Move along. Nothing to see. The problem was PD008 wasnt set to my line voltage. That'll teach me to push through being tired at midnight....
Spent the last few hours trying to get the VFD and spindle to play nice. not happening. I have found vfd setting elsewhere and tried them to no avail. im pretty sure the vfd works. it is slow to spool up and the gives error code eoca or eocn. VFD is hy02d211b-t and the spindle is kl-2200w. wiring is correct. vfd is on 30 amp circuit by itself. if anyone else is using this setup, or knows where i may have gone awry, please, help this tired soul out! off to bed...
Similar Threads:
Move along. Nothing to see. The problem was PD008 wasnt set to my line voltage. That'll teach me to push through being tired at midnight....
Last edited by kebuttke; 02-18-2017 at 10:20 AM. Reason: humor
Post what settings you are using, there are some wrong setting out there, that will let your spindle run, but after awhile the spindle or VFD will be damaged
There are some very important Parameters to be set, if you have used what I post and have checked that they are all set correct, then you should be good to go, one wrong Parameter setting can mean smoke
EOCA is over currant on ramp up
Mactec54
For posterity! Original poster is Mactec54.
This is all you need, all the basic Parameter Settings are the same for all the 400Hz Spindles, just voltage and Amps that are different
Don't do a Reset unless you have to, sometimes doing this affects the order of how the Parameters get set
Huanyang Mactec54
PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
PD001=0 (1 For Remote Control)
PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control )
( J1 Also Needs to be set for Terminal Control )
PD003=400
PD004=400
PD005=400
PD007=20
PD008=220 (120 If you have 120v VFD )
PD009=15
PD010=8
PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)
PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
PD014 Acceleration=12 ( Adjust to suit)
PD015 Deceleration=12 (Adjust to suit)
( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
PD141=220 ( Motor Rated Voltage ) (120 for VFD Rated for 120v )
PD142= ( Motor Max Amps)
PD142=( 220vSet for your motor Amp Rating 2.2Kw Spindle 9 amp )
PD142=( 220VSet for your motor Amp Rating 1.5Kw Spindle 7 amp )
PD142=( 220v Set for your motor Amps Rating 800w Spindle 4 amps )
PD142=( 120v Set for your motor Amp Rating 800w Spindle 7 amp )
PD143=2 ( Motor Number of Poles)
PD144=3000 (Max Motor RPM) =3,000= (24,000)
PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )
PD72=400
PD73=120 ( 100 Minimum Setting )