    Need help wiring VFD

    I need help determining what input power wires go to on my VFD. The unit I have is a TB Woods SW1. On the top of the unit there are three connection terminals, L1/L, L2/N, L3. So, going to the unit is the 220v which has a red (110v) a black (110v) a white (Neutral) and a green (ground). What terminals do the two 110v’s go to and what terminal does the neutral wire go to, if any?

    Unfortunately, the manual is lacking in clarity regarding the input power source and just shows three unlabeled lines going to L1/L, L2/N,L3.

    I understand the connections to the motor just need a little help with the power inputs.

    Any help would be greatly appreciated.

    Thanks


  2. #2
    UUU
    UUU is offline
    Registered
    Join Date
    Apr 2010
    Location
    UK
    Posts
    289
    Downloads
    0
    Uploads
    0
    What is the rated input voltage of the unit you have? This manufacturer seems to offer 115V and 240V models.


  3. #3
    Registered
    Join Date
    Jan 2005
    Location
    USA
    Posts
    2,920
    Downloads
    0
    Uploads
    0
    turboedgs

    Post a photo of the terminals,is there a PDF on the web we can look at as well
    The input terminals on some of these drives are easy to get messed up
    Mactec54


  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,930
    Downloads
    0
    Uploads
    0
    Inputting a N.A. neutral into a 3 phase bridge will not do anything, if using 2x 240v conductors.
    There will be no conduction on the neutral at all, I believe the reason they show L2/N is when used in countries that use one leg of the 240 as neutral, as in UK etc. or for a 115v version.
    I would think that the 240v go into L1 L2 .
    Do you have a link to the manual?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #5
    Registered
    Join Date
    Sep 2009
    Location
    US
    Posts
    29
    Downloads
    0
    Uploads
    0
    Here is the link, the wiring diagram is on page 23 of the PDF

    http://www.vacon.com/File.aspx?id=47...&name=DPD00286

    On the top of the unit the inputs are labled as L1/L - L2/N - L3 but is not listed that way in the PDF, just L1- L2 - L3

    My input power will be single pase 220-240v, black (110-120v), Red (110-120v), White (neutral), Green (Ground).


    As to the specs of the VFD:

    Input: 220-240v +/- 10%, 50-60hz, 1 or 3 phase
    Output: 10.5A, 3.0HP, (2.2kw) 3 phase

    Model number is SW1C20030H02

    Thanks for the help


  • #6
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,930
    Downloads
    0
    Uploads
    0
    As I mentioned, there is no point inputting a 240v with C.T. neutral if the input is to a 3 phase bridge, most VFD's I have stripped for power supply parts are wired this way, in any case if you just input 240 1 phase to L1 L2 you should not do any harm as it would simulate 2 of 3 phases with the L3 phase missing.
    If the unit does accepts 1 phase then from the manual I would hook up the 240v to L1 L2.
    Neutral is not connected.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #7
    Registered
    Join Date
    Sep 2009
    Location
    US
    Posts
    29
    Downloads
    0
    Uploads
    0
    Thanks for all the help guys!

    One of the 120v's into L1 and the other into L2 with no nuetral hooked up and the ground connected to the ground post and I have a fully functioning VFD.

    Thanks!


  • #8
    Registered
    Join Date
    Jan 2005
    Location
    USA
    Posts
    2,920
    Downloads
    0
    Uploads
    0
    turboedgs

    Do it the way Al has said, if you are still not sure give them a call the number is on the PDF file, Do not put the Neutral wire on to your VFD for 220v single phase, (US single phase), or you will have a problem, Cut that wire off before you start
    Mactec54


  • #9
    Registered
    Join Date
    Aug 2010
    Location
    United States
    Posts
    3
    Downloads
    0
    Uploads
    0
    Hi guys. I am inputting a 120v household line into a SW1 and Im a bit confused about which wire goes into the input leads (L1,L2,L3). Any help would be greatly appreciated.


  • #10
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,930
    Downloads
    0
    Uploads
    0
    According to the label with a 1 phase 2 wire input that has a neutral L1/L is hot and L2/N is neutral.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • Similar Threads

    1. Wiring Help
      By DistortedDesign in forum Hobbycnc (Products)
      Replies: 0
      Last Post: 05-05-2010, 07:30 PM
    2. Help with wiring!
      By SatanKlawz in forum DIY CNC Router Table Machines
      Replies: 4
      Last Post: 04-12-2010, 09:40 AM
    3. MPG wiring at x4
      By cvafiadis in forum Syil Products
      Replies: 1
      Last Post: 05-24-2008, 11:14 PM
    4. Needs some wiring help... please
      By nosplinters in forum General Electronics Discussion
      Replies: 11
      Last Post: 02-29-2008, 07:00 AM
    5. 425 wiring
      By cueshark in forum Automation Technology Products
      Replies: 6
      Last Post: 02-27-2008, 05:20 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.