2 pole, 4 pole? What max frequency do you need? 666 or 333 Hz?
If tables are similar to C300 then
F0.8 sets upper frequency limit.
What have got for F1.15 -- rated motor voltage.
F1.16 needs to be higher than the default of 50?
F1.17 rated current of motor. Is it set high enough?
F1.24 - F1.27 motor specs. may need changing from default.
F2.5 max frequency setting. Default is only 50
Does the unit have default settings initially or was it inherited form some unknown application with strange settings?
GC.0,1,2 Undervoltage/overvoltage limit, current limit.
Lots of things can make it sick.
Are using the front panel control or external voltage control F2.1 being not correct won't help.
Get it running on the front panel control first.