    Default Huanyang inverter PD settings

    I have bought the 4kw inverter form huanyang power my car lift which is 3 phase with a 3 KW motor, To be honest it was all quite easy to wire and athough the default figures were not what was specified in the instruction manual ive changed the ones i feel relevant.

    Problem is the inverter will run the lift fine apart from when i try to lift a car, My CRX is only 950kg and the motor gradually gets slower the further the car suspension goes up while trying to lift until its obviously going to stop so i havent pushed it as i dont want to blow anything up.

    I think my only solution would be to make a gearbox to run up the gearing as is currently 3.85:1.
    But i would like to make sure that theres nothing i have missed in the VFD settings which would give me a bit more torque.

    Heres the settings.



    Similar Threads:


  2. #2
    Registered
    Join Date
    Mar 2013
    Location
    USA
    Posts
    5
    Downloads
    0
    Uploads
    0

    Default

    pd003 - pd005 set to 60, pd014 is the ramp up time it should be shorter 1 to 3 maybe



  3. #3
    Registered
    Join Date
    Mar 2013
    Location
    USA
    Posts
    5
    Downloads
    0
    Uploads
    0

    Default

    My bad, you're in England. Keep the 50 Hz but change the ramp. You are waiting 30 seconds for the motor to ramp up to is set speed.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Huanyang inverter PD settings

Huanyang inverter PD settings