Problem Beating my head against the wall....

Results 1 to 5 of 5

Thread: Beating my head against the wall....

  1. #1
    Registered
    Join Date
    Dec 2016
    Location
    United States
    Posts
    49
    Downloads
    0
    Uploads
    0

    Angry Beating my head against the wall....

    Spent the last few hours trying to get the VFD and spindle to play nice. not happening. I have found vfd setting elsewhere and tried them to no avail. im pretty sure the vfd works. it is slow to spool up and the gives error code eoca or eocn. VFD is hy02d211b-t and the spindle is kl-2200w. wiring is correct. vfd is on 30 amp circuit by itself. if anyone else is using this setup, or knows where i may have gone awry, please, help this tired soul out! off to bed...

    Similar Threads:


  2. #2
    Registered
    Join Date
    Dec 2016
    Location
    United States
    Posts
    49
    Downloads
    0
    Uploads
    0

    Lightbulb Re: Beating my head against the wall....

    Move along. Nothing to see. The problem was PD008 wasnt set to my line voltage. That'll teach me to push through being tired at midnight....

    Attached Thumbnails Attached Thumbnails Beating my head against the wall....-drink-coffee-jpg  
    Last edited by kebuttke; 02-18-2017 at 10:20 AM. Reason: humor


  3. #3
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: Beating my head against the wall....

    Quote Originally Posted by kebuttke View Post
    Move along. Nothing to see. The problem was PD008 wasnt set to my line voltage. That'll teach me to push through being tired at midnight....
    Post what settings you are using, there are some wrong setting out there, that will let your spindle run, but after awhile the spindle or VFD will be damaged

    There are some very important Parameters to be set, if you have used what I post and have checked that they are all set correct, then you should be good to go, one wrong Parameter setting can mean smoke

    EOCA is over currant on ramp up

    Mactec54


  4. #4
    Registered
    Join Date
    Dec 2016
    Location
    United States
    Posts
    49
    Downloads
    0
    Uploads
    0

    Default

    Quote Originally Posted by mactec54 View Post
    Post what settings you are using, there are some wrong setting out there, that will let your spindle run, but after awhile the spindle or VFD will be damaged

    There are some very important Parameters to be set, if you have used what I post and have checked that they are all set correct, then you should be good to go, one wrong Parameter setting can mean smoke

    EOCA is over currant on ramp up
    I used your settings! Lol. The settings in particular had a note about making sure pd008 was set to line voltage.



  5. #5
    Registered
    Join Date
    Dec 2016
    Location
    United States
    Posts
    49
    Downloads
    0
    Uploads
    0

    Default Re: Beating my head against the wall....

    For posterity! Original poster is Mactec54.


    This is all you need, all the basic Parameter Settings are the same for all the 400Hz Spindles, just voltage and Amps that are different

    Don't do a Reset unless you have to, sometimes doing this affects the order of how the Parameters get set

    Huanyang Mactec54

    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock

    PD001=0 (1 For Remote Control)

    PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )
    ( J1 Also Needs to be set for Terminal Control )

    PD003=400

    PD004=400

    PD005=400

    PD007=20

    PD008=220 (120 If you have 120v VFD )

    PD009=15

    PD010=8

    PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)

    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings

    PD014 Acceleration=12 ( Adjust to suit)

    PD015 Deceleration=12 (Adjust to suit)

    ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)

    PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )

    PD142= ( Motor Max Amps)

    PD142=( 220vSet for your motor Amp Rating 2.2Kw Spindle 9 amp )
    PD142=( 220VSet for your motor Amp Rating 1.5Kw Spindle 7 amp )
    PD142=( 220v Set for your motor Amps Rating 800w Spindle 4 amps )
    PD142=( 120v Set for your motor Amp Rating 800w Spindle 7 amp )

    PD143=2 ( Motor Number of Poles)

    PD144=3000 (Max Motor RPM) =3,000= (24,000)

    PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )

    PD72=400

    PD73=120 ( 100 Minimum Setting )



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Beating my head against the wall....

Beating my head against the wall....