm, depending on the supply Freq. .
    With modern magnetic materials used for motor rotors & electronic control methods, synchronous motors are now seen in AC servo's, Where the rotor can faithfully follow the rotating field.
    Al.

    Last edited by Al_The_Man; 05-09-2007 at 02:49 PM.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  17. #17
    Registered
    Join Date
    Feb 2007
    Location
    USA
    Posts
    424
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by Al_The_Man View Post
    I think you are referring to Wound rotor motor for non-synchronous speed control, as is often used in Crane applications etc.
    A synchronous motor does not, or should not run with any slip, as the idea is to run in perfect synchronism with the supply frequency.
    The AC induction motor with DC injection to the rotor type were a very popular synchronous motor, 50hp and up for many years, these would run at exactly 3600/1800 or 3000/1500 rpm, depending on the supply Freq. .
    With modern magnetic materials used for motor rotors & electronic control methods, synchronous motors are now seen in AC servo's, Where the rotor can faithfully follow the rotating field.
    Al.
    Yeah you are right I was bluring some facts there, sync motors do have an armature though. I was called to a press in the midest of my message, so I lost track of my thoughts. I actual have a wound rotor motor on one of my die cutters at work its around a 5HP I think, I cannot read Italinan so I am not positive the press dates from around 1955 its got brushes and slip rings. Casacading is done on wound rotor motors, wound motor rotors are seeing a resurge in the hybrid car market of all places.

    chris



  18. #18
    Registered
    Join Date
    Mar 2007
    Location
    Australia
    Posts
    85
    Downloads
    0
    Uploads
    0

    Default

    If you have a 5Hp three phase motor available, that will work fine on your lathe if it will physically fit onto the motor mounting bracket.

    Just because it is 5Hp does not mean it is going to draw more power than a 3Hp motor, if it is only loaded up to 3Hp. Just set the current limit on the VFD at some safe value, and the VFD will limit the motor to 3HP output.

    As others have already said, single phase motors are just completely unsuitable for any reasonable speed reduction.



  19. #19
    Registered
    Join Date
    Feb 2007
    Location
    USA
    Posts
    424
    Downloads
    0
    Uploads
    0

    Default

    ???



  20. #20
    Member vladdy's Avatar
    Join Date
    Feb 2004
    Location
    Perogie Flats, Canada
    Posts
    361
    Downloads
    1
    Uploads
    0

    Default

    my origional interest was to allow about a +15/-35 % in speed using the vfd, from what I have read some places, a vfd will apparantly work with a single phase input, and I was hoping to get it to output single phase as well, but the baldor motor that I have on the old Gisholt has start windings, and looks like it won't work, not even a 'kinda close' speed range capability..
    I wasn't able to get any 3 phase motors [as of yet, anyways] so I guess it goes into the 'good, just can't use it right now' corner....
    guess i'm stuck with a six speed lathe...

    thanks all..



Page 1 of 2 12 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Will a VFD output single phase?

Will a VFD output single phase?